PostPosted: Sun Apr 25, 2010 7:03 pm Reply with quote

Hi Folks,

Have just had a new central heating system installed comprising :-
New combi boiler - Bosch Worcester 37 CDi,
new radiators,
new TRVs
new pipework (15mm copper replacing 8mm microbore).

The property is unoccupied whilst we refurbish it, although we're there most evenings and weekends.

Existing pipework was retained for cold water supply to boiler & domestic hot water. System was supplied and installed by a GasSafe plumber from an approved Bosch agent (a long established local business).

System pressure has remained constant for about 2 weeks - the system was bled and re-pressurised the day after installation / commissioning.

System works fine when the central heating is on (ie at times when the central heating clock is set to activate the central heating).

However if we run the hot water tap outwith these times (ie CH off) the water runs cold. The "Burner on indicator light" illuminates momentarily then goes out (for about 45 secs?) after this happens four times the boiler displays fault code "EA" ("Flame not detected") and the fault and mains power (blue) lights flash.

Reseting the boiler clears the error but the error returns if we run the hotwater. If we "Advance" the central heating clock (ie turn CH on) then boiler goes through a slow start warm-up (-!!- and XX (temp) alternate) for about 15 minutes (Bosch manual says this is to fill the condensate trap?). Then central heating and hotwater then both work OK.

Supplier has sent the plumber out a number of times and reports that the pressures and tempeartures are all ok and it's an air lock caused by the fact it's a a new system and the chemicals they put in. I think it's a boiler / install fault and the chemicals should only be in the CH system (would turning on central heating clear an air lock in DHW supply?).

This has been going on for 2 weeks and we haven't accepted the system (or received their bill) yet but we are getting exasperated and feel like taking the whole lot out and dropping it on their doorstep.

Can anyone advise what we should do eg persevere with the supplier or try contacting Bosch direct. Finally does anyone have any ideas as to what could be causing the problem?

THANKS
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
gordongas

from United Kingdom

Joined: 08 Sep 2005
Posts: 883
Location: Blackpool,
United Kingdom
Thanked: 84 times

PostPosted: Sun Apr 25, 2010 7:35 pm Reply with quote

phone bosch direct ,good boiler just unlucky,bosch will sort it
Back to top
 Alert Moderators
Gasman77

from United Kingdom

Joined: 18 Jan 2009
Posts: 1277
Location: Berkshire,
United Kingdom
Thanked: 143 times

PostPosted: Sun Apr 25, 2010 8:30 pm Reply with quote

A air lock would A: be very unlikely on a sealed system B: allow your heating to work and not your hot water.

i'd be asking your installer to look at working pressure and air/gas mix although this should have been done during the comissioning......

If you're getting an EA fault on HW only, I'd be suprised if its a boiler fault, more likely a installation fault such as under sized gas pipe or not set up properly.

What diameter is the gas supply and how far from the meter? how many bends? 37Kw is a fair sized combi but a good un, i have one icon_biggrin.gif
Back to top
 Alert Moderators
simond

from United Kingdom

Joined: 26 Oct 2004
Posts: 4066
Location: Surrey,
United Kingdom
Thanked: 272 times

PostPosted: Sun Apr 25, 2010 8:50 pm Reply with quote

Yes I vote for undersized gas pipe, partially closed ECV, or duff regulator on the meter.

Your installer may have checked for these issues by measuring the working pressure at the boiler when it is in engineer or HW mode. If not, that would be where to start.

NB: if they haven't shown any desire to call out the manufacturer themselves you can bet the gas pipe is under par.
Back to top
 Alert Moderators
twgas

from United Kingdom

Joined: 26 Oct 2007
Posts: 4706
Location: Kent,
United Kingdom
Thanked: 391 times

PostPosted: Mon Apr 26, 2010 7:48 am Reply with quote

Quote:
If we "Advance" the central heating clock (ie turn CH on) then boiler goes through a slow start warm-up (-!!- and XX (temp) alternate)
This says to me it may be wired wrongly as you should only get
-||- after the power supply has been reinstated after isolation.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52031
Location: London,
United Kingdom
Thanked: 3241 times

PostPosted: Mon Apr 26, 2010 7:57 am Reply with quote

I was just about to say the same thing.

It sounds as if he has NOT connected a permanent live correctly and the programmer is interupting the permanent live when it operates so that when it is restored the boiler thinks its a new installation and goes through the fill the condensate trap procedure of running for 20 min at minimum power.

If you call Bosch they may charge if its an installation error as we suspect !

Ask the installing firm to send someone more competent to check the way its been wired. If you are handy with electronics you may even be able to do that yourself.

Tony
Back to top
 Alert Moderators
RichThompson

from United Kingdom

Joined: 15 Feb 2007
Posts: 54
Location: Derbyshire,
United Kingdom
Thanked: 3 times

PostPosted: Mon Apr 26, 2010 11:35 am Reply with quote

I assume that when you say it works fine in CH mode, then every so often you hear the condensate trap emptying - it fires up for a few seconds and then switches off again. In addition to what's already been suggested, check there are no blockages in the drain pipe from the boiler to the condensate trap. I had that last year with an EA code and numerous parts were replaced before the fault was found. If the pipe to the condensate trap is blocked, or the trap is broken and cant empty, you get a backlog of waste gas vapour that cant escape, this causes a lockout. Does sound like installation error though.
Back to top
 Alert Moderators
Pickup

from United Kingdom

Joined: 28 Oct 2009
Posts: 93
Location: Aberdeen,
United Kingdom
Thanked: 5 times

PostPosted: Mon Apr 26, 2010 4:24 pm Reply with quote

Folks,

Many thanks the supervisor is going out to have a look tomorrow (Tuesday) so hopefully he'll spot something.

The gas supply is 22mm, the pipe run is about 12 metres from meter to boiler and I'd guess there are about 6 (give or take) 90 bends along the route.

From your description I think the condensate trap is working but as we're not there much it's difficult to tell. When I said it works fine I meant that the central heating works (ie rads get hot) and we get hot water too (sorry).

Thanks again.
Back to top
 Alert Moderators
Gasman77

from United Kingdom

Joined: 18 Jan 2009
Posts: 1277
Location: Berkshire,
United Kingdom
Thanked: 143 times

PostPosted: Mon Apr 26, 2010 6:55 pm Reply with quote

I'd guess that your boiler is under gassed. Any other gas appliances?
Back to top
 Alert Moderators
ianniann

from United Kingdom

Joined: 22 Mar 2009
Posts: 535
Location: Manchester,
United Kingdom
Thanked: 74 times

PostPosted: Mon Apr 26, 2010 7:04 pm Reply with quote

That pipework looks a bit borderline for your boiler.
Back to top
 Alert Moderators
Gasman77

from United Kingdom

Joined: 18 Jan 2009
Posts: 1277
Location: Berkshire,
United Kingdom
Thanked: 143 times

PostPosted: Mon Apr 26, 2010 7:05 pm Reply with quote

copycat icon_lol.gif
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52031
Location: London,
United Kingdom
Thanked: 3241 times

PostPosted: Mon Apr 26, 2010 10:53 pm Reply with quote

There seem to be two faults.

The apparent lack of ignition seems to me to be more likely to be as a result of a sticking regulator than an undersized gas pipe.

Its easy for a competent gas engineer to test for both though.

Tony
Back to top
 Alert Moderators
Pickup

from United Kingdom

Joined: 28 Oct 2009
Posts: 93
Location: Aberdeen,
United Kingdom
Thanked: 5 times

PostPosted: Thu May 06, 2010 9:05 pm Reply with quote

Sorry for the delay in updating everyone...

The supervisor eventually came out, and "fixed" the boiler (I was told it the pressure hadn't been set correctly at the boiler, and my partner was told it was water in the burner). Anyway when we tried running some hot water it ... FAILED with error EA icon_rolleyes.gif .

The Bosch engineer came out, unfortunately not on the day they originally arranged and as we couldn't get any more time off the plumber had to let him in.

Got a message saying it was a "faulty gas meter regulator and get BG out to replace the meter". Supply pressure was dropping to 3milli bars (?) when the hot water was turned on.

Transco came out and replaced the regulator(?) at the meter and the system now works.

Call me cycnical (amongst other things) but since the Transco guy replaced the meter part without checking anything (and we didn't get the opportunity to try the boiler before he arrived) isn't it a of a coincidence
that the boiler started working after the Bosch engineer visited and and that it took more than 7 visits to spot the "faulty" gas meter?

Now we wait with bated breath for the bill...

THANKS to all for their assistance.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52031
Location: London,
United Kingdom
Thanked: 3241 times

PostPosted: Thu May 06, 2010 9:41 pm Reply with quote

Tony wrote:


The apparent lack of ignition seems to me to be more likely to be as a result of a sticking regulator than an undersized gas pipe.

Tony


Thats what I said on the 26th April without even being within 300 miles of the boiler!
Back to top
 Alert Moderators
Pickup

from United Kingdom

Joined: 28 Oct 2009
Posts: 93
Location: Aberdeen,
United Kingdom
Thanked: 5 times

PostPosted: Thu May 06, 2010 10:24 pm Reply with quote

Hi Tony,

I'll gladly buy you a beer (or 5 icon_lol.gif) rather than pay their bill!!

We're (my good lady wife and I ) still debating the "long established local firm with a good reputation" question not to mention how much we should ask off their bill for the hassle (and the water stain in the newly painted ceiling).

THANKS again!
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
worcester greenstar 28 he plus Fault Code C1 7 11960 Mon Jan 01, 2007 11:57 am
Worcester Bosch ZWBR 7-28 HE PLUS - Fault Code C1 11 2760 Mon Aug 20, 2007 7:31 pm
Worcester Greenstar 42cdi - Weird Error Code for Heating 3 2540 Tue Dec 22, 2009 11:56 am
Code C6 Worcester Greenstar 5 4040 Sun Oct 04, 2009 1:05 pm
Worcester Bosch combi boiler error code 3 640 Thu Oct 07, 2010 10:52 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.