Joined: 08 Mar 2005 Posts: 1 Location: United Kingdom Thanked: 0 times
Posted: Tue Mar 08, 2005 1:25 pm Post Subject:
door heaters
hi there,
i\\\'m installing 4 over door heaters, 65 metres away from the board, drawing 24 amps each, 6000W each. according to the information on your site, a 4mm2 cable would do the job for each of them, this doesn\\\'t take in consideration the voltage drop on such long a run. any suggestions?
Cheers.
Joined: 18 Jul 2004 Posts: 5166 Location: Devon, United Kingdom Thanked: 20 times
Posted: Tue Mar 08, 2005 5:40 pm Post Subject:
And what is the supply arrangements?? 3 phase I hope?? What other loading is there on site?? You wil have 48amps on atleast one phase with just those heaters!
Last edited by Lectrician on Wed Mar 09, 2005 7:49 am, edited 1 time in total
Joined: 14 Sep 2004 Posts: 1291 Location: United Kingdom Thanked: 0 times
Posted: Wed Mar 09, 2005 12:34 am Post Subject:
Some might say that was a problem for the generating company. More immediately it would be a lot of load if you only have a single phase 100A supply at the moment.
__________________ His vorpal blade went snicker-snack
Joined: 24 Nov 2004 Posts: 1040 Location: United Kingdom Thanked: 0 times
Posted: Wed Mar 09, 2005 11:16 am Post Subject:
Don't forget that the 4% voltage drop is guideline when the maker does not specify otherwise, and supply conditions are unknown, and is certainly correct thinking for socket ciruits where anything may be plugged in.
If however the heaters are rated for example 230v+/-10%, (207V-253V)then a drop greater than 4% would be acceptable, as there is no risk of any other load being applied, and the heaters would be perfectly happy. Most heater type appliences can tolerate a much greater voltage variation than the 4%, particularly those made for the 220V continent originally.
I assume its a big shop, like a multi-level department store, as the leccy bill will be quite high- I presume they know this.
regards M.
PS cable drop calculator on the TLC website.
Joined: 13 Mar 2005 Posts: 1 Location: United Kingdom Thanked: 0 times
Posted: Sun Mar 13, 2005 7:10 pm Post Subject:
Door Heaters
Further to reply from mapj1, I agree with your comments, we sometimes get a bit hung up with volt drop.
More important is the safety aspect. The cable should be sized relative to the fuse or MCB rating.
The choice of cable to be such that the resistance (R1+R2) is low enough (combined with the Ze - external earth loop impedance), that in the event of a short circuit or earth fault the fuse will blow (MCB will trip) fast enough to prevent injury.
If an RCD (30mA tripping current) is installed this condition is not really an issue as Max impedance to be less than 50Volts/0.03Amps=1667ohms.
Remember other issues,
-grouping with other cables
-running cables in insulation
-use of rewirable fuses
-method of insulation