Fused Spur from Immersion Heater Point

This topic originated from the How to page called Adding a spur to a ring circuit from a socket
Click here to return to the page called Adding a spur to a ring circuit from a socket.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
KW

from United Kingdom

Joined: 03 Mar 2005
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Mar 03, 2005 7:37 pm    Post Subject:
Fused Spur from Immersion Heater Point
Reply with quote Thanks

I am planning to install a pump which will power two showers. The most convenient place to site the pump is in the airing cupboard.
We already have a power supply in the airing cupboard to run the immersion heater.
The immersion heater power supply is a switched, fused (13 amp) unit with a flex outlet. It seems to be part of a ring (there are two cables entering it) - probably the socket ring main, but I have not checked that.
The instructions with the pump say the pump must be connected to a 230 volt 50Hz supply with a switched spur fused at 5 amps.
Can I just run a spur from the immersion heater supply point and stick a 5 amp switched spur on the end of it?
Are there any other (better) options?
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4541
Location: United Kingdom
Thanked: 10 times

PostPosted: Thu Mar 03, 2005 8:03 pm    Post Subject:
Reply with quote Thanks

Yes you can connect your shower pump to the ring main via a fcu with appropiate fuse,

Whether the Immersion heater should be there or not is another matter, most would say not, but I can't see that it is immediatly dangerous
Back to top
 Alert Moderators
KW

from United Kingdom

Joined: 03 Mar 2005
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Mar 04, 2005 9:45 am    Post Subject:
Reply with quote Thanks

Thanks, but...

Would you like to elaborate on your comment about the immersion heater? What might be wrong with the immersion heater being there (and by "there" do you mean in the airing cupboard or in the ring main?).

It may not actually be in the ring main... all I know for sure is that it is not itself a spur because it has a cable coming in and a cable going out. It may be a totally different circuit - I did think when I looked at it that the wires looked a bit thicker than normal.

If it is on some other circuit does this affect whether I can run a 5amp fused spur from it?
Back to top
 Alert Moderators
mapj1

from United Kingdom

Joined: 24 Nov 2004
Posts: 1040
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Mar 04, 2005 10:31 am    Post Subject:
Reply with quote Thanks

As a fixed load, if it is on the ring main, it is potentially hogging 12 or 13A of the 32 you have for all the other sockets on the ring, effectively reducing your capacity for running other things. If you don't get much nuisance tripping/blown fuses, you don't actually have a problem right now, but if you ever do have trouble when a number of appliances are on together, then the heater should really be hived off onto its own circuit and fuse or breaker at the board, and this has been the recommended practice for the last 20 years or so. 'In the airing cupboard' is fine - the means of isolation should be as near as possible to the load or clearly labelled, sounds like in this case it already is!
regards M.
Back to top
 Alert Moderators
KW

from United Kingdom

Joined: 03 Mar 2005
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Mar 04, 2005 10:53 am    Post Subject:
Reply with quote Thanks

And if it is on its own circuit is it still OK to hang a 5amp fused spur off it?

From your explanation I am guessing that it is... I would be putting a relatively small load onto a circuit which is already designed to take a large load.

In fact we hardly ever use the immersion heater - just when the gas fired boiler fails...

(and I think this discussion may have explained the fuse in my fuse box that I have never labelled because I couldn't work out what it was...)
Back to top
 Alert Moderators
Panjandrum

from United Kingdom

Joined: 03 Dec 2004
Posts: 287
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Mar 04, 2005 11:12 am    Post Subject:
Reply with quote Thanks

KW: Do you have a switch somewhere else that controls the immersion heater? We have one in the airing cupboard, one in the kitchen. If you have, there would be two wires to the airing cupboard switch. even if on a dedicated circuit.
Back to top
 Alert Moderators
KW

from United Kingdom

Joined: 03 Mar 2005
Posts: 4
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Mar 04, 2005 11:28 am    Post Subject:
Reply with quote Thanks

No additional switch elsewhere (or, if there is, it must have been in the ON position for the past 20 years!!)

As far as I am aware the switch in the airing cupboard is all that is needed to switch on the immersion heater
Back to top
 Alert Moderators
kai

from United Kingdom

Joined: 15 Aug 2004
Posts: 729
Location: United Kingdom
Thanked: 5 times

PostPosted: Fri Mar 04, 2005 12:08 pm    Post Subject:
Immersion switch
Reply with quote Thanks

There should be a 13amp fused connection unit to control the immersion within 2 metres of it, your setup seems correct in that respect.
An immersion circuit should not be shared with anything else really, but in theory you could safely run a 13amp immersion plus a 3amp fused supply for a small pump off the same B16amp MCB, as 13 + 3 amp exactly equals 16amps. use 2.5.sq.mm. cable, or 4mm cable where run is very long. (see the IEE on-site guide for exact rules).
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Relocating Immersion heater supply point... 10 620 Thu Sep 14, 2006 11:23 pm
Change an existing spur point into a single power socket 14 460 Sat Jul 25, 2009 6:47 pm
cooker point and spur 4 200 Wed Mar 11, 2009 7:32 pm
Spur point 2 480 Sun Aug 07, 2005 5:49 pm
16A Spur for Immersion Heater - Additional Fused Spurs 6 380 Mon Feb 11, 2008 2:15 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.