MCB Switching off curve

This topic originated from the How to page called Miniature circuit breakers (MCBs)
Click here to return to the page called Miniature circuit breakers (MCBs).

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
chris911sc

from Ireland

Joined: 18 Mar 2005
Posts: 6
Location: Ireland
Thanked: 0 times

PostPosted: Mon May 30, 2005 12:40 pm    Post Subject:
MCB Switching off curve
Reply with quote Thanks

Could somebody explain to me the difference between MCB switching off curves A, B & C?
Thanks
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6931
Location: United Kingdom
Thanked: 16 times

PostPosted: Mon May 30, 2005 12:50 pm    Post Subject:
Reply with quote Thanks

afaict there is no type A

basically a mcb has two parts

the thermal trip is the same between a B a C and a D of the same rating and deals with relatively small but sustained overloads.

the magnetic trip is designed to take out short cuircuits and it either trips or it doesn't. If the magnitic trip point is hit the breaker will trip extremely fast (0.1 sec is the standard iirc but some manufacturers claim even faster). The type of the breaker determines how many times the rated current is needed to take out the magnetic trip

B is 3-5 times C is 5-10 times and D is 10-20 times.

A lower fast trip point makes cuircuit design to meet earth fault loop requirements easier but can cause nusense tripping with some loads (b6 breakers on lighting cuircuits are well known for this issue).
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon May 30, 2005 6:00 pm    Post Subject:
Reply with quote Thanks

As Breezer says, it's amazing what info you can find in the For Reference topic....

http://www.diynot.com/forums/viewtopic.php?p=76467#76467

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Senarathne

from Sri Lanka

Joined: 30 Aug 2006
Posts: 1
Location: Sri Lanka
Thanked: 0 times

PostPosted: Wed Aug 30, 2006 10:29 am    Post Subject:
miniature circuit breakers
Reply with quote Thanks

What are the advantages and disadvantages of minature circuit breakers?
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Wed Aug 30, 2006 11:07 am    Post Subject:
Reply with quote Thanks

Compared to a chocolate cake, an MCB doesn't taste so good (disadvantage) but is better at cutting electrical overloads or short circuits (advantage)
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16491
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Wed Aug 30, 2006 2:37 pm    Post Subject:
Reply with quote Thanks

JohnD wrote:
Compared to a chocolate cake, an MCB doesn't taste so good (disadvantage) but is better at cutting electrical overloads or short circuits (advantage)


I find victoria sponge better at cutting overloads than a choccy cake...must be the jam...

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Aug 30, 2006 5:19 pm    Post Subject:
Reply with quote Thanks

Surely currant buns are the best for that purpose?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10753
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Wed Aug 30, 2006 5:22 pm    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
Surely currant buns are the best for that purpose?


shouldn't that be a current bun? icon_wink.gif
Back to top
 Alert Moderators
TheGaffersSon

from United Kingdom

Joined: 29 Aug 2006
Posts: 111
Location: Manchester,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 30, 2006 5:47 pm    Post Subject:
Reply with quote Thanks

RF Lighting wrote:
ban-all-sheds wrote:
Surely currant buns are the best for that purpose?


shouldn't that be a current bun? icon_wink.gif


That's a shocking joke icon_lol.gif

I'll just get me' coat...
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Aug 30, 2006 6:13 pm    Post Subject:
Reply with quote Thanks

RF Lighting wrote:
ban-all-sheds wrote:
Surely currant buns are the best for that purpose?


shouldn't that be a current bun? icon_wink.gif

No - it's a homophonic pun.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Wed Aug 30, 2006 6:18 pm    Post Subject:
Reply with quote Thanks

homophonic bun, you mean.
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10753
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Wed Aug 30, 2006 6:26 pm    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
No - it's a homophonic pun.


Sorry I don't know what that word means.
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Wed Aug 30, 2006 6:29 pm    Post Subject:
Reply with quote Thanks

A pun is a humerous wordplay with words that sound the same.

"Homophonic" means sounds the same.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Aug 30, 2006 8:12 pm    Post Subject:
Reply with quote Thanks

But are spelled differently.

Can also be homographic - same spelling, different meanings, e.g. "Being in politics is just like playing golf: you are trapped in one bad lie after another."

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
2A/3A fuse to discriminate with 16A b-curve MCB? 31 960 Mon Oct 05, 2009 12:46 pm
Spur from Boiler Circuit for Volt-Free Switching Thermostat 6 380 Thu Jan 24, 2008 9:08 pm
Extractor fan switching 4 160 Sat Feb 02, 2008 5:12 pm
when switching bedroom light on 15 660 Wed Jan 16, 2008 7:46 am
Drayton Digistat +2 works, but not switching heating... 5 840 Sat Dec 22, 2007 12:36 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.