Called out to boiler fault, nothing working when arrived, client advised diaplay panel had not been working for several months. I changed display to get faults codes but nothing happened, so i then changed pcb as well. All seemed ok when i left, client then called to say 'L9' appeared and manual referred to possible blockage in heat exchanger.
I then returned to check all posibilities that the manual mentioned and all seemed fine except for the blocked heat exchanger. The thermistors were checked and all ok and the diverter valve was checked for debris and function and all ok. I then tried changing the plate heat exchanger but still getting 'L9', I'm thinking of going back tomorrow to powerflush the boiler, there was a little brown debris in the plate connections within the boiler but nothing too much. AM I DOING THE RIGHT THING, ITS DRIVING ME MAD? I have also spoke with ideal several times who don't seem to be much help.
Any help will be much appreiciated. Nick.
I then returned to check all posibilities that the manual mentioned and all seemed fine except for the blocked heat exchanger. The thermistors were checked and all ok and the diverter valve was checked for debris and function and all ok. I then tried changing the plate heat exchanger but still getting 'L9', I'm thinking of going back tomorrow to powerflush the boiler, there was a little brown debris in the plate connections within the boiler but nothing too much. AM I DOING THE RIGHT THING, ITS DRIVING ME MAD? I have also spoke with ideal several times who don't seem to be much help.