PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17444
Location: Londonderry,
United Kingdom
Thanked: 1737 times

PostPosted: Tue Nov 30, 2010 12:29 pm Reply with quote

I think I could have a small leak in my central heating system.
There is no signs of water damage anywhere or signs of leaks/drips on accessible pipes.
The water pressure on the boiler will reduce to a measurement that will not allow the boiler to operate (hot water and heating shut off)
This has taken a period of about 10 weeks from a new boiler being installed but did also happen with old boiler.
The system is all copper piping, so rather than rip up all the recently laid flooring, I would prefer to add a leak sealer to the system.
Is this a fair solution?
Does it work?
What is the best product to use?
I have seen Kilrock and fernox products on the shelves at the sheds but not visited any merchants.
Any help/advise would be much appreciated.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
John506

from United Kingdom

Joined: 14 Nov 2006
Posts: 1341
Location: Merseyside,
United Kingdom
Thanked: 69 times

PostPosted: Tue Nov 30, 2010 3:17 pm Reply with quote

Even thought you could be correct and it could well be a leak, first I would advise to re pressurize system, turn on and make sure no water comes out of blow off (pipe that goes through the wall behind the boiler, generally in copper, turning back to face the wall).

Check your expansion vessel. Drain system until 0bar pressure, and check with a tyre pressure gauge on the pressure gauge and make sure it is charged to correct pressure (should say on the vessel or in the manufacturers spec) and that there is no water coming out.

I've never used the leak sealer, always been a fan of doing things properly to be honest. So I can't give an opinion on that I'm afraid.
Back to top
The following user says thank you to John506 for this useful post:
PrenticeBoyofDerry (30 Nov 2010)
 Alert Moderators
hibeealex

from United Kingdom

Joined: 18 Dec 2005
Posts: 40
Location: Edinburgh,
United Kingdom
Thanked: 6 times

PostPosted: Tue Nov 30, 2010 7:09 pm Reply with quote

Well if its a new boiler its probably not the expansion vessel, and you did say it was the same on the old system. so probably a leak ,if its taken 10 weeks to lose pressure to stop the firing, then a leak sealer will probably be fine , just add it as per the manufacturer's instructions and you'll be ok it does work well on small leaks which is what you seem to have
I have used it a few times over the years and always successfully.
best to add it through a towel warmer if you have one.
Back to top
The following user says thank you to hibeealex for this useful post:
PrenticeBoyofDerry (30 Nov 2010)
 Alert Moderators
BingoBongo

from United Kingdom

Joined: 03 Feb 2008
Posts: 1496
Location: Glasgow,
United Kingdom
Thanked: 87 times

PostPosted: Tue Nov 30, 2010 7:13 pm Reply with quote

i wouldnt be sticking leak sealer in a brand new boiler,but thats just me.god knows what it dooes to the aav and small waterways.(what kind of boiler is it)check all the packing glands on the rad valves as a small sweat can evaporate when the heating is or run down the pipe and under the floor
Back to top
The following user says thank you to BingoBongo for this useful post:
PrenticeBoyofDerry (30 Nov 2010)
 Alert Moderators
rgas

from United Kingdom

Joined: 30 Nov 2010
Posts: 18
Location: Yorkshire,
United Kingdom
Thanked: 4 times

PostPosted: Tue Nov 30, 2010 8:09 pm Reply with quote

I agree, definitely do not put leak sealant in your system, will reduce the life of the boiler! Make sure its not your expansion vessel (while not common, its not unherd of for expansion vessels to be faulty on new boilers), weeping valves on the rads etc...
Back to top
The following user says thank you to rgas for this useful post:
PrenticeBoyofDerry (30 Nov 2010)
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17444
Location: Londonderry,
United Kingdom
Thanked: 1737 times

PostPosted: Tue Nov 30, 2010 8:52 pm Reply with quote

Thanks for the replies.
I Will check all the rad valves and tighten if needed.
I too would much prefer if any leaks were repair properly but....
There are areas under the floor that would be really difficult to access without major upheaval and also the added fact of evil looks of disapproval from the missus, could be a scary option.
The boiler is an ideal logic+ and was fitted about 3 months ago, I did have the same problem with the previos boiler but thought it was the boiler at fault as it was quite old.
Back to top
 Alert Moderators
John506

from United Kingdom

Joined: 14 Nov 2006
Posts: 1341
Location: Merseyside,
United Kingdom
Thanked: 69 times

PostPosted: Tue Nov 30, 2010 8:55 pm Reply with quote

Remember that you also have the option to go through the ceiling if it is possible and easy enough, easy enough to repair afterwards
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17444
Location: Londonderry,
United Kingdom
Thanked: 1737 times

PostPosted: Tue Nov 30, 2010 9:18 pm Reply with quote

Something tells me that the problem does not lay in the ceiling void, but is more likely to be downstairs rad under floor connection as they are newer installed rads and had not had this problem prior to that, but I have had a quick feel around some rad valves and found damp/wet around valves, no pools of water but defo moisture there.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Central Heating leak sealer 10 14160 Sun Feb 06, 2011 12:58 pm
Heating system leak sealer 2 980 Tue Oct 07, 2008 5:40 pm
Best Leak Sealer on the Market? 3 60 Tue Jan 31, 2012 8:02 pm
Central Heating Leak Sealer 13 35600 Mon Apr 04, 2005 10:16 am
Removing Leak Sealer?? 19 1120 Sat Mar 14, 2009 3:02 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.