DIYnot
Local | Network
   DIYnot > Forums
Local | Network
Wiring diagram correct for 63A RCCB and 50A MCB?
Author Message
Buzzcut
from United Kingdom
PostPosted: Fri Dec 04, 2009 4:27 pm Reply with quote
Afternoon...
I've just bought a new place and scarily there's no RCD on the 10.8 kW electric shower. I had a sparky in to check a few things out and he said to get a standalone 50A 30mA RCD unit that goes next to the CU (rather than replace the whole CU which is a bit old).
I've got one but would it be bi-directional i.e. can I switch the In with the Out. My feed from the CU is from below but does that still have to be wired into the top of the RCCB as drawn below? Common sense tells me that it can be wired either way but I'm not 100% sure.
See here for the wiring I'm planning.. http://www.filedump.net/dumped/mcbrccb1259943821.jpg
Cheers for any advice you can give. I'll get a whole new CU once funds allow but I just want to protect the shower at the mo.
Buzz
Back to top
 Alert Moderators
Steve
from United Kingdom
Thanked: 226 times
PostPosted: Fri Dec 04, 2009 4:28 pm Reply with quote
No. Wire it correctly.
Is your electrician coming back to test this RCD?
Back to top
 Alert Moderators
Buzzcut
from United Kingdom
PostPosted: Fri Dec 04, 2009 4:38 pm Reply with quote
..and correctly would be??
He'll check it when he wires in the heated floor next week.
Back to top
 Alert Moderators
Steve
from United Kingdom
Thanked: 226 times
PostPosted: Fri Dec 04, 2009 5:08 pm Reply with quote
Supply in the top of the RCD.
Shower wired to the N of the RCD bottom, and L of the 50A MCB.
Back to top
 Alert Moderators
Buzzcut
from United Kingdom
PostPosted: Fri Dec 04, 2009 5:16 pm Reply with quote
Thanks, Steve
So the drawing was correct only if the supply was coming in the top.
There's a bar already connecting the L RCD load to the L MCB supply.
Much appreaciated.
Buzz
Back to top
 Alert Moderators
flameport
from United Kingdom
Thanked: 695 times
PostPosted: Fri Dec 04, 2009 6:22 pm Reply with quote
I suggest you get a larger enclosure, that one is barely big enough for the devices and it will be extremely difficult to get 10mm cables in there.
Back to top
 Alert Moderators
ban-all-sheds
from United Kingdom
Thanked: 1874 times
PostPosted: Fri Dec 04, 2009 6:28 pm Reply with quote
There'd be more space if the pointless MCB were removed.
Back to top
 Alert Moderators
Taylortwocities
from United Kingdom
Thanked: 1096 times
PostPosted: Sat Dec 05, 2009 11:51 am Reply with quote
icon_question.gif Do you think that CDL7-63 thingy is an RCBO then?
Back to top
 Alert Moderators
mfarrow
from United Kingdom
Thanked: 186 times
PostPosted: Sat Dec 05, 2009 12:16 pm Reply with quote
I think BAS was trying to point out that the shower is already fed from the CU - therefore should already be protected by an MCB/fuse.
Back to top
 Alert Moderators
Page 1 of 1
Jump to:
Wiring Diagram - is this correct? 10 160 Sun Oct 07, 2012 9:08 am
bathroom fan wired in with lights is my diagram correct 25 1400 Sun Sep 25, 2005 12:17 pm
RCD / RCCB Continuous Tripping 13 1220 Sun Aug 26, 2007 2:38 pm
HELP: What AMP should RCCB/MCB For Electric Shower ? 20 1920 Mon Apr 23, 2007 7:31 pm
RCBO and RCCB question....?? 9 35620 Fri Feb 23, 2007 1:03 pm
DIYnot
Please read our Privacy Policy. Copyright © 2000-2015 DIYnot Limited.