Joined: 26 Feb 2005 Posts: 7 Location: United Kingdom Thanked: 0 times
Posted: Sat Feb 26, 2005 6:10 pm Post Subject:
There isnt any more space to move it thats why i wondered wheter that devise from Screwfix would do the same thing. The distance betwwen the shower and the board is about 15 meters. It would be a massive job to rewire. Do you see a problem?
Joined: 14 Sep 2004 Posts: 3972 Location: United Kingdom Thanked: 0 times
Posted: Sat Feb 26, 2005 6:55 pm Post Subject:
Matt Milner wrote:
Do you see a problem?
yes. 6mm is no good for your shower. it should be 10. unless you want a fire to start. 6mm may be ok for short lengths (5M) but not 15. do you have an RCD in the CU? do you have a spare space on the RCD side? if notm then go for the shower CU. however, youll have to split the tails, which is only a DIYers job IF there is a isolator between meter and CU. if not youll be best of gettin someone to do that for you
Joined: 27 Aug 2003 Posts: 21990 Location: London, United Kingdom Thanked: 78 times
Posted: Sat Feb 26, 2005 9:37 pm Post Subject:
Matt Milner wrote:
I think i will have to put a weekend to one side then and try and get all the boards up in the house. Will it really set on fire??
6mm˛ is very borderline for that load. In free air it's OK, but anything that reduces the cable's ability to shed heat, like being bunched with other cables, or being in trunking or conduit or insulation means that it will not be OK.
__________________ I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Joined: 23 Jan 2005 Posts: 900 Location: United Kingdom Thanked: 0 times
Posted: Sat Feb 26, 2005 11:02 pm Post Subject:
If 5m of 6mm cable is OK firewise then so is 15m - or 150m for that matter. The power dissipation PER METRE is the same in each case. Actually it goes down a little as the length goes up due to the real reason for using thicker cable on a long run. It's all about voltage drop.
According to my catalogue, 6mm cable is rated at 51 amps in free air but only 37 amps in conduit. Yours is in free air. I haven't got a calculator handy right now (thanks a bunch Microsoft) but some rough and ready mental arithmetic says that 15m of it is going to lose you about 5 volts. That's acceptable.
Joined: 26 Feb 2005 Posts: 7 Location: United Kingdom Thanked: 0 times
Posted: Sat Feb 26, 2005 11:31 pm Post Subject:
I can confirm its running free. It isnt bunched together nor runs through any installtion either. I have re mesashered and its actually about 18 meters from shower to box. It is currently protected by the old 32 MCB but I have ordered a new 45amp one. I also want to add a r.C.D thats why I asked about the Screwfix one.
Joined: 23 Jan 2005 Posts: 900 Location: United Kingdom Thanked: 0 times
Posted: Sat Feb 26, 2005 11:50 pm Post Subject:
No more so than any other cable might. To eliminate hot spots, make sure all your joints are tight but don't get paranoid. You might just manage to start a fire with a bad joint inside a piece of choc block wrapped in PVC tape lying in a pile of old wood shavings - but who would be that stupid?
The answer is a cowboy electrician who rewired a flat for a penny pinching landlord who rented it to us thirty years ago. That was in my student days. The flat is still standing and I'd be very surprized if anybody else has found that choc block!
Joined: 25 Feb 2005 Posts: 102 Location: United Kingdom Thanked: 0 times
Posted: Sun Feb 27, 2005 12:18 am Post Subject:
you don't always have to uprate the mcb, a 32amp mcb should take 1.5times its rated current for a period of time before tripping normally upto 4 hours ,most people only shower for 10 minutes or so,the mcb should provide over current protection for the cable,as well as short circuit protection. If you uprate the mcb you should consider uprating the cable as well. The current rating of the cable depends also on the type of fuse /MCB used to protect the circuit as well as the length of the circuit .Installing a R.C.D is always a good idea considering the location.Make sure you have adequate supplementary earth bonding of the pipework if in copper
Joined: 26 Feb 2005 Posts: 7 Location: United Kingdom Thanked: 0 times
Posted: Sun Feb 27, 2005 10:16 am Post Subject:
I must admit it has not tripped the MCB as yet and I would rather have a lower amp han a higher one. There is one problem running a 32 Amp one is that when the shower is on the MCB buzz's a bit and get warm. It has burned the double pole switch out as well but thats because it was only a standard 30amp one.