PostPosted: Fri May 20, 2005 8:19 pm    Post Subject:
mcbs
Reply with quote Thanks

hi, i have just installed a 10.5kw rated shower, which replaced an old 7.5kw, the problem is the old 32amp fuse is not powerfull enough for this shower and i cannot seem to find one any where, its a type2 nsb,
ive been told that they are an old type fuse and are hard to get hold of , am i right? plus the shower recomends a 45amp and i have read they dont make them any more, i am a novice when i comes to electrics, can someone help! thanx phil.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
andy

from United Kingdom

Joined: 14 Sep 2004
Posts: 3972
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri May 20, 2005 8:24 pm    Post Subject:
Re: mcbs
Reply with quote Thanks

phiggis wrote:
hi, i have just installed a 10.5kw rated shower, which replaced an old 7.5kw, the problem is the old 32amp fuse is not powerfull enough for this shower and i cannot seem to find one any where, its a type2 nsb,
ive been told that they are an old type fuse and are hard to get hold of , am i right? plus the shower recomends a 45amp and i have read they dont make them any more, i am a novice when i comes to electrics, can someone help! thanx phil.
what size is the cable to the shower? it needs to be 10mm. and what is the length of the run?

do you have an RCD protecting the shower?>
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Fri May 20, 2005 9:33 pm    Post Subject:
Re: mcbs
Reply with quote Thanks

Oh dear.

andrew2022 wrote:
what size is the cable to the shower? it needs to be 10mm


I reckon there's zero chance of that.

I also reckon there is a small but non-zero chance that it might only be 4mm˛.....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16491
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Fri May 20, 2005 10:25 pm    Post Subject:
Reply with quote Thanks

Ban

Perchance the chance of the cable being 4mm is slightly greater than the chance of it being 10mm??
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Fri May 20, 2005 11:36 pm    Post Subject:
Reply with quote Thanks

Probabibly...

Anyway - levity aside - phiggis - you must not simply upgrade the fuse to 45A - this could be very dangerous.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
delmel

from United Kingdom

Joined: 28 Nov 2004
Posts: 323
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat May 21, 2005 12:44 am    Post Subject:
Re: mcbs
Reply with quote Thanks

phiggis wrote:
hi, i have just installed a 10.5kw rated shower, which replaced an old 7.5kw, the problem is the old 32amp fuse is not powerfull enough for this shower and i cannot seem to find one any where, its a type2 nsb,
ive been told that they are an old type fuse and are hard to get hold of , am i right? plus the shower recomends a 45amp and i have read they dont make them any more, i am a novice when i comes to electrics, can someone help! thanx phil.



Type2 nsb is acually an MCB made by wylex type 2 and the catalogue reference is NSB follwed by the amps NSB32 = 32amp. It is and i am sure you may still be able to get in both 40 and 50 amps (you will need the 50) Be very careful though you also should check your cable size to ensure that is correct 10mm is what i would like to see.
TLC should have in stock

www.tlc-direct.co.uk
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Sat May 21, 2005 12:50 am    Post Subject:
Reply with quote Thanks

Phiggis - 10mm˛ is essential if you're going to use a 50A breaker.

See this: http://www.diynot.com/forums/viewtopic.php?p=81696#81696

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
phiggis

from United Kingdom

Joined: 20 May 2005
Posts: 6
Location: Birmingham,
United Kingdom
Thanked: 0 times

PostPosted: Sat May 21, 2005 1:57 pm    Post Subject:
Reply with quote Thanks

hi, i was concerned about upgrading an ncb in my consumer unit from a 32 amp to a 45amp, the cable i am sure is 6mm2 and is less than 1.5 metres from the unit to the shower, it is protected by a 30 amp rcd on the unit ,is this ok if i just upgrade the fuse?.. thanx for the replies and i hope this is a little clearer than before..
Back to top
 Alert Moderators
andy

from United Kingdom

Joined: 14 Sep 2004
Posts: 3972
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat May 21, 2005 2:39 pm    Post Subject:
Reply with quote Thanks

phiggis wrote:
hi, i was concerned about upgrading an ncb in my consumer unit from a 32 amp to a 45amp, the cable i am sure is 6mm2 and is less than 1.5 metres from the unit to the shower, it is protected by a 30 amp rcd on the unit ,is this ok if i just upgrade the fuse?.. thanx for the replies and i hope this is a little clearer than before..


if your RCD is 30A then there is something wrong. and you need to be 100% certain of what size cable it actually is
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Sat May 21, 2005 6:13 pm    Post Subject:
Reply with quote Thanks

30mA

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
phiggis

from United Kingdom

Joined: 20 May 2005
Posts: 6
Location: Birmingham,
United Kingdom
Thanked: 0 times

PostPosted: Sun May 22, 2005 6:59 pm    Post Subject:
Reply with quote Thanks

andrew2022 wrote:
phiggis wrote:
hi, i was concerned about upgrading an ncb in my consumer unit from a 32 amp to a 45amp, the cable i am sure is 6mm2 and is less than 1.5 metres from the unit to the shower, it is protected by a 30 amp rcd on the unit ,is this ok if i just upgrade the fuse?.. thanx for the replies and i hope this is a little clearer than before..


if your RCD is 30A then there is something wrong. and you need to be 100% certain of what size cable it actually is
sorry i forgot to add the m, it is a 30 mA RCD but do i still need to upgrade to 10mm2 cable or will 6mm2 cope with the load, if i change to a 45 or 50 amp mcb? thanx phil...
Back to top
 Alert Moderators
andy

from United Kingdom

Joined: 14 Sep 2004
Posts: 3972
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun May 22, 2005 7:07 pm    Post Subject:
Reply with quote Thanks

phiggis wrote:
andrew2022 wrote:
phiggis wrote:
hi, i was concerned about upgrading an ncb in my consumer unit from a 32 amp to a 45amp, the cable i am sure is 6mm2 and is less than 1.5 metres from the unit to the shower, it is protected by a 30 amp rcd on the unit ,is this ok if i just upgrade the fuse?.. thanx for the replies and i hope this is a little clearer than before..


if your RCD is 30A then there is something wrong. and you need to be 100% certain of what size cable it actually is
sorry i forgot to add the m, it is a 30 mA RCD but do i still need to upgrade to 10mm2 cable or will 6mm2 cope with the load, if i change to a 45 or 50 amp mcb? thanx phil...

change to 10mm^2. the RCD protects again earth leakage, NOT overload. thats what the MCB is for. but your gonna change it for a larger type which the cable might not support. the RCD is there for your own safety
Back to top
 Alert Moderators
phiggis

from United Kingdom

Joined: 20 May 2005
Posts: 6
Location: Birmingham,
United Kingdom
Thanked: 0 times

PostPosted: Tue May 24, 2005 6:08 pm    Post Subject:
Reply with quote Thanks

andrew2022 wrote:
phiggis wrote:
andrew2022 wrote:
phiggis wrote:
hi, i was concerned about upgrading an ncb in my consumer unit from a 32 amp to a 45amp, the cable i am sure is 6mm2 and is less than 1.5 metres from the unit to the shower, it is protected by a 30 amp rcd on the unit ,is this ok if i just upgrade the fuse?.. thanx for the replies and i hope this is a little clearer than before..


if your RCD is 30A then there is something wrong. and you need to be 100% certain of what size cable it actually is
sorry i forgot to add the m, it is a 30 mA RCD but do i still need to upgrade to 10mm2 cable or will 6mm2 cope with the load, if i change to a 45 or 50 amp mcb? thanx phil...

change to 10mm^2. the RCD protects again earth leakage, NOT overload. thats what the MCB is for. but your gonna change it for a larger type which the cable might not support. the RCD is there for your own safety
thanx for the advise, and have finnally decided to get it sorted by some one who nows what they are doing, plus im also having the lot rewired to be on the safe side, aint taking now chances anymore..
thanx for everyones advice. phil.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue May 24, 2005 7:29 pm    Post Subject:
Reply with quote Thanks

So on the basis of your original question, if you had been able to easily find a 45A MCB, e.g. in one of the sheds, you'd have stuck it in with nary a thought....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   This topic is locked you cannot edit posts or make replies    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Replacing wired fuses (Wylex) with MCBs 22 1440 Sun Mar 09, 2008 3:15 pm
mcbs for a clipsal insulated consumer unit. 9 300 Sat Mar 15, 2008 7:35 pm
Merlin Gerin Counterfiet MCBs 6 340 Fri Apr 04, 2008 10:51 pm
MCBs 16 600 Tue Feb 19, 2008 9:38 pm
Retro fit MCBs for old style CU 5 320 Wed Jan 30, 2008 3:20 am