Hi,
I've recently done a whole house calculation using the energy saving trust's site and some fairly accurate measuring of rooms. The total comes to 33.216 kW, which I believe needs 2kW added for water heating, making approx 35 kW required. My plumber did no measurements or (visible) calculations and specced a 30KW ariston clas HE system boiler. Prior to this I had 2 quotes, both of which recommended a Worcester Greenstar 40CDI boiler.
I also did my own calculations using Stelrad's STARS v3 program which gave a total BTU requirement of 117898 BTU (34.554 kW) (-1degrees outside, MTW set at 65, average room temp 21degrees).
I'm wondering whether I should go with my own calculations and insist on a bigger boiler, or go with what my plumber's specified. I feel like a bit of an armchair expert but I'm getting the feeling my calculations might be better.
The house which needs the new CH system is a detached, 2 storey, solid brick, Victorian property with single glazing at the front, double at the back, high ceilings, 4 Bedrooms, 3 Reception rooms (2 with big bay windows), large hall (with 6m^2 of glazing), 2 bathrooms, 1 ensuite, largish kitchen/diner with french doors and skylights and a utility room. Total floorspace for both floors is around 211m^2.
Insulation wise the house will be draughtproofed, the ground floor will have insulation added between the floor joists, the basement will be insulated, the kitchen is having a solid insulated floor put in.
So, do the energy saving trust's and stelrad calcs sound about right or am I oversizing too much?
Thanks.
I've recently done a whole house calculation using the energy saving trust's site and some fairly accurate measuring of rooms. The total comes to 33.216 kW, which I believe needs 2kW added for water heating, making approx 35 kW required. My plumber did no measurements or (visible) calculations and specced a 30KW ariston clas HE system boiler. Prior to this I had 2 quotes, both of which recommended a Worcester Greenstar 40CDI boiler.
I also did my own calculations using Stelrad's STARS v3 program which gave a total BTU requirement of 117898 BTU (34.554 kW) (-1degrees outside, MTW set at 65, average room temp 21degrees).
I'm wondering whether I should go with my own calculations and insist on a bigger boiler, or go with what my plumber's specified. I feel like a bit of an armchair expert but I'm getting the feeling my calculations might be better.
The house which needs the new CH system is a detached, 2 storey, solid brick, Victorian property with single glazing at the front, double at the back, high ceilings, 4 Bedrooms, 3 Reception rooms (2 with big bay windows), large hall (with 6m^2 of glazing), 2 bathrooms, 1 ensuite, largish kitchen/diner with french doors and skylights and a utility room. Total floorspace for both floors is around 211m^2.
Insulation wise the house will be draughtproofed, the ground floor will have insulation added between the floor joists, the basement will be insulated, the kitchen is having a solid insulated floor put in.
So, do the energy saving trust's and stelrad calcs sound about right or am I oversizing too much?
Thanks.