It's single phase suppplying a combi oven, testing it at the terminal block inside the oven I have good access and the tails are on their own no other supply in the same area and the reading responds to the boiler elements cycling on and off, I have metered the elements and there is none down to earth or open,although the cavity elements are tripping an upstream 80/30 RCD and its own 63/30 this is a new circuit I installed during an CU upgrade and new radial circuits all other circuits are ok, total load for this circuit is 9KW wired in 6mm T&E
Devlin
Sorry the 9k is total load if all are working together ie cavity and steam this will not happen as it's either or. the elements I am testing are the boiler elements 3 X750w 2.25 KW so I should get 9.8amps in and out but i get 5.6 L and 10 N I use a cheapo clamp it's generall good for guidance I have not checked each element individually so maybe thats the next check
Dev
Pugwash cheers for that, gives me another avenue to explore, This things been out of commision for 3 years and each fault I clear somthing else pops up Ho Hum another day another challenge
Dev