How do I acheive a 'Fire Rated' Ceiling


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Building Regulations and Planning Permission
Search this topic :: View previous topic :: View next topic  
Author Message
glangri2

from United Kingdom

Joined: 04 Feb 2010
Posts: 112
Location: Hertfordshire,
United Kingdom
Thanked: 3 times

PostPosted: Thu Mar 25, 2010 10:24 pm Reply with quote

My 2 storey extension will have an integral garage on the ground floor, and 2 bedrooms above it.

Can anyone tell me how I can achieve the necessary fire rating for the ceiling, in material terms?

Strength wise, the wooden joists need to be 146mm min, but I have read on another post that for the fire rating they have to be 195mm min

Is this true?

If so, and I go for 195 joists with 100mm of celotex between then, fitted in the gaps and flush with the top ...............

What flooring to I need for te bedrooms ? 22mm ?
What thickness of plaster board do I need for the garage ceiling?

And if I go for fire rated low energy down lighters, can I run the cables in the 95mm gap between the top of the plasterboard and the bottom side of the insulation?

And do I need to use temp resistant cable?

Sorry for all the questions !

Cheers
Gary
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
kevindgas

from United Kingdom

Joined: 28 Mar 2006
Posts: 5652
Location: Southampton,
United Kingdom
Thanked: 453 times

PostPosted: Thu Mar 25, 2010 11:01 pm Reply with quote

the bits i can help you on

1. ceiling plasterboard use the foil covered type this has a 30? mins fire resistance
2. if you fit downlighters in it you will need a fire hood for each light

suggest you download building regs document B this has all the fire stuff in it
Back to top
 Alert Moderators
glangri2

from United Kingdom

Joined: 04 Feb 2010
Posts: 112
Location: Hertfordshire,
United Kingdom
Thanked: 3 times

PostPosted: Thu Mar 25, 2010 11:06 pm Reply with quote

I was having a look through the regs earlier, and couldn't find the info I needed in simple enough terms .................... mind you I was looking at it at work at lunchtime, so was in a bit of a hurry.
Back to top
 Alert Moderators
freddymercurystwin

from United Kingdom

Joined: 21 Jan 2007
Posts: 11756
Location: Devon,
United Kingdom
Thanked: 1193 times

PostPosted: Fri Mar 26, 2010 12:37 am Reply with quote

1 layer of 15mm fireboard beneath and 22mm t&g flooring (chipboard or plywood (preferably plywood with lots of screws to try and stop the creaking)) above will achieve 1/2 hours fire resistance. Technically speaking the joists should be at least 195mm high, the depth of the joists is derived from fire tests carried out by British Gypsum, Building Control may well accept lesser joists, you will have to ask them.

Or use 1 layer of British Gypsum 12.5mm SoundBloc board instead.
Back to top
The following user says thank you to freddymercurystwin for this useful post:
glangri2 (26 Mar 2010)
 Alert Moderators
tfish

from United Kingdom

Joined: 05 Dec 2009
Posts: 137
Location: Tyne and Wear,
United Kingdom
Thanked: 6 times

PostPosted: Tue Mar 30, 2010 6:32 pm Reply with quote

either red board or double board with 12.5 norm. you need to go crazy on insulation as well otherwise the cool zone of the garage will be drawn into the over rooms, a very common fault with inbuild garages
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Building Regulations and Planning Permission All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
running a soil stack through a 60 minute fire ceiling 7 860 Tue Feb 23, 2010 9:47 am
Fire regs for exposed timber ceiling joists 8 220 Fri Oct 18, 2013 6:02 pm
Ceiling speaker wire 10 1000 Tue Jul 06, 2010 5:41 pm
Removal of RSJ from ceiling 8 400 Tue Sep 28, 2010 3:53 pm
vaulted ceiling on a lean to roof (new extension) 8 4980 Thu Nov 05, 2009 9:59 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.