Glow worm compact electronic boiler dreaded red light


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
Foxley20

from United Kingdom

Joined: 18 Sep 2010
Posts: 2
Location: Surrey,
United Kingdom

PostPosted: Sat Sep 18, 2010 10:24 am Reply with quote

Our Glow worm compact electronic boiler keeps cutting out with an increasing frequency. We had a similar problem a year ago and had it looked at by a Corgi/gas safe engineer who essentially repressurized the system. He commented that the floor was damp below the boiler and considered a leak, but at a follow-up visit (service) stated all was okay.

Over the last 2 weeks, the boiler has cut out approximately 11-12 times, usually in the morning. We have noticed that the water out of the hot water tap is excessively hot just before and after the boiler cuts out. The boiler makes a slightly unusaul whirring noise when the red light flicks on. Current pressure approx 0.7bar. Should I just re-pressurise or is there a more sinister problem? Many thanks.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Beerlover

from United Kingdom

Joined: 07 Sep 2010
Posts: 1072
Location: London,
United Kingdom
Thanked: 210 times

PostPosted: Sat Sep 18, 2010 10:38 am Reply with quote

It would sound that the DHW diapragm has stretched or there is carp behind it causing the boiler to carry on firing after the tap has closed.

It is the one on the right of the plate heat exchanger. Turn the power off to the boiler and remove the front cover to access. remove the microswitch and run a hot tap - pin moves out. Now turn the tap off, does the pin return quickly and fully?

http://www.glow-worm.co.uk/stepone/data/downloads_sd/4f/00/00/compact80e.pdf
Back to top
 Alert Moderators
Alfredo

from United Kingdom

Joined: 08 Aug 2006
Posts: 3633
Location: Yorkshire,
United Kingdom
Thanked: 714 times

PostPosted: Sat Sep 18, 2010 11:11 am Reply with quote

Its unusual for a failed diaphragm to send a compact into lockout. Having said that, a failed diaphragm is the commonest fault on them and I regard them pretty well as a service item, so unless its had a HW diaphragm recently I'd change it anyway.

At 0.7 bar I'd expect a Compact to run, but those gauges are not all that accurate, so if it is in fact a real pressure of 0.5 or less, it might go to lockout. Also the boiler should be pressure set to bewteen 1 and 1.3 bar when cold and should not lose pressure. If you are having to re presssurise it more than three or four times a year max. then it suggests a leak, which ought to be investigated. Putting fresh water into a system on a regular basis maximises and encourages internal corrosion/sludge etc.

My best guess on this is that you have a scaled up/blocked DHW plate to Plate Heat exchanger which is putting the boiler into overheat and locking out as a result. If the system water really is filthy then a flush is required and it must be refilled with a quality corrosion inhibitor

I do not think this is a DIY job personally

Alfredo
Back to top
 Alert Moderators
Beerlover

from United Kingdom

Joined: 07 Sep 2010
Posts: 1072
Location: London,
United Kingdom
Thanked: 210 times

PostPosted: Sat Sep 18, 2010 11:22 am Reply with quote

Foxley20 wrote:
We have noticed that the water out of the hot water tap is excessively hot just before and after the boiler cuts out.


Blocked plate would give poor DHW
Back to top
 Alert Moderators
Alfredo

from United Kingdom

Joined: 08 Aug 2006
Posts: 3633
Location: Yorkshire,
United Kingdom
Thanked: 714 times

PostPosted: Sat Sep 18, 2010 11:38 am Reply with quote

Yes but with a blocked DHE Heat Ex its not uncomon to get a little burst of red hot before it all goes cold, so the DHW heat ex has to be checked out at the very least for blockage. Its sounds like an overheat lockout too which ties in with the boiler being unable to get rid of its heat into the DHW heat ex.

It may not be of course, but you can't ignore it as something to check.

Alfredo
Back to top
 Alert Moderators
gas_man_gaz

from United Kingdom

Joined: 18 Sep 2007
Posts: 1510
Location: Sheffield,
United Kingdom
Thanked: 75 times

PostPosted: Sat Sep 18, 2010 11:53 am Reply with quote

the stuffing box where the pin comes out to make the dhw micro-switch are really common for leaking. they norm leak into the switch and create a false dhw demand causing the boiler to overheat.
just remove the switch and check if it is full of water
Back to top
 Alert Moderators
Foxley20

from United Kingdom

Joined: 18 Sep 2010
Posts: 2
Location: Surrey,
United Kingdom

PostPosted: Mon Sep 20, 2010 9:24 pm Reply with quote

Many thanks Alfredo, Beerlover and gas_man_gaz. I think this is a job for the professional. Will track down a gas safe engineer this week. Any suggestions of one in the south london/surrey area would be much appreciated.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Dreaded Baxi Barcelona System Boiler 6 660 Wed Dec 23, 2009 9:39 pm
The dreaded ISAR HE24! 5 320 Mon Jan 19, 2009 12:51 pm
dreaded ravenheat combi 5 1680 Mon May 15, 2006 8:32 pm
The dreaded Brittany Combi.............help needed 17 380 Tue Mar 15, 2011 11:09 am
Dreaded isar 15 620 Wed Sep 29, 2010 5:11 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.