Honeywell DT90E - how to wire up?

Joined
29 Jan 2008
Messages
42
Reaction score
1
Location
Berkshire
Country
United Kingdom
Have a ariston boiler system boiler.
Drayton RTS1 room stat and a drayton Lifestyle LP112 programmer.

I want to replace the RTS1 with the honeywell DT90E - I believe the system uses a neutral to switch @240 mains also in conjunction with this lifestyle timer.

So do I need all 3 wires to new Honeywell or can I just use 2?

The DT90E supports mains and low voltage so I just want to know wats the best method of doing of this please?

PS- some posts regading this are unclear with regards to my scenario so apologies to those who have supported this issue more than once!.
 
Sponsored Links
Just use the live in and live out . DONOT use the neutral disconnect it at both ends
 
Just use the live in and live out . DONOT use the neutral disconnect it at both ends

Thanks for the info, can i make the neutral at stat side"safe" and leave the other side connected, simply as i do not want to open up the junction box its all wired up too.

Thanks
 