Grant Vortex Condensing Combi 26 hot water problems

Goto page 1, 2, 3  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
didspip

from United Kingdom

Joined: 19 Feb 2011
Posts: 14
Location: Lincolnshire,
United Kingdom

PostPosted: Sat Feb 19, 2011 3:45 pm Reply with quote

I have a problem with my Grant Vortex condensing combi 26 Oil boiler.
When I run the hot water for a bath after a few minutes the water runs luke warm, turn off the hot tap and wait a few minutes and it is hot again.
It always used to work ok.
The other thing I have noticed is I can hear air bubbles traveling around the heat exchanger pipes and the water store. the heating is ok and quiet.
Its almost as if there is not enough water in the store?
The boiler is only 4 years old but has had a few problems needing the boiler to be drained and re filled a number of times.
Leaking washer on heat exchanger - leaking flow switch washer - leaking auto air vents and leaking filling loop taps.
I have replaced the filling loop, air vents and washer on the exchanger.
When I re fill the boiler via the filling loop does this also fill the water store?
Any help as to the cool water issue would be appreciated.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Terrywookfit

from Antarctica

Joined: 19 Jul 2007
Posts: 2328
Location: Antarctica
Thanked: 271 times

PostPosted: Sat Feb 19, 2011 4:09 pm Reply with quote

Have you checked the TMV?
Back to top
 Alert Moderators
didspip

from United Kingdom

Joined: 19 Feb 2011
Posts: 14
Location: Lincolnshire,
United Kingdom

PostPosted: Sun Feb 20, 2011 9:55 am Reply with quote

Terrywookfit wrote:
Have you checked the TMV?


In what way? it is set ok
Back to top
 Alert Moderators
moliver34

from United Kingdom

Joined: 10 May 2007
Posts: 138
Location: Isle of Wight,
United Kingdom
Thanked: 2 times

PostPosted: Sun Feb 20, 2011 6:42 pm Reply with quote

if its not the TMV; then more likely the pcb for the heat store is faulty.

contact; www.grantuk.com

ask to speak to the technical department who will be able to assist you.
Back to top
 Alert Moderators
didspip

from United Kingdom

Joined: 19 Feb 2011
Posts: 14
Location: Lincolnshire,
United Kingdom

PostPosted: Tue Feb 22, 2011 7:07 pm Reply with quote

Terrywookfit wrote:
Have you checked the TMV?


Thanks for the reply but can you tell me how I check the TMV? icon_question.gif
Back to top
 Alert Moderators
didspip

from United Kingdom

Joined: 19 Feb 2011
Posts: 14
Location: Lincolnshire,
United Kingdom

PostPosted: Tue Feb 22, 2011 7:10 pm Reply with quote

moliver34 wrote:
if its not the TMV; then more likely the pcb for the heat store is faulty.

contact; www.grantuk.com

ask to speak to the technical department who will be able to assist you.


Thanks for the info, can you explain why I hear air bubbling through the store and heat exchanger pipes when the hot water is running?
Back to top
 Alert Moderators
oilhead

from United Kingdom

Joined: 29 Nov 2009
Posts: 882
Location: Shropshire,
United Kingdom
Thanked: 208 times

PostPosted: Tue Feb 22, 2011 8:46 pm Reply with quote

Check heat store AAV for operation. Is the cap open?
Are there any manual vents on the pipework you can bleed?
Is the DHW ht exchanger scaled? How does the flow of hot water compare to cold water flow?Is the flow pipe to the TMV hot when the tap starts to cool down?
Back to top
 Alert Moderators
didspip

from United Kingdom

Joined: 19 Feb 2011
Posts: 14
Location: Lincolnshire,
United Kingdom

PostPosted: Wed Feb 23, 2011 8:11 am Reply with quote

oilhead wrote:
Check heat store AAV for operation. Is the cap open?
Are there any manual vents on the pipework you can bleed?
Is the DHW ht exchanger scaled? How does the flow of hot water compare to cold water flow?Is the flow pipe to the TMV hot when the tap starts to cool down?

Thanks for the reply.
AAV on heat store has been replaced and the cap is open but I never hear air coming out even when I drain the system and re fill? does the water in the store drain when the system is drained and re fill when I fill the system back up?
All manual air vents have been bled.
Four year old boiler, will the ht exchanger be scaled after this period? if so do I need to strip it out to check? clean or replace?
Doesn't it use the ht exchanger for the central heating?
As for the TMV flow pipe I will check that later when I run the bath and get back to you.
Back to top
 Alert Moderators
didspip

from United Kingdom

Joined: 19 Feb 2011
Posts: 14
Location: Lincolnshire,
United Kingdom

PostPosted: Thu Feb 24, 2011 8:46 am Reply with quote

oilhead wrote:
Check heat store AAV for operation. Is the cap open?
Are there any manual vents on the pipework you can bleed?
Is the DHW ht exchanger scaled? How does the flow of hot water compare to cold water flow?Is the flow pipe to the TMV hot when the tap starts to cool down?


I can confirm that The flow pipe to the TMV also cools down when the hot water cools down, normally it is too hot to touch.
Does this mean the TMV is b*****r?
Back to top
 Alert Moderators
leakydave

from United Kingdom

Joined: 02 Nov 2005
Posts: 628
Location: Gloucestershire,
United Kingdom
Thanked: 43 times

PostPosted: Thu Feb 24, 2011 9:01 am Reply with quote

What do the heating pipes do when you run hot water? Do they get hot even if the heating is off?
Back to top
 Alert Moderators
oilhead

from United Kingdom

Joined: 29 Nov 2009
Posts: 882
Location: Shropshire,
United Kingdom
Thanked: 208 times

PostPosted: Thu Feb 24, 2011 11:24 am Reply with quote

I can confirm that The flow pipe to the TMV also cools down when the hot water cools down, normally it is too hot to touch.
Does this mean the TMV is b*****r?[/quote]

No, it means that the problem is within the controls of the DHW operations.
Does the burner start up when HW is demanded? Possible flow switch problem.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 52899
Location: London,
United Kingdom
Thanked: 3331 times

PostPosted: Thu Feb 24, 2011 6:06 pm Reply with quote

With oil on the way out and prices rising daily why not consider an alternative fuel source?




[img]

http://img.allvoices.com/thumbs/image/609/609/73717055-moammar-gadhafi-on-fire.jpg

[/img]

Anyone know why the picture will not display here? Click on the link until its corrected!
Back to top
 Alert Moderators
didspip

from United Kingdom

Joined: 19 Feb 2011
Posts: 14
Location: Lincolnshire,
United Kingdom

PostPosted: Fri Feb 25, 2011 7:32 pm Reply with quote

oilhead wrote:
I can confirm that The flow pipe to the TMV also cools down when the hot water cools down, normally it is too hot to touch.
Does this mean the TMV is b*****r?


No, it means that the problem is within the controls of the DHW operations.
Does the burner start up when HW is demanded? Possible flow switch problem.[/quote]

Burner starts up ok every time. Flow switch was replaced last year due to intermittant hot water. This gave hot then stone cold water and I could hear the relay clicking in and out. I have Hot then warm water with no relay clicks. When it runs warm if I turn the tap off for a minute or two it is back up to full temp.
Yesterday as an experiment whilst running the bath I tapped the TMV lightly with a hammer thinking that if it is scaled up this may free it off. After this the hot in pipe stayed too hot to touch and this morning I ran a full bath without it going cold. Does this seem feasible or is it just a coincidence?
Back to top
 Alert Moderators
manortim

from United Kingdom

Joined: 01 Dec 2007
Posts: 2064
Location: Wiltshire,
United Kingdom
Thanked: 417 times

PostPosted: Fri Feb 25, 2011 7:35 pm Reply with quote

What is the water in your area like for hardness or do you have a softener?

What happens if you run the tap slowly?
Back to top
 Alert Moderators
didspip

from United Kingdom

Joined: 19 Feb 2011
Posts: 14
Location: Lincolnshire,
United Kingdom

PostPosted: Tue Mar 01, 2011 7:41 am Reply with quote

manortim wrote:
What is the water in your area like for hardness or do you have a softener?

What happens if you run the tap slowly?


According to Anglian Water the water in my area is Vert Hard.
I have had a bit of success using an un conventional method based around everyones advice that the TMV may be scaled.
Whilst the bath was running I tapped the TMV with a small hammer, as I was doing this all of a sudden the hot in pipe became too hot to touch again, as it should. I was then able to run the full bath without heat loss whilst having the heating on.
I think I may have dislodged some scale?
Does this sound possible?
When the boiler was installed nearly 4 years ago it was a cash barrow job and I suspect there was no inhibitor used.
If so once I have replaced the TMV and the bleed valves again what is the best inhibitor to tackle limescale?
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2, 3  Next
Page 1 of 3

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Grant Vortex condensing oil boiler 15/26 Problems 12 2800 Wed Apr 25, 2012 1:55 pm
Grant Vortex Condensing Combi 26 - no hot water 16 320 Sat Jul 12, 2014 6:41 am
Grant Vortex Pro External Electronic Condensing Combi 21kw 4 480 Tue Nov 03, 2009 11:18 pm
Grant Vortex Condensing combi 26 - pressure gauge help 4 140 Thu Jul 10, 2014 10:13 am
grant vortex pro condensing boiler cutting out 14 220 Fri Dec 28, 2012 12:34 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.