gst300

Joined: 28 Mar 2009 Posts: 8 Location: United Kingdom
|
Posted: Wed Mar 16, 2011 10:36 pm |
|
|
I am replacing a 9kw electric shower with a 10.8kw - or I was until I was told I need to replace the existing 6mm cable with 10mm cable. Is this necessary? What are the consequences if I don't? If it is necessary then it is beyond my capabilities so should I then pay someone to do it or buy another 9kw shower?
All advise greatly appreciated
PS: I am a single mum on a tight budget so the cheapest solution is the best one for me |
|
| Back to top |
|
|
|
If you do not want to see this advert, click here to login or if you are new click here to join free. |
 |
onlyfitidealboilers

Joined: 11 Jan 2010 Posts: 1592 Location: Aberdeen, United Kingdom Thanked: 98 times
|
Posted: Wed Mar 16, 2011 10:43 pm |
|
|
the shower could draw a lot of electric and the cable may
burn out due to lenth of run etc will req 10mm tho |
|
| Back to top |
The following user says thank you to onlyfitidealboilers for this useful post:
gst300 (17 Mar 2011) |
| Alert Moderators
|
|
|
|
 |
seco services

Joined: 03 Dec 2007 Posts: 15464 Location: Essex, United Kingdom Thanked: 1215 times
|
Posted: Wed Mar 16, 2011 10:53 pm |
|
|
| gst300 wrote: |
PS: I am a single mum on a tight budget so the cheapest solution is the best one for me |
is it in my eyes the safest solution is the best one. |
|
| Back to top |
|
|
|
 |
1john

Joined: 03 Oct 2009 Posts: 3336 Location: West Glamorgan, United Kingdom Thanked: 336 times
|
Posted: Thu Mar 17, 2011 8:35 am |
|
|
The 10,8kw shower wont work on the circuit as it is, if it's constucted safely. It will blow the fuse every time you switch it on. You need to replace like for like if you want to keep the job price to a minimum.
Seco services comment is very very true. You need a safe competent job by a tradesman who will test this work is electrically safe. Not a cheap job. Pop in the electricial forum and read the 'so sad' thread  |
|
| Back to top |
|
|
|
 |
gst300

Joined: 28 Mar 2009 Posts: 8 Location: United Kingdom
|
Posted: Thu Mar 17, 2011 2:30 pm |
|
|
Thanks guys. I suppos that's pretty much what I expected to hear  . Think my cheapest option is to buy another 9kw shower, and avoid the rewiring bit.
Thanks again for the advice |
|
| Back to top |
|
|
|
 |
JohnD

Joined: 15 Nov 2005 Posts: 34358 Location: Hampshire, United Kingdom Thanked: 1087 times
|
Posted: Thu Mar 17, 2011 2:59 pm |
|
|
You haven't got a combi boiler have you? if you have a cylinder, where is it, and the cold tank (distance and height) in relation to the shower? |
|
| Back to top |
|
|
|
 |
gst300

Joined: 28 Mar 2009 Posts: 8 Location: United Kingdom
|
Posted: Thu Mar 17, 2011 3:10 pm |
|
|
No combi boiler. Cold tank in loft - above shower about 6-7metres away. Have had no probs since I moved in (4 years ish) until 2 months ago when shower stopped working and is leaking water. Have now been given a brand new 10.8kw shower - same make, so minimal fuss regarding installation (or so I thought!)
What am I losing by buying a smaller (and cheaper) 7 or 8 kw shower? |
|
| Back to top |
|
|
|
 |
JohnD

Joined: 15 Nov 2005 Posts: 34358 Location: Hampshire, United Kingdom Thanked: 1087 times
|
Posted: Thu Mar 17, 2011 3:19 pm |
|
|
less hot water from a less powerful shower (or the same amount of water but not as hot)
electric showers are quite weedy, especially in winter when the incoming water is colder. |
|
| Back to top |
|
|
|
|
|
 |
ajrobb

Joined: 23 Jan 2010 Posts: 1656 Location: Sussex, United Kingdom Thanked: 162 times
|
Posted: Thu Mar 17, 2011 3:28 pm |
|
|
I suggest you check the rating of the fuse or circuit breaker for the shower in your consumer unit (fuse box).
Assuming winter water temperature of 5°C and shower temperature of 38°C:
32 A = 7.6 kW (3.4 litre/min)
40 A = 9.6 kW (4.2 litre/min)
45 A = 10.8 kW (4.8 litre/min)
Last edited by ajrobb on Thu Mar 17, 2011 3:32 pm, edited 1 time in total |
|
| Back to top |
|
|
|
 |
gst300

Joined: 28 Mar 2009 Posts: 8 Location: United Kingdom
|
|
| Back to top |
|
|
|
 |
1john

Joined: 03 Oct 2009 Posts: 3336 Location: West Glamorgan, United Kingdom Thanked: 336 times
|
Posted: Thu Mar 17, 2011 5:05 pm |
|
|
The pressure releive valve may have gone on the shower and you may be able to get a replacment from the shower doctor website which will be cheaper than buying a new shower. |
|
| Back to top |
|
|
|
 |
PrenticeBoyofDerry

Joined: 30 Jun 2009 Posts: 13599 Location: Londonderry, United Kingdom Thanked: 1174 times
|
Posted: Thu Mar 17, 2011 5:07 pm |
|
|
This will depend on the length of run to calculate voltage drop and the method it is installed.
6mm Twin and earth can carry 47A if clipped direct (ref method C)
if the the length of the run is less than 33.5 Metres, the voltaged dropped is within the permitted range.
10.8Kw/230V
=46.96A
It's borderline but you don't need to upgrade your cable, providing it's clipped direct, no thermal insulation, run is less than 33.5M
Last edited by PrenticeBoyofDerry on Thu Mar 17, 2011 8:57 pm, edited 1 time in total |
|
| Back to top |
|
|
|
 |
simond

Joined: 26 Oct 2004 Posts: 3980 Location: Surrey, United Kingdom Thanked: 257 times
|
Posted: Thu Mar 17, 2011 7:38 pm |
|
|
But the 10.8Kw shower should be fused/protected at 50A.
And then the protection is beyond the current capacity of the cable, and that is without any external factors applied.
I agree it is borderline, but in the wrong direction. Strictly speaking, the job can''t be done. |
|
| Back to top |
|
|
|
 |
PrenticeBoyofDerry

Joined: 30 Jun 2009 Posts: 13599 Location: Londonderry, United Kingdom Thanked: 1174 times
|
Posted: Thu Mar 17, 2011 8:59 pm |
|
|
Again borderline but by putting a 45A protective device on the circuit, it would be possible.
I don't think the overload that will be applied for the period of a shower would be too, disruptive. |
|