Okay today, end of, Connected from the henley blocks to 80A fused switch to supply a C.U. via 16mm SWA.

Ze was 0.14 NICE!!

IR between L,N, E were all >299MOhm

between armour and L,N,E all >299MOhm.

Decided to measure V approx 243V

Then decided to check Voltage L,N L,E N,E and L,Armour N, Armour E,Armour

L,Armour as expected

N,Armour and E, Armour 27Volts!!!!!

What had the silly boy done????
 
Sponsored Links
Not bonded the armour to earth?

How else could you measure a potential difference between the armour and earth?
 
You need a cardboard cut-out electrician with you. Explain to him what you've done and you'll find the fault a lot quicker.
 
Sponsored Links
Sometimes it's the simple things that trip you up.

At least you identified and rectified? It.
 
Working too quickly, taking mobile phone calls, chatting to customer ?

Safe and methodical. A tea break mid morn and mid afternoon is the distraction time. Lunch time being the point where you work out how long the afternoon will take :D
 
I think it was a lack of 'Fag and a Brew' so that progress review never happened, oh and the fact the plumber/plaster just cannot stop talking!!
 