PostPosted: Sat May 15, 2010 10:17 am Reply with quote
icon_confused.gif Hi
I need to change my MCB B32 to MCB B40 for a new shower.
The C/U is around 12 years old.
Will any make of MCB fit my Crabtree Star Breaker C/U ?
For instance the BusBar?
Many thanks.
Stephen
Back to top
 Alert Moderators
ban-all-sheds
from United Kingdom
Thanked: 1870 times
PostPosted: Sat May 15, 2010 10:25 am Reply with quote
  1. What size cable is it?
  2. Do you know what its current carrying capacity is given how it is installed?
  3. How will you verify that its R1+R2 is OK for a breaker of increased rating?
  4. Is the circuit RCD protected?
  5. electrics:part_p
No. Ones other than the originals might fit, but it is absolutely not the case that any and all will fit.
Back to top
 Alert Moderators
zappastix
from United Kingdom
Thanked: 2 times
PostPosted: Sat May 15, 2010 11:28 am Reply with quote
Thanks ban-all-sheds.
I just wanted to know if there are any physical differences between MCB's (B rated).
This is because I have a long journey to ScrewFix/B & Q and don't want to find out there are differences and a different brand would not fit.
I wanted to get he job done this weekend. If I have to order online then I'll do that.
In answer to your concerns;
I've spent hours looking into this.
The cable is 6mm.
6mm twin and earth cable is rated at 47 Amps at best. At 240V (real, not nominal).
The old shower was 8.5kW.
The MCB for the old shower is B32.
We have lived here for 7 years and the shower has never tripped.
90% of the cable is in an airy/large loft.
Showers up to 8.5kw may carry a 6mm cable as long as the shower unit is within 18 meters of the fuseboard. Fuses and switches should be rated at 40 amps.
It is because it seems the person who fitted the MCB for the shower didn't seems to fit the correct rating MCB, is why I want to change this for B40.
In saying this - maybe Regs years ago were different.
My electric oven is on a MCB B32 running on 6mm cable - no problem there.
Thanks.
Back to top
 Alert Moderators
ban-all-sheds
from United Kingdom
Thanked: 1870 times
PostPosted: Sat May 15, 2010 12:43 pm Reply with quote
There are.
And 23.5A at worst.
The other 10%?
Back to top
 Alert Moderators
Taylortwocities
from United Kingdom
Thanked: 1092 times
PostPosted: Sat May 15, 2010 2:41 pm Reply with quote
Yes, but the oven won't be pulling 32amps and if it did then not for too long as it has thermostats and stuff.
Electric showers are wham 37amp all the time until you turn them off devices so overloads and tripping of mcbs are likely unless the circuit is designed properly.
What is the R1+R2 for the 6mm circuit?
Back to top
 Alert Moderators
STI
from United Kingdom
Thanked: 27 times
PostPosted: Sat May 15, 2010 4:08 pm Reply with quote
TTC genuine interest and wanting to learn and understand. If i have understood your last response correctly why does knowing what the R1+R2 is, which i understand is a continuity check between phase and earth, impact/effect/influence the choice of MCB.
Back to top
 Alert Moderators
ban-all-sheds
from United Kingdom
Thanked: 1870 times
PostPosted: Sat May 15, 2010 4:13 pm Reply with quote
Because if it is too high a L/E fault will not be cleared quickly enough by the MCB.
http://www.diynot.com/forums/viewtopic.php?p=1602798#1602798
Back to top
The following user says thank you to ban-all-sheds for this useful post:
STI (15 May 2010)
 Alert Moderators
STI
from United Kingdom
Thanked: 27 times
PostPosted: Sat May 15, 2010 4:30 pm Reply with quote
Thanks BAS, I need to read that link in detail to get my head around the inter relationships of the Zs , Ze etc but with this topic example it will make more sense.
Back to top
 Alert Moderators
ban-all-sheds
from United Kingdom
Thanked: 1870 times
PostPosted: Sat May 15, 2010 4:38 pm Reply with quote
Zs = Ze + (R1+R2).
Or Ze + (r1+r2) for a ring final.
Back to top
 Alert Moderators
Spark123
from United Kingdom
Thanked: 415 times
PostPosted: Sat May 15, 2010 5:09 pm Reply with quote
Zs = Ze + (r1+r2)/4 for a ring final circut icon_wink.gif
Back to top
The following user says thank you to Spark123 for this useful post:
STI (15 May 2010)
 Alert Moderators
ban-all-sheds
from United Kingdom
Thanked: 1870 times
PostPosted: Sat May 15, 2010 8:02 pm Reply with quote
Got them the wrong way round.... icon_evil.gif icon_redface.gif icon_cry.gif
Back to top
STI (15 May 2010)
 Alert Moderators
STI
from United Kingdom
Thanked: 27 times
PostPosted: Sat May 15, 2010 8:22 pm Reply with quote
Thanks to both. A further question, if the calculated Zs result is different to the actual measured result, does it signify a problem or is it ok as long as the actual result is within the limits of the tables.
Back to top
 Alert Moderators
Taylortwocities
from United Kingdom
Thanked: 1092 times
PostPosted: Sat May 15, 2010 10:47 pm Reply with quote
Measured and calculated are often slightly different. Its OK as long as within the EFLI limits. And don't forget the rule of thumb.
Back to top
The following user says thank you to Taylortwocities for this useful post:
STI (16 May 2010)
 Alert Moderators
Page 1 of 1
Jump to:
Crabtree SB6000 5 500 Thu Jan 31, 2008 8:31 am
Crabtree MCB compatability 8 860 Sun Jan 20, 2008 7:29 pm
Crabtree MCB 6 780 Thu Nov 29, 2007 6:39 pm
Crabtree Switched FCU has no socket outlet ? 2 440 Tue Aug 14, 2007 3:03 pm
Crabtree C.U. 2 360 Tue Mar 04, 2008 2:06 pm
DIYnot
Please read our Privacy Policy. Copyright © 2000-2015 DIYnot Limited.