I have a Grant vortex 26 combi oil boiler. It is about 5 yrs old and has a couple of issues.

1. It doesn't seem to hold its pressure. I pressurise the system to 1bar but in a couple of days it reduces to almost zero but not low enough to trip the LP switch. There is a discharge from the PRV that must happen during normal operation. I have bled the system at the boiler and radiators and I have checked for leaks but can find none

2. The domestic hot water occasionally runs cold even when demand is low e.g. washing up.

I would appreciaye any help

Ivan
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Terrywookfit

from Antarctica

Joined: 19 Jul 2007
Posts: 2387
Location: Antarctica
Thanked: 289 times

PostPosted: Wed Nov 10, 2010 2:57 pm Reply with quote

Check the charge on the exp vessell
Back to top
 Alert Moderators
ijb2302

from United Kingdom

Joined: 10 Nov 2010
Posts: 7
Location: Bath,
United Kingdom

PostPosted: Wed Nov 10, 2010 7:45 pm Reply with quote

Thanks I will try that.
I actually fitted anew one a year ago. The other was filled with water.
Back to top
 Alert Moderators
ijb2302

from United Kingdom

Joined: 10 Nov 2010
Posts: 7
Location: Bath,
United Kingdom

PostPosted: Fri Nov 12, 2010 7:06 am Reply with quote

I checked the exp vessel pressure and it was 0.95bar.

The system pressure was low again. I filled it to a preesure of 1 bar and fired the boiler. The pressure went up to 2bar+ and the PRV vented.
It seems that there is not enough capacity to cope with the expansion of the fluid.

Should I pressurise the system to to a lower pressure say 0.5bar
Back to top
 Alert Moderators
Terrywookfit

from Antarctica

Joined: 19 Jul 2007
Posts: 2387
Location: Antarctica
Thanked: 289 times

PostPosted: Fri Nov 12, 2010 9:51 am Reply with quote

Did you completely de pressurise the system before checking the vessell ?

How many rads are on the system.

An additional 18 litre vessell would help, as the one fitted as standard is only big enough on a small system.
Back to top
 Alert Moderators
ijb2302

from United Kingdom

Joined: 10 Nov 2010
Posts: 7
Location: Bath,
United Kingdom

PostPosted: Fri Nov 12, 2010 11:03 am Reply with quote

Thanks for this

Yes I de-pressurised the system.

There are 11 radiators. I have calculated the volume when I installed the boiler as around 80 litres which should be within the Grant stated maximum of 128 litres.

I notice that this is at expansion vessel charge of 1 bar and system pressure of 0.5 bar.

I have just checked after about 4 hours of operation.

After starting with the exp vessel pressure of 1 bar and system pressure of 1 bar when cold about 1 litre of water has discharged via the PRV and the system pressure (hot) is now 0.5 bar.
Back to top
 Alert Moderators
dcawkwell

from United Kingdom

Joined: 02 Nov 2010
Posts: 3345
Location: Humberside,
United Kingdom
Thanked: 505 times

PostPosted: Fri Nov 12, 2010 12:58 pm Reply with quote

ijb2302 wrote:
Thanks for this

Yes I de-pressurised the system.

There are 11 radiators. I have calculated the volume when I installed the boiler as around 80 litres which should be within the Grant stated maximum of 128 litres.

I notice that this is at expansion vessel charge of 1 bar and system pressure of 0.5 bar.

I have just checked after about 4 hours of operation.

After starting with the exp vessel pressure of 1 bar and system pressure of 1 bar when cold about 1 litre of water has discharged via the PRV and the system pressure (hot) is now 0.5 bar.


What pressure have you got in the expansion vessel now?
If it has dropped the expansion vessel is at fault.
Faulty tyre valve on the expansion vessel possible.
Back to top
 Alert Moderators
ijb2302

from United Kingdom

Joined: 10 Nov 2010
Posts: 7
Location: Bath,
United Kingdom

PostPosted: Fri Nov 12, 2010 6:11 pm Reply with quote

The exp vessel pressure is still 1 bar so I think it is OK. It was new a year ago.
Back to top
 Alert Moderators
slapper

from United Kingdom

Joined: 20 Jan 2008
Posts: 1396
Location: Lincolnshire,
United Kingdom
Thanked: 272 times

PostPosted: Fri Nov 12, 2010 6:44 pm Reply with quote

ijb2302 wrote:
Thanks for this

Yes I de-pressurised the system.

There are 11 radiators. I have calculated the volume when I installed the boiler as around 80 litres which should be within the Grant stated maximum of 128 litres.

I notice that this is at expansion vessel charge of 1 bar and system pressure of 0.5 bar.

I have just checked after about 4 hours of operation.

After starting with the exp vessel pressure of 1 bar and system pressure of 1 bar when cold about 1 litre of water has discharged via the PRV and the system pressure (hot) is now 0.5 bar.
Why dont you fit a new PRV,it shouldnt discharge at less than 3bar and or 90degrees centigrade
Back to top
 Alert Moderators
Tibbot

from United Kingdom

Joined: 27 Nov 2009
Posts: 1874
Location: Hertfordshire,
United Kingdom
Thanked: 321 times

PostPosted: Fri Nov 12, 2010 6:58 pm Reply with quote

ijb2302 wrote:
There are 11 radiators. I have calculated the volume when I installed the boiler as around 80 litres which should be within the Grant stated maximum of 128 litres.


Did you remember to allow for the 50 or so litres contained in the boiler in your calculation? That leaves only 78 to fill 11 rads and pipework. Extra vessel is probably required.
Back to top
 Alert Moderators
dcawkwell

from United Kingdom

Joined: 02 Nov 2010
Posts: 3345
Location: Humberside,
United Kingdom
Thanked: 505 times

PostPosted: Fri Nov 12, 2010 8:09 pm Reply with quote

Faulty pressure relief valve if it discharged at low pressure.
Back to top
The following user says thank you to dcawkwell for this useful post:
ijb2302 (13 Nov 2010)
 Alert Moderators
ijb2302

from United Kingdom

Joined: 10 Nov 2010
Posts: 7
Location: Bath,
United Kingdom

PostPosted: Sat Nov 13, 2010 7:17 am Reply with quote

Tibbot wrote:
ijb2302 wrote:
There are 11 radiators. I have calculated the volume when I installed the boiler as around 80 litres which should be within the Grant stated maximum of 128 litres.


Did you remember to allow for the 50 or so litres contained in the boiler in your calculation? That leaves only 78 to fill 11 rads and pipework. Extra vessel is probably required.


Thanks that is a good point. I had not allowed for the boiler capacity so I am right on the limit. So it looks like another exp vessel.

Where be th best place to put it? The boiler is in a boiler room.
Back to top
 Alert Moderators
ijb2302

from United Kingdom

Joined: 10 Nov 2010
Posts: 7
Location: Bath,
United Kingdom

PostPosted: Sat Nov 13, 2010 7:19 am Reply with quote

dcawkwell wrote:
Faulty pressure relief valve if it discharged at low pressure.


Thanks. I have checked the PRV and it is OK
Back to top
 Alert Moderators
Terrywookfit

from Antarctica

Joined: 19 Jul 2007
Posts: 2387
Location: Antarctica
Thanked: 289 times

PostPosted: Sat Nov 13, 2010 9:38 am Reply with quote

Tee into the return pipework in the boiler room.

I would use an 18 ltr.
Back to top
The following user says thank you to Terrywookfit for this useful post:
ijb2302 (13 Nov 2010)
 Alert Moderators
orinvolucri

from United Kingdom

Joined: 26 Mar 2011
Posts: 1
Location: United Kingdom

PostPosted: Sat Mar 26, 2011 4:06 pm Reply with quote

We had a Grant combi boiler which 'blew up' in 2008 ruining much of the contents of our garage with dirty water leakage. It was replaced with a Grant vortex combi 26 by our plumber and has been trouble ever since. We've had a PCB replaced and the pressure always drops after a week or so well below 1 bar meaning the heating and hot water do not come on. It requires resetting every time which the subcontracted Grant engineer showed me how to do.

However, in using the one years extended warranty through Grant, the engineer found no fault indicating that we had to pay 235 to Grant. Their engineer only charges 57 call out fee! So, we are left with court case to fight (which we are presently doing) and a boiler that clearly has something wrong such as a faulty pressure vessel, pressure switch or similar. Moral of the story from our experience - avoid Grant boilers.

Any advice on how to proceed (legally and plumbing wise) would be greatly appreciated.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Grant Vortex Condensing Combi 26 hot water problems 30 8020 Sat Feb 19, 2011 3:45 pm
Grant Vortex condensing oil boiler 15/26 Problems 12 3200 Wed Apr 25, 2012 1:55 pm
Grant Vortex combi external oil boiler overheat 11 520 Mon Dec 24, 2012 1:55 pm
grant vortex 36 combi boiler low pressure 5 720 Sun Dec 13, 2009 8:41 pm
Grant vortex 26 combi oil boiler 4 100 Sun May 04, 2014 7:22 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.