PostPosted: Tue Mar 08, 2005 1:25 pm    Post Subject:
door heaters
Reply with quote Thanks

hi there,
i\\\'m installing 4 over door heaters, 65 metres away from the board, drawing 24 amps each, 6000W each. according to the information on your site, a 4mm2 cable would do the job for each of them, this doesn\\\'t take in consideration the voltage drop on such long a run. any suggestions?
Cheers.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4538
Location: United Kingdom
Thanked: 10 times

PostPosted: Tue Mar 08, 2005 3:10 pm    Post Subject:
Reply with quote Thanks

You will need to use 10mm cable to keep the volt drop below 4%
Back to top
 Alert Moderators
Lectrician

from United Kingdom

Joined: 18 Jul 2004
Posts: 5166
Location: Devon,
United Kingdom
Thanked: 20 times

PostPosted: Tue Mar 08, 2005 5:40 pm    Post Subject:
Reply with quote Thanks

And what is the supply arrangements?? 3 phase I hope?? What other loading is there on site?? You wil have 48amps on atleast one phase with just those heaters!


Last edited by Lectrician on Wed Mar 09, 2005 7:49 am, edited 1 time in total
Back to top
 Alert Moderators
theshogun

from United Kingdom

Joined: 25 Feb 2005
Posts: 102
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Mar 08, 2005 11:31 pm    Post Subject:
Reply with quote Thanks

4 x24amps =96amps

Thats a lot of load for one phase.
Back to top
 Alert Moderators
Damocles

from United Kingdom

Joined: 14 Sep 2004
Posts: 1291
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 09, 2005 12:34 am    Post Subject:
Reply with quote Thanks

Some might say that was a problem for the generating company. More immediately it would be a lot of load if you only have a single phase 100A supply at the moment.

__________________
His vorpal blade went snicker-snack
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Mar 09, 2005 1:01 am    Post Subject:
Re: door heaters
Reply with quote Thanks

ollie le roux wrote:
i\\\'m installing 4 over door heaters, drawing 24 amps each, 6000W each.. any suggestions?

Yes - ask your customer if he's heard of global warming, and ask him WTF he thinks he's doing installing 24kW of over-door heating.

Tell him that he may not have a social conscience, may not give a stuff about the environment, but you do, and you aren't going to do the job.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
swelec

from United Kingdom

Joined: 12 Sep 2004
Posts: 444
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 09, 2005 7:03 am    Post Subject:
Reply with quote Thanks

googled oven door heaters

nothing came up

what are they ?

( please don't tell me they are heaters for oven doors icon_biggrin.gif icon_biggrin.gif )
Back to top
 Alert Moderators
Lectrician

from United Kingdom

Joined: 18 Jul 2004
Posts: 5166
Location: Devon,
United Kingdom
Thanked: 20 times

PostPosted: Wed Mar 09, 2005 7:48 am    Post Subject:
Reply with quote Thanks

Over, to Oven icon_lol.gif

Warm Air Curtains - Normally in shops.
Back to top
 Alert Moderators
mapj1

from United Kingdom

Joined: 24 Nov 2004
Posts: 1040
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 09, 2005 11:16 am    Post Subject:
Reply with quote Thanks

Don't forget that the 4% voltage drop is guideline when the maker does not specify otherwise, and supply conditions are unknown, and is certainly correct thinking for socket ciruits where anything may be plugged in.
If however the heaters are rated for example 230v+/-10%, (207V-253V)then a drop greater than 4% would be acceptable, as there is no risk of any other load being applied, and the heaters would be perfectly happy. Most heater type appliences can tolerate a much greater voltage variation than the 4%, particularly those made for the 220V continent originally.
I assume its a big shop, like a multi-level department store, as the leccy bill will be quite high- I presume they know this.

regards M.
PS cable drop calculator on the TLC website.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Mar 09, 2005 6:49 pm    Post Subject:
Reply with quote Thanks

Lectrician wrote:
Warm Air Curtains - Normally in shops.

And a more obscene example of unnecessary energy use, this side of patio heaters, it it hard to imagine.

Our grandchildren will not thank us for this sort of thing.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
swelec

from United Kingdom

Joined: 12 Sep 2004
Posts: 444
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 09, 2005 8:15 pm    Post Subject:
Reply with quote Thanks

swelec wrote:
googled oven door heaters

nothing came up

what are they ?

( please don't tell me they are heaters for oven doors icon_biggrin.gif icon_biggrin.gif )



I'm really not a morning person

Air curtains - right I know them



icon_redface.gif icon_redface.gif icon_redface.gif
Back to top
 Alert Moderators
amtomo999

from United Kingdom

Joined: 13 Mar 2005
Posts: 1
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Mar 13, 2005 7:10 pm    Post Subject:
Door Heaters
Reply with quote Thanks

Further to reply from mapj1, I agree with your comments, we sometimes get a bit hung up with volt drop.

More important is the safety aspect. The cable should be sized relative to the fuse or MCB rating.

The choice of cable to be such that the resistance (R1+R2) is low enough (combined with the Ze - external earth loop impedance), that in the event of a short circuit or earth fault the fuse will blow (MCB will trip) fast enough to prevent injury.

If an RCD (30mA tripping current) is installed this condition is not really an issue as Max impedance to be less than 50Volts/0.03Amps=1667ohms.

Remember other issues,
-grouping with other cables
-running cables in insulation
-use of rewirable fuses
-method of insulation

Sorry to get a bit techy but safety is important.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
fitting outside light from in door switch 7 1700 Mon Nov 19, 2007 7:05 pm
Front Door light: PIR and CFLs 6 440 Wed Nov 07, 2007 9:15 pm
Door Bell - Fault finding with multimeter 4 460 Tue Dec 18, 2007 11:45 pm
fitting downlights over the garage door 7 400 Sat Jan 12, 2008 7:39 pm
Door bell transformer 2 300 Sat May 31, 2008 8:28 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.