Burying cable- how can gas pipe run across?

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
RRRRRR

from United Kingdom

Joined: 04 Feb 2010
Posts: 122
Location: Surrey,
United Kingdom
Thanked: 2 times

PostPosted: Tue Mar 16, 2010 11:57 am Reply with quote

Hi- I'm burying mains cables in a brick wall, before a nice Gas Safe man runs a new gas pipe to a cooker. Am I going to cause problems here, as I believe gas pipes must not be nearer than 25mm to circuits, and the pipe will be running across my vertical cable runs? Is there a way around this for the regs. such as the cable being in plastic tubing in the wall for extra insulation, otherwise I'll have to dig really deep channels? Thanks.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 47226
Location: London,
United Kingdom
Thanked: 1722 times

PostPosted: Tue Mar 16, 2010 12:19 pm Reply with quote

What did you tell the council would be the way you'd comply with the Building Regulations regarding the electrical work?
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17427
Location: Londonderry,
United Kingdom
Thanked: 1734 times

PostPosted: Tue Mar 16, 2010 12:45 pm Reply with quote

Where installation pipes are not separated by electrical insulating material, at least 25mm away from electricity supply and distribution cable

Electrical insulating material is best fulfilled by a piece of conduit, such as where a buried cable must cross a gas pipe buried in same wall surface.

But it is a kitchen and deemed the same as a special location, so as always part p applys as does informing building controls of new electircal work.
Back to top
The following user says thank you to PrenticeBoyofDerry for this useful post:
RRRRRR (16 Mar 2010)
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 47226
Location: London,
United Kingdom
Thanked: 1722 times

PostPosted: Tue Mar 16, 2010 1:09 pm Reply with quote

If the gas pipe is buried in the wall, won't it be the type with a PVC layer on the outside?
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17427
Location: Londonderry,
United Kingdom
Thanked: 1734 times

PostPosted: Tue Mar 16, 2010 1:13 pm Reply with quote

Sounds like the op is burying the cable in the wall and the gas pipe will run up the outside of this wall at a right angle to the cable.
Assuming the pipe should be clipped, this could well bring the pipe away form the wall a distance too.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 47226
Location: London,
United Kingdom
Thanked: 1722 times

PostPosted: Tue Mar 16, 2010 1:35 pm Reply with quote

PrenticeBoyofDerry wrote:
Sounds like the op is burying the cable in the wall and the gas pipe will run up the outside of this wall at a right angle to the cable.

It does, doesn't it. icon_redface.gif

Sorry.
Back to top
 Alert Moderators
RRRRRR

from United Kingdom

Joined: 04 Feb 2010
Posts: 122
Location: Surrey,
United Kingdom
Thanked: 2 times

PostPosted: Tue Mar 16, 2010 2:43 pm Reply with quote

Hi ban-all-sheds. Thanks for getting back. I haven't told them anything yet, as I'm trying to work out what I can and can't do so things don't have to be redesigned after submitting. Not done this before, and a bit confused to be honest. Is it that you do the best you can to meet the regs., but if really not practicable, there's limited flexibility?
Back to top
 Alert Moderators
RRRRRR

from United Kingdom

Joined: 04 Feb 2010
Posts: 122
Location: Surrey,
United Kingdom
Thanked: 2 times

PostPosted: Tue Mar 16, 2010 2:49 pm Reply with quote

Sorry to be dim here, but does this mean that if I bury the cables in a wall in plastic piping/conduit near the surface, a gas pipe can then happily run on the outside of the walll at right angles, and the 25mm rule is not relevant as I have plastic/ plaster as insulation?
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17427
Location: Londonderry,
United Kingdom
Thanked: 1734 times

PostPosted: Tue Mar 16, 2010 3:15 pm Reply with quote

Yes, as then then you have electrical insulation between both cable and pipe.
Back to top
The following user says thank you to PrenticeBoyofDerry for this useful post:
RRRRRR (16 Mar 2010)
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 47226
Location: London,
United Kingdom
Thanked: 1722 times

PostPosted: Tue Mar 16, 2010 5:55 pm Reply with quote

RRRRRR wrote:
Hi ban-all-sheds. Thanks for getting back. I haven't told them anything yet, as I'm trying to work out what I can and can't do so things don't have to be redesigned after submitting.

Not an issue, as they won't want detailed designs, just a statement on how you intend to comply.

You can read all about it here: electrics:part_p


Quote:
Not done this before, and a bit confused to be honest. Is it that you do the best you can to meet the regs., but if really not practicable, there's limited flexibility?

The Building Regs are pretty easy to comply with, as the requirement is very short on specifics.

The Wiring Regs too, if you want to go that way, won't stop you do anything which you would sensibly want to do.


Your biggest issue, I suspect, will be your council's attitude to DIY electrics - if they are one of the miscreant ones then you may want to think again about DIYing.

Or about notifying.... icon_confused.gif

Is this just a refurb, or are you doing an extension?


RRRRRR wrote:
Sorry to be dim here, but does this mean that if I bury the cables in a wall in plastic piping/conduit near the surface, a gas pipe can then happily run on the outside of the walll at right angles, and the 25mm rule is not relevant as I have plastic/ plaster as insulation?

Yup.

Do be aware of the rules on where you can bury cables though....
Back to top
 Alert Moderators
RRRRRR

from United Kingdom

Joined: 04 Feb 2010
Posts: 122
Location: Surrey,
United Kingdom
Thanked: 2 times

PostPosted: Tue Mar 16, 2010 6:39 pm Reply with quote

Hi ban-all-sheds again- great name, and thanks for taking the time to send me the very useful links. I'm knocking through a kitchen wall into an integral garage, to make a bigger kitchen and partitioned storage room, doing what I can myself where I'm allowed to these days (i.e. nowt). I've tackled high levels of wiring/ plumbing/ building in the past, but It's been a while and I'm having an absolute nightmare trawling through Part P's, new partition insulation targets, ventilation, heating, water and drainage, window area, sock colour etc. etc. working out what the BC's will expect when they turn up, once I've applied. I've just discovered for instance that the partition needs to be thermally insulated, so that's another trawl, as I know you can't cover electric cables with heat insulation materials, yet they need to be in the partition too. I think I need to go somewhere quiet and cry in a manly sort of way.....
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 47226
Location: London,
United Kingdom
Thanked: 1722 times

PostPosted: Tue Mar 16, 2010 6:50 pm Reply with quote

RRRRRR wrote:
I know you can't cover electric cables with heat insulation materials, yet they need to be in the partition too.

You just have to take account of the thermal insulation when calculating the current carrying capacity of the cables, and adjust their size and/or protective device rating to maintain IbInIz.
Back to top
 Alert Moderators
RRRRRR

from United Kingdom

Joined: 04 Feb 2010
Posts: 122
Location: Surrey,
United Kingdom
Thanked: 2 times

PostPosted: Tue Mar 16, 2010 7:21 pm Reply with quote

You've hit exactly where my problems are cutting in! I can work out the depth of insulation required by the regs. and buy the corresponding depth of wood for the partition, build a DPC and the partition wall with water pipes in it, hang the door, plasterboard one side, skim it, everything by the book/ regs., prior to the electrical work being done by a friendly Part P man (or woman- alright Stan) and then find it's all got to come down because the partition's now too thin to accommodate the required width of insulation now that that Ib ≤ In ≤ Iz thingy's come along, 'cos I didn't know about it!
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17427
Location: Londonderry,
United Kingdom
Thanked: 1734 times

PostPosted: Tue Mar 16, 2010 8:01 pm Reply with quote

It's cable size that will be effected by calculating thermal insulation factors.
That will not effect the size of your stud wall.
If the cable installed is completely surround by thermal insulation, it will effect the current carrying capacity of the cable, so the cable could well need up grading.
Back to top
 Alert Moderators
RRRRRR

from United Kingdom

Joined: 04 Feb 2010
Posts: 122
Location: Surrey,
United Kingdom
Thanked: 2 times

PostPosted: Wed Mar 17, 2010 10:18 am Reply with quote

Hi- thanks for even more info. Can't seem to find this area on the regs. Could a Part P electrician then turn up and wire up for a cooker point and extractor hood, with the insulation in place, or do you know if I'd have to get him to do the wiring in the partition first, then ask the friendly BC man what to do with insulation where the cables run?

When that part's resolved, do you know if I could do the fiddly bit of feeding/ channelling etc. all the wiring in a kitchen extension (all to Part P regs of course), and just get a friendly Part P man to connect it all up if he's happy with it, so Part P's certified? Or is that unacceptable?
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Burying a section of ring cable under the plaster in hallway 12 360 Thu Feb 28, 2013 9:34 am
Advice about burying a cable under a driveway.... 9 360 Tue Jun 11, 2013 10:22 am
Regulations for burying cable in wall 7 220 Fri Aug 10, 2012 1:18 pm
burying cable underground 22 4480 Sat May 24, 2008 11:43 pm
Burying SWA Cable 4 380 Fri Oct 09, 2009 8:06 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.