i wonder if someone can help,the service head fuse is 60amp,does this dictate what size switch i need in a new CU i.e.100amp DP isolator or 80amp RCD, because someone told me it has to be the same value as the service head fuse.And that didnt sound right to me,but i may stand corrected.Some advice would be greatly appreiciated!!! |
|
kai

Joined: 15 Aug 2004 Posts: 729 Location: United Kingdom Thanked: 5 times
|
Posted: Wed Mar 09, 2005 12:42 pm Post Subject: Use 100amp switch. |
 |
|
Use a 100amp switch. the main fuse can be smaller than the switch, but not the other way round - ask them for a free supply fuse upgrade perhaps. |
|