Potterton Puma 80 - Intermittent CH


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
Wiggla

from United Kingdom

Joined: 08 Mar 2010
Posts: 4
Location: London,
United Kingdom

PostPosted: Mon Mar 08, 2010 8:43 pm Reply with quote

Hi, I have got a Puma 80 that has been giving me some problems the last few weeks. The issue is around the CH, I've had no problems drawing hot water on demand at any time. The problem with the heating is that it is intermittent. When it's on the timer the boiler fires up for a short while then turns itself off, even though the thermostat is set way above the current temperature. It comes on for about 1 minute then turns off for about 5-10, and runs through this cycle throughout the timer period. I switched it to constant to see if that made a difference and it worked. I just controlled it through setting the thermostat. It was working fine for about 2-3 weeks, firing everytime I turned the thermostat up past the ambient temperature, but now it's doing the same on constant as it was on the timer, so it only ever fires intermittently now regardless of the thermostat setting and temperature.

I've taken the front off to have a look and the pump appears to be working fine (HW is still drawing fine and the boiler fires everytime I use the HW). I did notice that the relay on the PCB is clicking off when the CH turns off each time, it's relay RL2. The PCB has actually been replaced in the last two years (it caught fire in the corner, as they do). So the electrics on that should be fine.. should be. Having said that the red LED is not lit.

Can anyone offer an explanation for the intermittent firing? I'm thinking it may be the CH sensor switch but I don't have a meter to measure resistance etc. Is it obvious to anyone?

Any help gratefully received, apologies for the length of post, I just wanted to get all the detail in. Thanks.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
combispecialist

from United Kingdom

Joined: 04 Mar 2010
Posts: 269
Location: Lincolnshire,
United Kingdom
Thanked: 35 times

PostPosted: Mon Mar 08, 2010 8:52 pm Reply with quote

Sounds 2 me like the wax capsule in the diverter valve is getting stuck in hw mode,make sure theres no dripping taps etc,straight forward job 2 change wax capsule icon_biggrin.gif
Back to top
 Alert Moderators
Wiggla

from United Kingdom

Joined: 08 Mar 2010
Posts: 4
Location: London,
United Kingdom

PostPosted: Mon Mar 08, 2010 9:42 pm Reply with quote

Hi, thanks for the reply, appreciate it. Just wondered whether if it was getting stuck on HW should the boiler be firing or does it not necessarily fire unless you actually turn the tap on? I can't find any taps that are leaking.
Back to top
 Alert Moderators
combispecialist

from United Kingdom

Joined: 04 Mar 2010
Posts: 269
Location: Lincolnshire,
United Kingdom
Thanked: 35 times

PostPosted: Mon Mar 08, 2010 10:18 pm Reply with quote

The boiler will still fire for heating but will go off after short while cos wax capsule is not opening up heating circuit.its a common fault on a puma like the p.c.b burning out icon_smile.gif
Back to top
 Alert Moderators
Wiggla

from United Kingdom

Joined: 08 Mar 2010
Posts: 4
Location: London,
United Kingdom

PostPosted: Tue Mar 09, 2010 7:35 pm Reply with quote

Thanks. The last couple of days the heating has apparently been working in that the rads are hot, even though the boiler only fires for 30-60 seconds every 5 minutes or so. It still flicks itself off but the radiators are heating up, albeit gradually. Is this consistent with the valve not working?
Back to top
 Alert Moderators
powell30

from United Kingdom

Joined: 29 Jan 2008
Posts: 1214
Location: Birmingham,
United Kingdom
Thanked: 129 times

PostPosted: Tue Mar 09, 2010 7:44 pm Reply with quote

Yes......wax capsule needs changing. Some heat is passing into the heating circuit but m ost is just going round the boiler....hence boiler reaches temp and cuts off

Not difficult if you just change the front section
Back to top
 Alert Moderators
Wiggla

from United Kingdom

Joined: 08 Mar 2010
Posts: 4
Location: London,
United Kingdom

PostPosted: Tue Mar 09, 2010 7:47 pm Reply with quote

Great, thanks. Is it a DIY job (for someone of average ability) or should I get a pro in?

Thanks
Back to top
 Alert Moderators
powell30

from United Kingdom

Joined: 29 Jan 2008
Posts: 1214
Location: Birmingham,
United Kingdom
Thanked: 129 times

PostPosted: Tue Mar 09, 2010 7:50 pm Reply with quote

If you have the manual do it yourself..........drain boiler first and turn off cold mains......saves having water pour out onto the pcb......
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Intermittent problem with Potterton Puma 80E 6 560 Tue Dec 29, 2009 9:15 am
Potterton Puma 80e:- intermittent hot water supply 2 520 Sun Nov 27, 2005 8:36 am
potterton puma boiler - intermittent pumping 3 300 Wed Feb 06, 2008 7:52 pm
Potterton Puma 80 intermittent DHW 7 280 Mon Sep 20, 2010 6:57 pm
Potterton puma 80e - Intermittent hot water 3 620 Tue Mar 23, 2004 12:38 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.