i wonder if someone can help,the service head fuse is 60amp,does this dictate what size switch i need in a new CU i.e.100amp DP isolator or 80amp RCD, because someone told me it has to be the same value as the service head fuse.And that didnt sound right to me,but i may stand corrected.Some advice would be greatly appreiciated!!!
 
Sponsored Links
Use a 100amp switch. the main fuse can be smaller than the switch, but not the other way round - ask them for a free supply fuse upgrade perhaps.
 