lighting poblem in garage

Joined
15 Nov 2008
Messages
10
Reaction score
0
Location
Clwyd
Country
United Kingdom
hi my garage got broken into a few days ago so i decided to fit 2 more security lights 1 light works fine, the other one which is connected to its own fuse, blows the rcd every time you connect a live wire to the light
i have changed the light and all the wiring to the wylex board, which was fitted by an electrician a couple of years ago
any help would be very grateful
thanks
 
Sponsored Links
Is the neutral terminated in the right hole? Can you upload a labeled pic?
 
neutral is terminated in board correctly and light correctly i have changed the wiing to the board and to the light without any luck
 
Sponsored Links
Can you connect a temporary light to the end of the cable? this will eliminate the old light as the cause(if it works) if not you have a problem with your cable.
 
Take a picture of the CU with cover off, I think theres a neutral in the wrong place.
 
you've put a switch in I presume?
get us photo's of that..

odds are that you've mixed up a black switched live and a neutral.. causing a direct short when you operate the switch..
 