Potterton over heat thermostat


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
okneedhelpplease

from United Kingdom

Joined: 24 Sep 2008
Posts: 44
Location: Warwickshire,
United Kingdom

PostPosted: Fri Jun 18, 2010 5:58 am Reply with quote

Hi again all i have a potterton performa 24 and the overheat stat keeps clicking out and i have to push the little button in on it to reset. It only happens when the hot water runs but not all the time.

Anyone help please
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
powell30

from United Kingdom

Joined: 29 Jan 2008
Posts: 1214
Location: Birmingham,
United Kingdom
Thanked: 129 times

PostPosted: Fri Jun 18, 2010 7:10 am Reply with quote

It's overheating

Your plate heat ex is most likely sludged or scaled. Clean or replace
Back to top
 Alert Moderators
echoes

from United Kingdom

Joined: 27 Mar 2007
Posts: 956
Location: Surrey,
United Kingdom
Thanked: 108 times

PostPosted: Fri Jun 18, 2010 12:31 pm Reply with quote

I had exactly this problem with a similar Potterton. The clips which should hold the thermostats to the return pipe inside had both bust and the stats were just flapping around inside. Worth checking.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 51898
Location: London,
United Kingdom
Thanked: 3222 times

PostPosted: Fri Jun 18, 2010 12:57 pm Reply with quote

That last post is not logical !

If an overheat stat is not in contact it cannot trip because its not being subjected to the heat in the flow pipe.

The first reply is the one to follow up as its a blocked plate HE.

Tony
Back to top
 Alert Moderators
echoes

from United Kingdom

Joined: 27 Mar 2007
Posts: 956
Location: Surrey,
United Kingdom
Thanked: 108 times

PostPosted: Fri Jun 18, 2010 2:20 pm Reply with quote

Quote:
That last post is not logical !

If an overheat stat is not in contact it cannot trip because its not being subjected to the heat in the flow pipe.

The first reply is the one to follow up as its a blocked plate HE.


The 2 stats not in contact were the control stat on front of boiler and the pump overrun stat. I didn't mention that the overheat stat was attached & functioning (should have done).

So the only stat functioning was the overheat stat.

Logical now?

Sorry for not being clear icon_redface.gif
Back to top
 Alert Moderators
okneedhelpplease

from United Kingdom

Joined: 24 Sep 2008
Posts: 44
Location: Warwickshire,
United Kingdom

PostPosted: Fri Jun 18, 2010 4:23 pm Reply with quote

thank you for all the replys, but please tell me, how do i clean the heat exchanger.
O did i mention it only happens when the hot water is switched off. For example if we shower its fine but when we turn it off it trips
Back to top
 Alert Moderators
petit_pablo

from United Kingdom

Joined: 18 Nov 2007
Posts: 6723
Location: Lincolnshire,
United Kingdom
Thanked: 1045 times

PostPosted: Fri Jun 18, 2010 4:27 pm Reply with quote

echoes wrote:
Quote:
That last post is not logical !

If an overheat stat is not in contact it cannot trip because its not being subjected to the heat in the flow pipe.

The first reply is the one to follow up as its a blocked plate HE.


The 2 stats not in contact were the control stat on front of boiler and the pump overrun stat. I didn't mention that the overheat stat was attached & functioning (should have done).

So the only stat functioning was the overheat stat.

Logical now?

Sorry for not being clear icon_redface.gif

performa doesn't have a pump overrun stat and control stat is connected to board. Thermsistor is screwed into primary flow pipe.
Are you thinking of profile?
Back to top
The following user says thank you to petit_pablo for this useful post:
echoes (21 Jun 2010)
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 51898
Location: London,
United Kingdom
Thanked: 3222 times

PostPosted: Sat Jun 19, 2010 1:42 am Reply with quote

okneedhelpplease wrote:
thank you for all the replys, but please tell me, how do i clean the heat exchanger.

O did i mention it only happens when the hot water is switched off. For example if we shower its fine but when we turn it off it trips


That is a classic description of a primary heat exchanger which is scaled with lime compounds.

It can be cleaned in situ with hot sulphonic acid ( DS3 ) but is messy and has to be done by someone who knows what they are doing.

If it were removed by a gas engineer then it could be cleaned with sulphonic acid or HCl. Again messy and somewhat risky working with acids.

Not what I would recommend as a DIY job !

Tony
Back to top
 Alert Moderators
okneedhelpplease

from United Kingdom

Joined: 24 Sep 2008
Posts: 44
Location: Warwickshire,
United Kingdom

PostPosted: Sat Jun 19, 2010 5:42 am Reply with quote

thank you all
Back to top
 Alert Moderators
echoes

from United Kingdom

Joined: 27 Mar 2007
Posts: 956
Location: Surrey,
United Kingdom
Thanked: 108 times

PostPosted: Mon Jun 21, 2010 9:34 am Reply with quote

Quote:
performa doesn't have a pump overrun stat and control stat is connected to board. Thermsistor is screwed into primary flow pipe.
Are you thinking of profile?


Yes petit_pablo, you are spot on - mine was a profile. Thought it was worth a quick post just in case the OP's control stat sensor had become unattached, but thanks for putting me right.
Good that Potterton ditched the flimsy clips in favour of screws
Back to top
 Alert Moderators
Andygasman2010

from United Kingdom

Joined: 03 Mar 2010
Posts: 2176
Location: Middlesbrough,
United Kingdom
Thanked: 202 times

PostPosted: Mon Jun 21, 2010 9:50 pm Reply with quote

Ahh the confusion! Performa and profile are very different boilers. If it's tripping after the hot water has satisfied then i'd look at the pump overrun facility or the bypass on the system.

Check that when demand ends the pump continues to run.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Over Heat Thermostat on Worcester 240BF 5 340 Mon Jun 16, 2008 5:17 pm
Room thermostat not switching off heat 4 120 Mon Sep 16, 2013 7:18 am
Thermostat Not calling for heat? 3 280 Thu Feb 21, 2008 8:55 pm
Cannot get boiler/timer/thermostat set up to only heat water 4 60 Sat Apr 27, 2013 2:05 pm
Thermostat calling for heat, heating not coming on...... 3 340 Fri Jan 29, 2010 10:34 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.