what is the difference between a 3 port valve & a mid position motorised valve?
Can one be replaced with the other?
If not why not?
Cheers |
|
Mr Smyth

Joined: 26 Nov 2005 Posts: 272 Location: Surrey, United Kingdom Thanked: 25 times
|
Posted: Mon Apr 26, 2010 12:24 pm |
|
|
A 3-Port valve lets you select HW or Htg whereas a mid position valve lets you select HW, Htg or both HW and Htg.
Yes you can change a 3-Port to a mid position valve but there will be some simple changes to your wiring.
Hope this helps |
|
45yearsagasman

Joined: 14 Mar 2010 Posts: 4176 Location: Norfolk, United Kingdom Thanked: 696 times
|
Posted: Mon Apr 26, 2010 12:32 pm |
|
|
Both of these have "3 Ports" ie inlet port and hw and heating outlet ports.
A mid position valve is able to allow water to flow to HW only,CH only and to both at once by holding the valve in the Mid Position,These valves normally have 5 wires. A 3 port diverter normally has 3 wires and can only supply CH on its own or HW on its own but not both together.These valves as such are interchangeable with some wiring alterations. |
|
angelf

Joined: 07 Jun 2006 Posts: 235 Location: Kent, United Kingdom
|
Posted: Mon Apr 26, 2010 7:31 pm |
|
|
thanks Mr Smyth & 45 year gas man |
|