6mm vs 10mm cable for electric shower

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
gst300

from United Kingdom

Joined: 28 Mar 2009
Posts: 8
Location: United Kingdom

PostPosted: Wed Mar 16, 2011 10:36 pm Reply with quote

I am replacing a 9kw electric shower with a 10.8kw - or I was until I was told I need to replace the existing 6mm cable with 10mm cable. Is this necessary? What are the consequences if I don't? If it is necessary then it is beyond my capabilities so should I then pay someone to do it or buy another 9kw shower?

All advise greatly appreciated

PS: I am a single mum on a tight budget so the cheapest solution is the best one for me
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
onlyfitidealboilers

from United Kingdom

Joined: 11 Jan 2010
Posts: 2023
Location: Aberdeen,
United Kingdom
Thanked: 149 times

PostPosted: Wed Mar 16, 2011 10:43 pm Reply with quote

the shower could draw a lot of electric and the cable may
burn out due to lenth of run etc will req 10mm tho
Back to top
The following user says thank you to onlyfitidealboilers for this useful post:
gst300 (17 Mar 2011)
 Alert Moderators
seco services

from United Kingdom

Joined: 03 Dec 2007
Posts: 15607
Location: Essex,
United Kingdom
Thanked: 1240 times

PostPosted: Wed Mar 16, 2011 10:53 pm Reply with quote

gst300 wrote:

PS: I am a single mum on a tight budget so the cheapest solution is the best one for me


is it in my eyes the safest solution is the best one.
Back to top
 Alert Moderators
1john

from United Kingdom

Joined: 03 Oct 2009
Posts: 3349
Location: West Glamorgan,
United Kingdom
Thanked: 340 times

PostPosted: Thu Mar 17, 2011 8:35 am Reply with quote

The 10,8kw shower wont work on the circuit as it is, if it's constucted safely. It will blow the fuse every time you switch it on. You need to replace like for like if you want to keep the job price to a minimum.

Seco services comment is very very true. You need a safe competent job by a tradesman who will test this work is electrically safe. Not a cheap job. Pop in the electricial forum and read the 'so sad' thread icon_sad.gif
Back to top
The following user says thank you to 1john for this useful post:
gst300 (17 Mar 2011)
 Alert Moderators
gst300

from United Kingdom

Joined: 28 Mar 2009
Posts: 8
Location: United Kingdom

PostPosted: Thu Mar 17, 2011 2:30 pm Reply with quote

Thanks guys. I suppos that's pretty much what I expected to hear icon_sad.gif. Think my cheapest option is to buy another 9kw shower, and avoid the rewiring bit.

Thanks again for the advice
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 36609
Location: Hampshire,
United Kingdom
Thanked: 1352 times

PostPosted: Thu Mar 17, 2011 2:59 pm Reply with quote

You haven't got a combi boiler have you? if you have a cylinder, where is it, and the cold tank (distance and height) in relation to the shower?
Back to top
 Alert Moderators
gst300

from United Kingdom

Joined: 28 Mar 2009
Posts: 8
Location: United Kingdom

PostPosted: Thu Mar 17, 2011 3:10 pm Reply with quote

No combi boiler. Cold tank in loft - above shower about 6-7metres away. Have had no probs since I moved in (4 years ish) until 2 months ago when shower stopped working and is leaking water. Have now been given a brand new 10.8kw shower - same make, so minimal fuss regarding installation (or so I thought!)

What am I losing by buying a smaller (and cheaper) 7 or 8 kw shower?
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 36609
Location: Hampshire,
United Kingdom
Thanked: 1352 times

PostPosted: Thu Mar 17, 2011 3:19 pm Reply with quote

less hot water from a less powerful shower (or the same amount of water but not as hot)

electric showers are quite weedy, especially in winter when the incoming water is colder.
Back to top
 Alert Moderators
ajrobb

from United Kingdom

Joined: 23 Jan 2010
Posts: 1656
Location: Sussex,
United Kingdom
Thanked: 162 times

PostPosted: Thu Mar 17, 2011 3:28 pm Reply with quote

I suggest you check the rating of the fuse or circuit breaker for the shower in your consumer unit (fuse box).
Assuming winter water temperature of 5C and shower temperature of 38C:
32 A = 7.6 kW (3.4 litre/min)
40 A = 9.6 kW (4.2 litre/min)
45 A = 10.8 kW (4.8 litre/min)


Last edited by ajrobb on Thu Mar 17, 2011 3:32 pm, edited 1 time in total
Back to top
 Alert Moderators
gst300

from United Kingdom

Joined: 28 Mar 2009
Posts: 8
Location: United Kingdom

PostPosted: Thu Mar 17, 2011 3:32 pm Reply with quote

Thanks for that. Think I will get new 9kw - can live with weedy I suppose, but maybe not weedier icon_smile.gif
Back to top
 Alert Moderators
1john

from United Kingdom

Joined: 03 Oct 2009
Posts: 3349
Location: West Glamorgan,
United Kingdom
Thanked: 340 times

PostPosted: Thu Mar 17, 2011 5:05 pm Reply with quote

The pressure releive valve may have gone on the shower and you may be able to get a replacment from the shower doctor website which will be cheaper than buying a new shower.
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17444
Location: Londonderry,
United Kingdom
Thanked: 1737 times

PostPosted: Thu Mar 17, 2011 5:07 pm Reply with quote

This will depend on the length of run to calculate voltage drop and the method it is installed.
6mm Twin and earth can carry 47A if clipped direct (ref method C)
if the the length of the run is less than 33.5 Metres, the voltaged dropped is within the permitted range.
10.8Kw/230V
=46.96A
It's borderline but you don't need to upgrade your cable, providing it's clipped direct, no thermal insulation, run is less than 33.5M


Last edited by PrenticeBoyofDerry on Thu Mar 17, 2011 8:57 pm, edited 1 time in total
Back to top
 Alert Moderators
simond

from United Kingdom

Joined: 26 Oct 2004
Posts: 4071
Location: Surrey,
United Kingdom
Thanked: 273 times

PostPosted: Thu Mar 17, 2011 7:38 pm Reply with quote

But the 10.8Kw shower should be fused/protected at 50A.

And then the protection is beyond the current capacity of the cable, and that is without any external factors applied.

I agree it is borderline, but in the wrong direction. Strictly speaking, the job can''t be done.
Back to top
 Alert Moderators
PrenticeBoyofDerry

from United Kingdom

Joined: 30 Jun 2009
Posts: 17444
Location: Londonderry,
United Kingdom
Thanked: 1737 times

PostPosted: Thu Mar 17, 2011 8:59 pm Reply with quote

Again borderline but by putting a 45A protective device on the circuit, it would be possible.
I don't think the overload that will be applied for the period of a shower would be too, disruptive.
Back to top
 Alert Moderators
PEDANTICVINDICTIVEMAN

from Western Sahara

Joined: 10 Jul 2004
Posts: 6574
Location: Western Sahara
Thanked: 1035 times

PostPosted: Thu Mar 17, 2011 10:30 pm Reply with quote

I "once" ran a 6mm cable 21 meters, which I was told by an electrician who worked it out on his calculator was the max for an 8.5Kw shower and ok, never again, the cable got shiny and rather hot after 20 minutes of use icon_cry.gif
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
shower electric cable installation 6 500 Sat Jun 16, 2007 9:50 am
electric shower and cable size 7 820 Fri Sep 17, 2004 3:00 pm
Gas pipe - Electric cable 14 1140 Thu Sep 07, 2006 9:24 am
Electric cable in heating pipe notch 5 100 Sat Nov 12, 2011 9:49 am
shower cable (flex) too short 7 380 Sun Apr 18, 2010 5:43 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.