Gas flue vent distance from window??

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
rsthomas11

from United Kingdom

Joined: 27 May 2010
Posts: 4
Location: Kent,
United Kingdom

PostPosted: Thu May 27, 2010 9:13 am Reply with quote

I am having a conservatory built and I will have a glazed window (non-opening) near to my boiler's gas flue vent. I'm not sure of exact distance but currently it is 300mm from the centre of the vent to my kitchen window frame. The conservatory will be just outside the window therefore approx. 250mm. The top & other side of the vent is clear and is over the height of my neighbour's fence (i.e. not enclosed any further on any other side, just the one where my new conservatory will be).

I have had two heating engineers to visit and they both seem to unsure of the current regulations which is worrying! Can anyone on here help?!

I have looked into extending the flue upwards but they don't seem to do the correct vertical extension kit for my boiler. If anyone can help with this too I would be grateful. My boiler is a Potterton Suprima 30 (standard efficiency) installed in 1998.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Axel

from United Kingdom

Joined: 21 Sep 2008
Posts: 936
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu May 27, 2010 9:38 am Reply with quote

Back to top
The following user says thank you to Axel for this useful post:
rsthomas11 (28 May 2010)
 Alert Moderators
Richard C

from United Kingdom

Joined: 26 Apr 2005
Posts: 10589
Location: United Kingdom
Thanked: 990 times

PostPosted: Thu May 27, 2010 9:48 am Reply with quote

rsthomas11 wrote:

I have had two heating engineers to visit and they both seem to unsure of the current regulations which is worrying!

That seems rather worrying are they bon fide Gas Safe registered?

See page 42/43 here;
http://www.planningportal.gov.uk/uploads/br/BR_PDF_ADJ_2002.pdf
New edition applies from October 2010.
Back to top
The following user says thank you to Richard C for this useful post:
rsthomas11 (28 May 2010)
 Alert Moderators
Richard C

from United Kingdom

Joined: 26 Apr 2005
Posts: 10589
Location: United Kingdom
Thanked: 990 times

PostPosted: Thu May 27, 2010 9:49 am Reply with quote

Sorry Axel didn't check before posting.
Back to top
The following user says thank you to Richard C for this useful post:
rsthomas11 (28 May 2010)
 Alert Moderators
Axel

from United Kingdom

Joined: 21 Sep 2008
Posts: 936
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu May 27, 2010 9:55 am Reply with quote

Fair enough...I was going on the basis that the MI's superseed the BS regulations.

I suppose that presenting a new clearance to a flue could be counted as re-fitting or installing a new flue, in which case the new regs would apply.
Back to top
The following user says thank you to Axel for this useful post:
rsthomas11 (28 May 2010)
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 53343
Location: London,
United Kingdom
Thanked: 3381 times

PostPosted: Thu May 27, 2010 9:56 am Reply with quote

All measurements have to be made form the OUTSIDE of the flue.

So as your flue is within 300mm it is already too close to the window based on the CORGI interpretation which is likely to be continued by Gas Safe that 300mm applies because the window could be replaced with an opening one at any time.

Only condensing boilers can have their outlet gases diverted away from the terminal externally. All others have to be moved internally.

Dont expect flue parts to be readily available for 10 year old boilers.

Tony
Back to top
The following user says thank you to Agile for this useful post:
rsthomas11 (28 May 2010)
 Alert Moderators
rsthomas11

from United Kingdom

Joined: 27 May 2010
Posts: 4
Location: Kent,
United Kingdom

PostPosted: Thu May 27, 2010 10:12 am Reply with quote

Axel wrote:


So would my description above be described as J in the above key - therefore 600mm??
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 53343
Location: London,
United Kingdom
Thanked: 3381 times

PostPosted: Thu May 27, 2010 10:19 am Reply with quote

You have not given details of your neighbours boundary.

The 600mm is the official minimum distance from the centerline of the boundary to the closest part of your flue.

Its not very important in practice as its not normally a gas safety issue, just a matter of not annoying your neighbour.

Tony
Back to top
The following user says thank you to Agile for this useful post:
rsthomas11 (28 May 2010)
 Alert Moderators
kirkgas

from United Kingdom

Joined: 26 Dec 2007
Posts: 4841
Location: Lanarkshire,
United Kingdom
Thanked: 457 times

PostPosted: Thu May 27, 2010 11:37 am Reply with quote

the other thing to consider is the requirement for a flue to be more than 150mm from a fabric opening in a building ie where the window frame meets the building, so the existing flue is well inside the requirements

on this point, how would you classify a room sealed flue too near an opening in a building as per CURRENT edition of IUP
Back to top
The following user says thank you to kirkgas for this useful post:
rsthomas11 (28 May 2010)
 Alert Moderators
simond

from United Kingdom

Joined: 26 Oct 2004
Posts: 4071
Location: Surrey,
United Kingdom
Thanked: 273 times

PostPosted: Thu May 27, 2010 8:07 pm Reply with quote

I think you'll find the diagram posted above by Axel is not for a 1998 Suprima.

Correct me if I'm wrong - I won't fit Poxi Batterton so am not familiar - but I reckon it is a Suprima HE manual, and thus of no relevence to the OP.
Back to top
The following user says thank you to simond for this useful post:
rsthomas11 (28 May 2010)
 Alert Moderators
rsthomas11

from United Kingdom

Joined: 27 May 2010
Posts: 4
Location: Kent,
United Kingdom

PostPosted: Fri May 28, 2010 9:46 am Reply with quote

simond wrote:
I think you'll find the diagram posted above by Axel is not for a 1998 Suprima.

Correct me if I'm wrong - I won't fit Poxi Batterton so am not familiar - but I reckon it is a Suprima HE manual, and thus of no relevence to the OP.


Thanks Simon, I have found the original manual online via the Potterton website and it shows a similar drawing with dimensions. It seems like I only need 25mm (fingers crossed!) gap to an internal/external corner and I am waiting on confirmation from the heating engineer.

Thanks everyone else for your help.
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8763
Location: Sussex,
United Kingdom
Thanked: 1013 times

PostPosted: Fri May 28, 2010 3:46 pm Reply with quote

The OP said:
rsthomas11 wrote:
I am having a conservatory built and I will have a glazed window (non-opening) near to my boiler's gas flue vent.

So the regulations about the distance of the flue from a opening window are irrelevant. It's only the distance from the internal corner formed by the existing wall and the conservatory wall which is relevant.
Back to top
The following user says thank you to D_Hailsham for this useful post:
rsthomas11 (28 May 2010)
 Alert Moderators
rsthomas11

from United Kingdom

Joined: 27 May 2010
Posts: 4
Location: Kent,
United Kingdom

PostPosted: Fri May 28, 2010 4:14 pm Reply with quote

D_Hailsham wrote:
The OP said:
rsthomas11 wrote:
I am having a conservatory built and I will have a glazed window (non-opening) near to my boiler's gas flue vent.

So the regulations about the distance of the flue from a opening window are irrelevant. It's only the distance from the internal corner formed by the existing wall and the conservatory wall which is relevant.


Yes, I don't think I explained myself very well in the opening post (sorry everyone!) but the conservatory is enclosing the existing kitchen window and the new conservatory window pane coming out away from the house adjacent to the flue will be approx. 150-200mm away from the flue. I was worried this would be too close but I think it is covered by the internal/external corner dimensions quoted so therefore I need 25mm gap - which I will have.

Thanks everyone!
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 53343
Location: London,
United Kingdom
Thanked: 3381 times

PostPosted: Fri May 28, 2010 8:43 pm Reply with quote

Be aware that neither the OP nor D Hailsam are gas registered.

They are making up their own intrepretations of the manufacturers instructions.

A conservatory in terms of MI is a window and not a wall.

Whilst I agree that the MI does not cover the OP's situation, its only the manufacturer who should advise when there is no clear information given.

Another aspect often ignored is that the flue can only be fitted in a location where it will not cause any "nuisance".

Tony
Back to top
 Alert Moderators
namsag

from United Kingdom

Joined: 12 May 2004
Posts: 9909
Location: United Kingdom
Thanked: 321 times

PostPosted: Sat May 29, 2010 12:58 am Reply with quote

Whilst D Hailsham or op is not registere they both have a better understanding of the the regs than you Agile
You are certainly a nupty

Scary who is allowed to be ACS registered
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Required distance from boiler flue to window 3 60 Fri Sep 20, 2013 8:18 pm
Safe distance between boiler exhaust flue and bedroom window 4 120 Sat Nov 16, 2013 5:09 pm
Vaillant vertical flue (distance from window) 7 140 Mon Nov 12, 2012 10:52 am
boiler flu-- distance from window 4 940 Fri Oct 24, 2008 6:20 pm
gas fire to window distance? 6 620 Tue Aug 22, 2006 6:45 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.