wiring problem s plan


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
terence7556

from United Kingdom

Joined: 25 Mar 2008
Posts: 1801
Location: Staffordshire,
United Kingdom
Thanked: 259 times

PostPosted: Fri Aug 06, 2010 7:22 pm Reply with quote

im having trouble with using the s plan in the honeywell book, page 2, sundial s plan. i have a fused spur under the boiler, 240v on the supply side direct from the ccu and on the load side a twin &earth to the wiring centre and also a short length of flex into the boiler 500mm above.
on the wiring diagram the lower right hand box is a t&e from the boiler with a live to no10 and the neutral and earth to 2 and 3 .
i do not have a cable from the boiler to the wiring centre to accomadate this, what can i do? (short of running one in )
the boiler is an ideal classic 270 ff,programmer is a siemens RWB 29Si,wilo gold 15/60 set on 2,acl CH valve, Drayton dhw valve, honeywell cylinder stat and room stat
Problem and reason for adaption?
boiler was random firing when heat or dhw not required or asked for. as far as i can tell 5/6 times a day ,firing up for approx. 60 seconds. the 28mm pipe above the pump and the dhw valve always appear to be hot to touch, ch valve always cold, so i suspect this external control to be playing up. the original wiring centre was a group of mixed size connector blocks all shoved in a twin box and i bought a honeywell 10 way block to tidy it up but i am having a bit of bother re wiring it
any advice please and thanks for putting up with the long post
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
twgas

from United Kingdom

Joined: 26 Oct 2007
Posts: 4775
Location: Kent,
United Kingdom
Thanked: 405 times

PostPosted: Fri Aug 06, 2010 7:42 pm Reply with quote

it's usual to have the wiring centre (junction box) in the airing cupboard next to the cylinder, valves and pump. All the wires ought to go to the wiring centre, it makes life much easier, especially for the not-so-competent.
I'm a little confused with the wire to the boiler - where does it come from?
Back to top
 Alert Moderators
kevindgas

from United Kingdom

Joined: 28 Mar 2006
Posts: 5691
Location: Southampton,
United Kingdom
Thanked: 467 times

PostPosted: Fri Aug 06, 2010 7:45 pm Reply with quote

Back to top
The following user says thank you to kevindgas for this useful post:
terence7556 (6 Aug 2010)
 Alert Moderators
terence7556

from United Kingdom

Joined: 25 Mar 2008
Posts: 1801
Location: Staffordshire,
United Kingdom
Thanked: 259 times

PostPosted: Fri Aug 06, 2010 7:52 pm Reply with quote

sorry tw did,nt make it clear the wiring centre is in the airing cupboard as expected.this is my problem, i have a supply from the fused spur to the w.c. but not one from the boiler to the w.c. taking the live conductor to no 10 in the w.c.
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8676
Location: Sussex,
United Kingdom
Thanked: 998 times

PostPosted: Fri Aug 06, 2010 8:55 pm Reply with quote

terence7556 wrote:
i have a fused spur under the boiler, 240v on the supply side direct from the ccu and on the load side a twin &earth to the wiring centre

OK, so far.

Quote:
also a short length of flex into the boiler 500mm above.

Does this come straight from the fused spur? If which terminals does it connect to in the boiler

Quote:
I do not have a cable from the boiler to the wiring centre to accommodate this, what can I do? (short of running one in )

That's probably the cause of your original problem.

You need to find out exactly what the flex to the boiler is doing.
Back to top
 Alert Moderators
terence7556

from United Kingdom

Joined: 25 Mar 2008
Posts: 1801
Location: Staffordshire,
United Kingdom
Thanked: 259 times

PostPosted: Fri Aug 06, 2010 9:22 pm Reply with quote

hi mr hailsham the flex is direct from the fused spur and the other end is the mains plug which connects to the rear r/h side of the p.c.b.
Back to top
 Alert Moderators
terence7556

from United Kingdom

Joined: 25 Mar 2008
Posts: 1801
Location: Staffordshire,
United Kingdom
Thanked: 259 times

PostPosted: Fri Aug 06, 2010 9:25 pm Reply with quote

the phrase "mains plug " is from page 20 item 38 pictorial wiring in the m.i.s and the brown goes in and out of the o/h stat, then on to the on/off switch.the neutral goes direct to the on/off switch and the earth goes straight to the earth connection in the boiler.
Back to top
 Alert Moderators
D_Hailsham

from United Kingdom

Joined: 18 Oct 2007
Posts: 8676
Location: Sussex,
United Kingdom
Thanked: 998 times

PostPosted: Sat Aug 07, 2010 11:02 am Reply with quote

terence7556 wrote:
hi mr hailsham the flex is direct from the fused spur and the other end is the mains plug which connects to the rear r/h side of the p.c.b.

So the boiler will run 24/7, controlled by the boiler thermostat and the overheat thermostat. All the programmer, cylinder stat and wall stat are doing is to control when the motorized valves open and close.

You need to run a 3 core cable from the wiring centre (L=10, N=2, E=3) to the L, N and E terminals on the boiler. Remove the short flex from spur to boiler completely.
Back to top
The following user says thank you to D_Hailsham for this useful post:
terence7556 (7 Aug 2010)
 Alert Moderators
terence7556

from United Kingdom

Joined: 25 Mar 2008
Posts: 1801
Location: Staffordshire,
United Kingdom
Thanked: 259 times

PostPosted: Sat Aug 07, 2010 11:55 am Reply with quote

ok i will do that . much appreciated.
Back to top
 Alert Moderators
bengasman

from United Kingdom

Joined: 28 Jan 2005
Posts: 30937
Location: London,
United Kingdom
Thanked: 2750 times

PostPosted: Sat Aug 07, 2010 1:21 pm Reply with quote

The best way to go about solving a problem with an obviously incorrectly wired up control system, is to strip it, and start again. It is a lot quicker and easier than trying to undo other people's eff ups.

Bear in mind that the connections to the pump and the boiler should be heat-resistant flex.
Back to top
The following 2 users say thank you to bengasman for this useful post:
terence7556 (7 Aug 2010), matt1e (7 Aug 2010)
 Alert Moderators
matt1e

from United Kingdom

Joined: 13 Dec 2008
Posts: 2215
Location: Tyne and Wear,
United Kingdom
Thanked: 226 times

PostPosted: Sat Aug 07, 2010 2:13 pm Reply with quote

bengasman wrote:
The best way to go about solving a problem with an obviously incorrectly wired up control system, is to strip it, and start again. It is a lot quicker and easier than trying to undo other people's eff ups.


I totally agree
Back to top
The following user says thank you to matt1e for this useful post:
terence7556 (7 Aug 2010)
 Alert Moderators
terence7556

from United Kingdom

Joined: 25 Mar 2008
Posts: 1801
Location: Staffordshire,
United Kingdom
Thanked: 259 times

PostPosted: Sat Aug 07, 2010 2:26 pm Reply with quote

thats what im doing. the original wiring centre was 6 or 7 connector blocks shoved into a double box3.... and i0 01a1m1231 041 3
attemp ting t0o sort01 0out a random firing problem, possibly dhw valve/cyl stat and i decided to install a honeywell 10 way.did this, belled out to sort out whats whats and caused this. cable problem which dave has pointed out a solution to.all looks neater so part one sorted and ive learned a little bit so all good
thanks guys
ps my grandson is helping me type this154
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Y plan wiring problem 2 60 Wed Jan 04, 2012 12:23 pm
worcester r35he plus s plan wiring problem 36 760 Thu Jul 05, 2012 11:35 am
Extra zone valve wiring in - y plan system 68 940 Thu Sep 13, 2012 9:40 am
Y-plan wiring issues 6 100 Fri Nov 25, 2011 7:42 pm
S plan plus wiring for 2 zone programmer 5 100 Wed Sep 18, 2013 5:03 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.