Powering a cooker hood

This topic originated from the How to page called Installing a cooker hood
Click here to return to the page called Installing a cooker hood.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
cludo

from United Kingdom

Joined: 10 May 2005
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue May 10, 2005 12:53 am    Post Subject:
Powering a cooker hood
Reply with quote Thanks

Hi,

Apologies first of all if this is an obvious answer to some...

I have an oven extractor fan whose power cable has 2 wires (no earth). Can I attach a plug to it and then plug it into the socket on the cooker power switch or would this kind of installation mean it was not earthed?

I\\\'ve cheked the instructions that came with it and the 2 lines of how to wire it does not cover this.

Cheers.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21980
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue May 10, 2005 2:47 am    Post Subject:
Re: Powering a cooker hood
Reply with quote Thanks

cludo wrote:
I have an oven extractor fan whose power cable has 2 wires (no earth).

I take it you mean a cooker hood?

Quote:
Can I attach a plug to it and then plug it into the socket on the cooker power switch or would this kind of installation mean it was not earthed?

It won't be earthed, but it's not supposed to be, that's why it only has 2 wires...

3A fuse in the plug, and it'll be fine.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
cludo

from United Kingdom

Joined: 10 May 2005
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue May 10, 2005 9:34 am    Post Subject:
Reply with quote Thanks

Hi ban all sheds,

Yes, sorry I meant a cooker hood.

That certainly makes my life easier, thanks for the response!
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21980
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue May 10, 2005 10:15 am    Post Subject:
Re: Powering a cooker hood
Reply with quote Thanks

ban-all-sheds wrote:
cludo wrote:
I have an oven extractor fan whose power cable has 2 wires (no earth).

I take it you mean a cooker hood?

Yeah - you did, didn't you.

Exactly as per the title of this thread, "Powering a cooker hood".

Sorry... icon_redface.gif icon_redface.gif icon_redface.gif icon_redface.gif

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Tue May 10, 2005 4:15 pm    Post Subject:
Reply with quote Thanks

cludo wrote:
Can I attach a plug to it and then plug it into the socket on the cooker power switch


wouldnt that look a wee bit tatty? Plus, theres the safety issue of having its flex dangling around over the cooker?? And why has nobody else picked up on this???
Back to top
 Alert Moderators
oldfart

from United Kingdom

Joined: 14 Apr 2005
Posts: 35
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue May 10, 2005 7:36 pm    Post Subject:
Reply with quote Thanks

I agree with crafty, if you havent decorated yet, you could always chop in a switched fused spur unit next to your cooker point, taking the power off that, using a 3amp fuse in it. chase a cable from the spur upto a fixed connection unit near your hood or inside if its big enough. No dangly cables and you can isolate it using the swithed spur if you need to. icon_smile.gif
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23346
Location: Sussex,
United Kingdom
Thanked: 5 times

PostPosted: Tue May 10, 2005 8:36 pm    Post Subject:
Reply with quote Thanks

oldfart wrote:
you could always chop in a switched fused spur unit next to your cooker point, taking the power off that


er, how does NO sound
you can not spur off an electric cooker point
(you would need to use same size cable (6mm) to do it, so its an almost physical imposibility

__________________
Do you like music Mr Finch?
Forum = Opinions
Back to top
 Alert Moderators
oldfart

from United Kingdom

Joined: 14 Apr 2005
Posts: 35
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed May 11, 2005 8:34 am    Post Subject:
Reply with quote Thanks

Hi breezer,

excuse my ignorance I thought it was ok to tap off cooker point with 2.5 cable. If it is,nt I apoligse for the duff advice(please disregard)!.

Breezer, I,ve recently done this, the cooker point has a socket outlet as well, I,ve taken power using 2.5 to a spur which is directly adjacent to it.
Sounds like I may have dropped a clanger, what are the implications?

Its all part of a two storey extension, the room above has,nt been floored
yet so I have the option of changing what i,ve done.

cheers
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21980
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed May 11, 2005 11:56 am    Post Subject:
Reply with quote Thanks

It is considered safe to run a spur in 2.5mm˛ from a ring with a 32A breaker.

It is not considered safe to run a spur in 2.5mm˛ from a cooker circuit with a 32A breaker.

Discuss.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
oldfart

from United Kingdom

Joined: 14 Apr 2005
Posts: 35
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed May 11, 2005 12:49 pm    Post Subject:
Reply with quote Thanks

thanx ban,

interesting point, like u say circiuts on the same size breaker, I assumed rightly or wrongly, I was ok.
being protected either end by breaker & rcd at cu and 3amp fuse in switched spur, perhaps breezers thinking about the amount of power the 6mm is carrying and then transferring to the 2.5 and a possible heat increase?

I obvoiusly want to do the job right and safely just unsure to what extremes I take it. icon_confused.gif
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Wed May 11, 2005 9:16 pm    Post Subject:
Reply with quote Thanks

it is specifically allowed to run a 2.5mm spur off a 32A ring

it is not specifcially allowed to run one off a 32A cooker cuircuit but i don't think its specificially prohibited either and i can't see it being any less safe.

running such a spur off a higher rated cooker cuircuit is more dodgy though.
Back to top
 Alert Moderators
Nick M.

from United Kingdom

Joined: 11 May 2005
Posts: 1
Location: Middlesex,
United Kingdom
Thanked: 0 times

PostPosted: Wed May 11, 2005 9:39 pm    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
It is considered safe to run a spur in 2.5mm˛ from a ring with a 32A breaker.

It is not considered safe to run a spur in 2.5mm˛ from a cooker circuit with a 32A breaker.

Discuss.


Interesting point & something that I had an argument with someone recently about this.

This is my take on this,

Firstly can I use the words bad practice instead of unsafe as I don't think its unsafe, it has the same loading whether its run off a ring or a radial, the cable can't tell what its connected to.

Secondly "what does the spur feed", if its a cooker hood with a load of say 250W & the cooker is rated at 6kw, theres nothing wrong with that, I would argue till I am blue in the face that you haven't exceeded the design current of the circuit & I have done this recently in a kitchen & had a row with a LABC inspector who had done a three day course (part P) & read somewhere that this couldn't be done, he couldn't show me why though.
If the spur is feeding a tumble dryer for arguments sake, then I would say that is bad design & unworkable, not unsafe as the protective device should operate & protect the cables from overheating as it should do.

Just my tuppence worth

Nick
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21980
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu May 12, 2005 11:48 am    Post Subject:
Reply with quote Thanks

You've hit 2 nails firmly on the head there.

1) Good/Bad practice and the instant LABC expert. This is really a distillation of the environment, encouraged by the OSG, of what I term "electrical installations for the hard of thinking". The reliance on the use of standard circuits means that people don't bother to do proper design, or think about what design principles underpin those standard circuits, they just follow "the rules" and don't consider other options or other designs.

2) What the "spur" feeds. You're right about the cooker hood load, but your tumble drier comment is interesting - I'll bet there's at least 1 person in the country with a T/D plugged into the integral socket on a CCU not knowing that the design current for that socket is only 5A. We're back to the "rules", and how you either have to unthinkingly follow them or work things out properly. A spur in 2.5mm˛ is considered safe because the rules say only 1 socket, so when you follow the rules you can't overload the cable.


When I said "discuss", it wasn't a rhetorical, or sarcastic remark. A cooker circuit is of course a radial, so a circuit coming off of it is not a spur, it is a leg of the radial, and there are no rules explicitly limiting the number of sockets on it - you're into the realm of designing the circuit properly. There is no simple "only 1 socket" rule that "prevents" more from being added, which is why you do have to be very careful, and which is why I agree that you should not attach a 2.5mm˛ leg to a 32A 6mm˛ radial, except via an FCU to provide proper protection of the cable. A spur on a ring is a special exemption to the Ib <= In <= Iz rule, and it does not apply to other circuits.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
mapj1

from United Kingdom

Joined: 24 Nov 2004
Posts: 1040
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu May 12, 2005 3:46 pm    Post Subject:
Reply with quote Thanks

Ah, but an 13A FCU from a cooker box, in 2.5mm cable is OK, because the cable is protected against overload at the load end, by the FCU fuse, and against short circuit (nail gun?) by the 32A breaker at the other end.
Not prohibited at all, and quite common for running a 3kw oven under a higher rated hob.
repeat after me " we should think rather than just blindly use standard circuits"

__________________
regards Mike(G7VZY)
-STICKY Reference Info @ top of forum, Has diagrams & answers to common probs-
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21980
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu May 12, 2005 10:22 pm    Post Subject:
Reply with quote Thanks

Indeed, the 2.5mm˛ is protected as you say, just as it is when spurring off a ring. I don't do that, either (or at least, have so far managed not to) - I put FCUs directly onto the ring.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Extractor fan in the bathroom not powering off 5 420 Fri Dec 15, 2006 12:37 pm
Powering laptop PC in the car 2 740 Mon Aug 21, 2006 1:24 am
Kitchen Island Extractor - powering it 15 900 Fri Apr 27, 2007 3:57 pm
Powering External Alarm Siren from Loft 12 320 Sat Nov 08, 2008 10:11 am
Powering an outbuilding 13 8400 Wed Sep 03, 2003 2:37 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.