i now live in spain we only get winter here for about 3 months and we dont have gas mains i have been looking at a room wood fire with a backboiler so i could here 3-4 radiators (no hot water needed) does any one have a design for the system and any help
On the most basic arrangement, you'll probably find the manufacturer will ask for some of the system to be un-controlled eg. gravity heat leak rads usually towel rails. This side would also connect with open F&E/safety vent. The other rads would be on pumped circuit, controlled by pipe stats to shut down pump when return temps are too low for back boiler.