What junction box to use with armoured cable?


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
s999

from United Kingdom

Joined: 05 Mar 2005
Posts: 38
Location: United Kingdom

PostPosted: Mon May 09, 2005 1:51 pm Reply with quote

This is where the armoured cable terminated, and then goes into normal 2.5mm T&E cable.

The actual juntion will be indoors, do can I use a normal 30amp junction box or does it have to be one or those big expensive weatherproof junction boxes (that cost at least £5)?
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46778
Location: London,
United Kingdom
Thanked: 1701 times

PostPosted: Mon May 09, 2005 3:04 pm Reply with quote

You don't need a waterproof box as it's not outside, but an ordinary JB is no use at all as you need to be able to mount a SWA gland on it, so you'll need one of those metal adaptable boxes.

But if you think that £5 is "expensive" then I would caution you against doing any electrical work, as sooner or later you'll bodge something to save a few quid. It's going to cost you more than that just for a metal box and a set of glands - this is not something you should approach with the mindset that £5 is "expensive"....

What are you supplying with the SWA? Is 2.5mm≤ big enough?
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 1 time

PostPosted: Mon May 09, 2005 4:12 pm Reply with quote

Why not simply take the SWA to the origin of the circuit and terminate it in the Board. Other than I can only echo BAS's comments.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46778
Location: London,
United Kingdom
Thanked: 1701 times

PostPosted: Mon May 09, 2005 4:25 pm Reply with quote

I was assuming that, like most (all) CUs, it would be too flimsy and too cramped to terminate SWA in it.

s999 - another Q for you - I take it you are using 3-core SWA?
Back to top
 Alert Moderators
mapj1

from United Kingdom

Joined: 24 Nov 2004
Posts: 1041
Location: United Kingdom
Thanked: 2 times

PostPosted: Mon May 09, 2005 4:31 pm Reply with quote

Almost any metal box will do - it is possible to go in to the back of a double socket box and blanking plate. It doesn't need to be weatherproof, but enough room to work in is useful. You are right about the tail wagging the dog with a plastic box, it is possible but not something I'd recommend without seeing the box first. If the metal box is along side the plastic CU or whatever, then the cores of the SWA can pass through the metal box that holds the gland, straight into the plastic one, without actually having extra joins in the metal box. Remember to bring an earth tail wire out to earth the box and the SWA armour though.


Last edited by mapj1 on Fri May 13, 2005 2:57 pm, edited 1 time in total
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 1 time

PostPosted: Mon May 09, 2005 5:20 pm Reply with quote

ban-all-sheds wrote:
I was assuming that, like most (all) CUs, it would be too flimsy and too cramped to terminate SWA in it.

s999 - another Q for you - I take it you are using 3-core SWA?


All Consumer Units are not plastic, and those that are, not all are flimsy, although I accept that many nof the cheaper brands certainly are.

We are not talking about a 4C16mm or 3C25mm here, we are talking about at most a 3C2.5mm, this is hardly much more than a bootlace and the strain it would put on any CCU would be minimal. As for being able to terminate a SWA into a Consumer unit due to room, what rot in my opinion, I have never had this trouble.

If want to know how tight a board can be, try terminating 20 4C or 3C 16mm and several other largish SWA's into a TPN panel, then you know what tight is.
Back to top
 Alert Moderators
s999

from United Kingdom

Joined: 05 Mar 2005
Posts: 38
Location: United Kingdom

PostPosted: Mon May 09, 2005 6:53 pm Reply with quote

First things first......... what does SWA stand for? icon_redface.gif

£5 isn't a lot for me....... its just that I've got a normal 30amp junction at home and I'm wondering if theres any point in buying another one.

I'm gonna run a 2.5 T&E from the consumer unit....... under the floorboards and then terminate it just as it reaches the back garden a wall........ and then the armoured cable come in.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46778
Location: London,
United Kingdom
Thanked: 1701 times

PostPosted: Mon May 09, 2005 7:14 pm Reply with quote

FWL_Engineer wrote:
All Consumer Units are not plastic, and those that are, not all are flimsy, although I accept that many nof the cheaper brands certainly are.

That's true

Quote:
We are not talking about a 4C16mm or 3C25mm here, we are talking about at most a 3C2.5mm, this is hardly much more than a bootlace

It's bigger than 6mm≤ T/E. And isn't the gland size the same for SWA up to 6mm≤?

Quote:
and the strain it would put on any CCU would be minimal. As for being able to terminate a SWA into a Consumer unit due to room, what rot in my opinion, I have never had this trouble.

Well - there's no getting away from the fact that you've probably seen one or two more CUs than I have, icon_wink.gif , but of the popular makes that represent 90% of the domestic market, is it reasonable to expect that you could retro-fit a 20mm SWA gland into the side/top/bottom of many of them?

If it is then I'll apologise for misleading s999, but at the time, not knowing how adept he was, not knowing what CU he has, not knowing what kind of a rats nest is inside, not knowing what access around the outside is like and not knowing what experience of terminating SWA he has, I went for what I considered the more trouble free option.....
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46778
Location: London,
United Kingdom
Thanked: 1701 times

PostPosted: Mon May 09, 2005 7:19 pm Reply with quote

s999 wrote:
First things first......... what does SWA stand for? icon_redface.gif

Steel Wire Armoured.

Quote:
£5 isn't a lot for me....... its just that I've got a normal 30amp junction at home and I'm wondering if theres any point in buying another one.

It's no use for this.

Quote:
I'm gonna run a 2.5 T&E from the consumer unit....... under the floorboards and then terminate it just as it reaches the back garden a wall........ and then the armoured cable come in.

And what happens then?

Where does the armoured cable go, how does it get there, what load will it be powering at the other end, and what will be the total distance from CU to the far end? And is it 3-core?

And do you know what sort of earth your supply has (TN-S, TN-C-S/PME or TT)? A description or photograph would be useful if you don't.

And finally - are you aware of the requirements of Part P of the Building Regulations vis-a-vis running electrical supplies to gardens and outbuildings?
Back to top
 Alert Moderators
s999

from United Kingdom

Joined: 05 Mar 2005
Posts: 38
Location: United Kingdom

PostPosted: Mon May 09, 2005 7:23 pm Reply with quote

^ I don't know any of that....... all I'm gonna do is run the wires under the floorboards (because we're about to lay carpet soon and I don't wanna cause a mess later).

I'm actually gonna get an electrician to connect it at the consumer unit and in the shed (where I want the power).

I'm using 3 core T&E armoured cable.
Back to top
 Alert Moderators
s999

from United Kingdom

Joined: 05 Mar 2005
Posts: 38
Location: United Kingdom

PostPosted: Mon May 09, 2005 7:27 pm Reply with quote

^ Actually I do know the answer to all of that......... but I just said that I didn't for the hell of it.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46778
Location: London,
United Kingdom
Thanked: 1701 times

PostPosted: Mon May 09, 2005 7:33 pm Reply with quote

Well I suggest you use that knowledge to determine if 2.5mm≤ is enough before you put the carpet down......

PS:

s999 wrote:
I'm actually gonna get an electrician to connect it at the consumer unit and in the shed (where I want the power).

Have you checked that he's happy with this? He'll have to sign it off to say that he designed, installed and tested the circuit, and if you just have him along to connect each end without any knowledge of what lies in between, you might be in for a nasty surprise.

Like pick one:

a) "No, I won't do it"

b) "I'll have to rip it all up and start again"

As I said, are you aware of the requirements of Part P of the Building Regulations vis-a-vis running electrical supplies to gardens and outbuildings?
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 1 time

PostPosted: Mon May 09, 2005 8:11 pm Reply with quote

ban-all-sheds wrote:

It's bigger than 6mm≤ T/E. And isn't the gland size the same for SWA up to 6mm≤?


FWL_Engineer wrote:
and the strain it would put on any CCU would be minimal. As for being able to terminate a SWA into a Consumer unit due to room, what rot in my opinion, I have never had this trouble.


ban-all-sheds wrote:
Well - there's no getting away from the fact that you've probably seen one or two more CUs than I have, icon_wink.gif , but of the popular makes that represent 90% of the domestic market, is it reasonable to expect that you could retro-fit a 20mm SWA gland into the side/top/bottom of many of them?

If it is then I'll apologise for misleading s999, but at the time, not knowing how adept he was, not knowing what CU he has, not knowing what kind of a rats nest is inside, not knowing what access around the outside is like and not knowing what experience of terminating SWA he has, I went for what I considered the more trouble free option.....


Ban, a 3 Core 6mm will require a 25mm Gland generally, although if you can get one of the larger 20mm from BICC then this may fit. 3C2.5mm will usually fit a BW20S gland, so whilst the gland thread size is the same as a larger or any other 20mm gland, the gland will be physically smaller and produce less strain on the consumer unit.

Regarding the fitting of the 20mm gland to a consumer unit, if you have a 20mm Starrett cutter then you can fit one to any of them. The cables, regardless of type, should only ever enter a consumer unit in the top or bottom, unless you have trunking or some other enclosure covering the side opening...in an ideal world any way icon_biggrin.gif

BAS, I don't think you misled anyone, or have anything to possibly apologise for, you gave good advise based on your personal experience and knowledge, no-one can criticise that. Your comment about S999 ability is very valid, and my personal feeling he is not competent to undertake the work he wants to do, if he was then he probably would not be asking these questions, so perhaps your answer was the best one here.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 8484
Location: United Kingdom
Thanked: 215 times

PostPosted: Mon May 09, 2005 9:15 pm Reply with quote

well tlc said that a 20mm gland was right for 3 core 6mm and the 20mm BW glands they sent me were just fine with 6mm

once you get into 25mm glands you either have to use a bloddy big box or make the holes yourself with a holesaw afaict
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
armoured cable query 3 520 Wed Sep 19, 2007 10:02 am
Running an armoured cable outside to feed floodlights 4 880 Wed Sep 26, 2007 9:12 am
Connecting Armoured Cable 22 1940 Tue Oct 02, 2007 8:37 am
Can You Join Armoured Cable ???? 12 1520 Mon Aug 06, 2007 5:44 pm
Armoured Cable Size 10 9800 Wed Jun 13, 2007 2:22 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.