DIYnot
Local | Network
   DIYnot > Forums
Local | Network
Portable 230/240v power
Author Message
Pyromaniac
from United Kingdom
Thanked: 1 time
PostPosted: Fri Apr 30, 2010 9:10 am Reply with quote
I am guessing this is best put here as it involves 230/240 v supplies.
I have a 3000w output generator of no name (old- no stickers or stamps) which has 2 connections on it as the builders use - the round style sockets.
1 x 110v and 1 x 230v
I want this to feed 230v to the back of my van to power key cutting machines and one tool battery charger.
Effectively I want 3 x household type sockets installed into my van.
I have no cables for this generator, and I also want the option of powering these sockets from a customers mains supply via an extension cable.
How would I best acheive this without electrocuting myself or anyone else who is nearby and without inadvertently making my van 'live' ?
There is an earth attachment point on the generator to which I assume a spike is attached to insert into the ground, but of little use on tarmac, but on tarmac I should be in reach of a mains supply via extension lead to my sockets.
Is there a safe way of connecting the generator to 3 x sockets
Is there a safe way of connecting external mains to 3 x sockets
That I can change around as required.
I dont want to have cables with exposed live from generator or extension leads to plug into something to power my sockets, as I can see this being an accident waiting to happen. And I guess I will need some type of protective device between me and the incoming connection.
Gerry
Back to top
 Alert Moderators
Pyromaniac
from United Kingdom
Thanked: 1 time
PostPosted: Fri Apr 30, 2010 9:57 am Reply with quote
Back to top
 Alert Moderators
ricicle
from United Kingdom
Thanked: 377 times
PostPosted: Fri Apr 30, 2010 10:02 am Reply with quote
Your best option would be to have one single socket off the generator and run one appliance at a time. This would provide electrical isolation and does away with the need for an earth spike so you can use the genny anywhere.
Back to top
 Alert Moderators
bongos
from United Kingdom
Thanked: 78 times
PostPosted: Fri Apr 30, 2010 10:07 am Reply with quote
You could try something like this if you wanted to plug the extension you linked to into a house. This would limit your extension to 13A.
I think ricicles idea sounds better!
Back to top
 Alert Moderators
ericmark
from United Kingdom
Thanked: 690 times
PostPosted: Fri Apr 30, 2010 11:15 am Reply with quote
As already pointed out the scenario is similar to people with tents or caravans and I would expect similar methods will allow safe operation.
So in van you need say three sockets and these will either plug into house or generator.
First the house since you can't be certain that the house already has a RCD then I would use a RCD plug and this will reduce any problems to within an acceptable level.
The generator needs earthing to the van. It will come under section 717 of BS7671:2008
this again shows 7e if required see below:-
Key to Figures 717.1 to 4
1a Connection of the unit to a supply through a transformer with simple separation
1 b Connection of the unit to a supply in which the protective measures are effective
1c Connection to an LV generator set in accordance with Section 551
2 Class II or equivalent enclosure up to the first protective device providing automatic disconnection of supply
6 Socket-outlets for use exclusively within the unit
7 Main equipotential bonding in accordance with Regulation 717.411.3.1.2 7a to an antenna pole, if any
7c to a functional earth electrode, if required
7d to the conductive enclosure of the unit
7e to an earth electrode for protective purposes, if required
8 Protective devices, if required, for overcurrent and/or for protection by disconnection of supply in case of a second fault
10 Socket-outlets for current-using equipment for use outside the unit
13 Current-using equipment for use exclusively within the unit
14 Overcurrent protective device, if required 14a Overcurrent protective device, if required
15 Overcurrent protective device
16a RCD having the characteristics specified in Regulation 415.1.1 for protection by automatic disconnection of supply for circuits of equipment for use outside the unit
16b RCD for protection by automatic disconnection of supply for circuits of equipment for use inside the unit
18 Main earthing terminal or bar
I would say normally an earth is not required is generator is close to your van only if you have it away from van do you really need an earth. I would myself have a steel cable which will bolt onto generator and van so it forms both earth between the two and anti-theft device. Electric wise 4mm earth wire is enough.
There are 4 pages of regulations just for vans like you are using can't really cut and paste all on here.
Back to top
 Alert Moderators
Pyromaniac
from United Kingdom
Thanked: 1 time
PostPosted: Fri Apr 30, 2010 1:35 pm Reply with quote
So I cant just buy the above 3 socket kit, fit a blue socket to an extension lead and use that to use a customers electricity supply ?
Ref generator earthing - how does any current go to ground if you earth it to the van ?
Or is this working the opposite way - genny supplies something inside the van which has a fault - so the earth link to the generator carries current from the van > generator > earth ?
Back to top
 Alert Moderators
Page 1 of 1
Jump to:
240v portable generator - industrial socket to domestic? 10 200 Thu Oct 24, 2013 4:38 pm
Portable appliance testing 22 840 Thu Jan 24, 2013 10:25 pm
Where/how to plug in my portable hot tub? 58 5400 Wed Jun 16, 2010 2:02 pm
Martindale Easy PAT 2100 Portable Appliance Tester 5 120 Tue Oct 04, 2011 1:45 pm
Sizing Portable transformer for operating US 110V tools 31 720 Tue Jun 10, 2014 8:56 am
DIYnot
Please read our Privacy Policy. Copyright © 2000-2015 DIYnot Limited.