Isolator Switch for Bathroom Extractor Fan

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
Gaurdian65

from United Kingdom

Joined: 04 May 2010
Posts: 9
Location: London,
United Kingdom

PostPosted: Tue May 04, 2010 5:04 pm Reply with quote

Hi All
Newbie on DIYnot.
Im replacing an extractor fan in the Bathroom with a same brand.
The new fans instructions says that a 3 pole isolator switch should be fitted however, the current fan which worked absolutely fine over several years did not have an isolator switch.
Is an isolator switch a must?
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 12202
Location: Oxfordshire,
United Kingdom
Thanked: 1000 times

PostPosted: Tue May 04, 2010 5:12 pm Reply with quote

Has your bathroom got a window? It is a 100% requirement if there is no window.
Back to top
 Alert Moderators
Gaurdian65

from United Kingdom

Joined: 04 May 2010
Posts: 9
Location: London,
United Kingdom

PostPosted: Tue May 04, 2010 5:24 pm Reply with quote

Taylortwocities wrote:
Has your bathroom got a window? It is a 100% requirement if there is no window.


Yes it does have a window
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 12202
Location: Oxfordshire,
United Kingdom
Thanked: 1000 times

PostPosted: Tue May 04, 2010 5:47 pm Reply with quote

Then there is no regulation that says you MUST have a fan isolator.
It is good practice to fit one though.
Back to top
 Alert Moderators
holmslaw

from Vanuatu

Joined: 12 Dec 2006
Posts: 5844
Location: Vanuatu
Thanked: 400 times

PostPosted: Tue May 04, 2010 6:39 pm Reply with quote

..


Last edited by holmslaw on Mon Apr 02, 2012 7:43 am, edited 1 time in total
Back to top
 Alert Moderators
Gaurdian65

from United Kingdom

Joined: 04 May 2010
Posts: 9
Location: London,
United Kingdom

PostPosted: Wed May 05, 2010 9:41 am Reply with quote

holmslaw wrote:
Seems like TTC has had a few too many sniffs of the bar maids apron.

There absolutely no electrical regulations related to windows , or lack of windows, and fan isolation.

The isolator is required by the regs as a safety device for any one working on the fan.

Also manufacturers instructions override the regs - strange but true.


Thankyou top everyone who responded.
Due to siting of fan and wiring etc can the Isolator switch be placed inside the bathroom near the fan, and if its an issue due to the steam and humidity etc is there a waterproof Isolator switch.
Sorry for sounding a bit dumb but Im trying to establish just how big a job it may become if the Isolator switch has to be sited outside the bathroom.
Back to top
 Alert Moderators
GaryMo

from United Kingdom

Joined: 03 Jul 2007
Posts: 4108
Location: Manchester,
United Kingdom
Thanked: 165 times

PostPosted: Wed May 05, 2010 9:53 am Reply with quote

Where would the isolator be if it was by the fan in relation to the floor and bath/shower? Height from floor and distance from bath/shower

Do the Manufacturers Instructions also state that the fan must be protected by a 1A or 3A fuse?
Back to top
 Alert Moderators
Gaurdian65

from United Kingdom

Joined: 04 May 2010
Posts: 9
Location: London,
United Kingdom

PostPosted: Wed May 05, 2010 10:11 am Reply with quote

GaryMo wrote:
Where would the isolator be if it was by the fan in relation to the floor and bath/shower? Height from floor and distance from bath/shower

Do the Manufacturers Instructions also state that the fan must be protected by a 1A or 3A fuse?


Thankyou.
The Isolator would be a foot away from the fan, and it would be 7 feet from the floor and 4 feet from showerhead.
In the wiring instructions there is a mention of 1 Phase supply 220-240V 50Hz, and the Live feed shows a 1 Amp fuse
Back to top
 Alert Moderators
GaryMo

from United Kingdom

Joined: 03 Jul 2007
Posts: 4108
Location: Manchester,
United Kingdom
Thanked: 165 times

PostPosted: Wed May 05, 2010 10:18 am Reply with quote

You'll need a fused spur with a 1A fuse to comply with the MI.

You mention 4ft from the shower head? That's around 1220mm.
Measurments are taken from the basin and your fan isolator must be a minimum of 600mm away (2ft).
Back to top
 Alert Moderators
Gaurdian65

from United Kingdom

Joined: 04 May 2010
Posts: 9
Location: London,
United Kingdom

PostPosted: Wed May 05, 2010 10:24 am Reply with quote

GaryMo wrote:
You'll need a fused spur with a 1A fuse to comply with the MI.

You mention 4ft from the shower head? That's around 1220mm.
Measurments are taken from the basin and fan switch must be a minimum of 600mm away (2ft).


Gary Thankyou

I can confirm that the switch will be at least 4 feet from any water source.
the fused spur with 1A which you mentioned, does that act as the Isolator switch or is it in addition to the Isolator switch,and lastly does it have to be waterproof icon_redface.gif
Back to top
 Alert Moderators
GaryMo

from United Kingdom

Joined: 03 Jul 2007
Posts: 4108
Location: Manchester,
United Kingdom
Thanked: 165 times

PostPosted: Wed May 05, 2010 10:28 am Reply with quote

Gaurdian65 wrote:


I can confirm that the switch will be at least 4 feet from any water source.
the fused spur with 1A which you mentioned, does that act as the Isolator switch or is it in addition to the Isolator switch,and lastly does it have to be waterproof icon_redface.gif


It probably does as you mention a 3 pole isolator but just checking - does this fan have an over-run timer? ie it runs for 10 mins or so after the light has been turned off?

If it does, how is it currently wired? One single 3 core and earth cable originating from the light fitting?

If the isolator is more than 600mm from the edge of the shower base then it doesn't need any special protection.
Back to top
 Alert Moderators
Gaurdian65

from United Kingdom

Joined: 04 May 2010
Posts: 9
Location: London,
United Kingdom

PostPosted: Wed May 05, 2010 10:45 am Reply with quote

GaryMo wrote:
Gaurdian65 wrote:


I can confirm that the switch will be at least 4 feet from any water source.
the fused spur with 1A which you mentioned, does that act as the Isolator switch or is it in addition to the Isolator switch,and lastly does it have to be waterproof icon_redface.gif


It probably does as you mention a 3 pole isolator but just checking - does this fan have an over-run timer? ie it runs for 10 mins or so after the light has been turned off?

If it does, how is it currently wired? One single 3 core and earth cable originating from the light fitting?

If the isolator is more than 600mm from the edge of the shower base then it doesn't need any special protection.


Thankyou Garymo
1.It is a new fan which has not been fitted yet.
2.The previous fan was wired in without earth or an Isolator switch.
3.The new fan is double insulated and must NOT be earthed (per instructions)
4.The new fan has a timer set at 15mins after it is switched off.
5.yes it will be more than 600mm away from any wet source bar any steam etc.
Back to top
 Alert Moderators
GaryMo

from United Kingdom

Joined: 03 Jul 2007
Posts: 4108
Location: Manchester,
United Kingdom
Thanked: 165 times

PostPosted: Wed May 05, 2010 10:51 am Reply with quote

You'll still use a 3 core and earth cable to supply the fan but terminate the earch (cpc) in a small connector block.

Have you got an accessible loft over the bath/shower room? If so, are you against surface mounted backboxes at high level outside your bath/shower room door, on the landing? If you want a neater option then you'll need to consider chasing into the wall.
Back to top
 Alert Moderators
Gaurdian65

from United Kingdom

Joined: 04 May 2010
Posts: 9
Location: London,
United Kingdom

PostPosted: Wed May 05, 2010 11:11 am Reply with quote

GaryMo wrote:
You'll still use a 3 core and earth cable to supply the fan but terminate the earch (cpc) in a small connector block.

Have you got an accessible loft over the bath/shower room? If so, are you against surface mounted backboxes at high level outside your bath/shower room door, on the landing? If you want a neater option then you'll need to consider chasing into the wall.


Thankyou Garymo
No accessible loft as its an extension to the House.
Im happy to have it surface mounted in the Bathroom at least 3ft+ away from any wet source.
To recap:
1A fused spur will act as Isolating switch and can be sited inside the bathroom as long as its 600mm min away from shower/water sources etc.
A waterproof switch would be ideal but not an absolute must as long as it is safe distance as you mentioned min 600mm.
If this is correct then I'll give the go ahead. icon_rolleyes.gif
Back to top
 Alert Moderators
GaryMo

from United Kingdom

Joined: 03 Jul 2007
Posts: 4108
Location: Manchester,
United Kingdom
Thanked: 165 times

PostPosted: Wed May 05, 2010 11:20 am Reply with quote

It's not going to be so simple but it's very acheivable. You're going to have to create more damage than you probably wished for though.

You've got a permanant line, a switched line and a neutral.
A FCU is double pole, meaning it can only isolate two poles, normally permanant line and neutral. Your switched line will still be live.

Have a look at the wiring diagram which came with the fan and you'll see that the 1A fuse is situated before the swiched line comes into play so that it's protecting both the permanant and switched lines.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
shower extractor fan isolator switch 4 820 Wed Mar 21, 2012 7:57 pm
3 pole isolator switch for extractor fan 10 240 Thu Feb 16, 2012 3:30 pm
Extractor Fan - FCU or Isolator Switch or Both? 19 1500 Thu Sep 11, 2008 6:09 am
Extractor Fan - Isolator Switch?!? 3 1180 Tue Sep 04, 2007 2:32 pm
Extractor Fan Isolator Switch???? 75 1760 Sun Jan 20, 2013 9:41 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.