Hi,
My old Satchwell room stat has thrown it's hand in. I have bought a new RAA20-GB from the plumbers merchants, but the wiring is completly different. I have a Baxi back boiler and old Glowworm Mastermind clock controller. The old Satchwell stat had red to terminals 1 and 3 and 2 blacks to terminal 4. The new Siemens has L live and Y1 and Y2, I have tried various combinations and it trips the circuit, I have put the earths together and insulated as there is none on the new stat. As far as I am aware, there is no motorised valve in my system, so I think it is only powering the pump and boiler, or not as the case may be.

Any help much appreciated.
 
Sponsored Links
The new Siemens has L live and Y1 and Y2
Do you have a multimeter?

If so measure the voltage between each red and the paired black. The red which measures 240Vac should connect to terminal L; the other red goes to Y1. The two blacks are neutrals, which are not required. Connect them to the same terminal of a terminal strip.
 
Thanks, the red that went to 3 was constant live, I have put this to L and the other to Y1. The 2 blacks are now in a block connector and the system is working. Managed to get this done last night as thought it might be another cold one.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top