PostPosted: Sun Jun 05, 2005 10:01 am    Post Subject:
Selection of MCB
Reply with quote Thanks

How we will have to select the MCB based on thier Grades (A, B, C, D...)


Earlier of any one your response is appreciated.,

K.Jeyabalan


Last edited by Jeyabalan.K on Sun Jun 05, 2005 10:03 am, edited 1 time in total
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
pdcelec

from United Kingdom

Joined: 05 Jun 2005
Posts: 707
Location: Birmingham,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jun 05, 2005 10:02 am    Post Subject:
Reply with quote Thanks

What is it going to be used for?
Back to top
 Alert Moderators
Jeyabalan.K

from India

Joined: 05 Jun 2005
Posts: 2
Location: India
Thanked: 0 times

PostPosted: Sun Jun 05, 2005 10:21 am    Post Subject:
Reply with quote Thanks

pdcelec wrote:
What is it going to be used for?



For COmputer applications.

2. How the grades are to be seen before selection of MCB's for any applications?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Sun Jun 05, 2005 2:17 pm    Post Subject:
Reply with quote Thanks

The things that affect the choice are tolerance of surges, disconnection time needed and earth-fault-loop impedance. You probably shouldn't be making the selection if you don't understand the factors involved.

Also, I doubt if anyone here is familiar with Indian supply systems and regulations...

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6931
Location: United Kingdom
Thanked: 16 times

PostPosted: Sun Jun 05, 2005 4:50 pm    Post Subject:
Reply with quote Thanks

1: as already mentioned it depends on the load
2: you mention A B C and D in our system of breakers there is no such thing as type A are you using kit made to british standards and are you actually in india
3: assuming you are using uk breakers you generally wan't to use type B unless you have a good reason not to (such as equipment with large switch on surges) with type C and D you need far lower impedances to ensure fast fault disconnection so only use theese if you know what your doing.
Back to top
 Alert Moderators
mapj1

from United Kingdom

Joined: 24 Nov 2004
Posts: 1040
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Jun 06, 2005 2:02 pm    Post Subject:
Reply with quote Thanks

India follows the old 'round pin' radial British system, in red and black PVC, still has a lot of class zero (metal case no earth, not double insulated)gear. Some of us are remarkably familiar with it. icon_confused.gif
The Indian wiring regs are based on BS7671 (like ireland, like Malta - its the old colonial influence what-ho)
now i've finished berating my colleagues, to the question,
If you know the live-earth fault resistance, which sets the prospective maximum fault current, and the type of load you can determine what you need.
Type a (instant trip) is never used, and isn't readily available in the UK
Type B, C D all have two mechanisms for tripping,
1) a thermal part which (like a fuse) does not fire for very brief overloads, but will trip before the cables get dangerously hot. This sets the rating of the trip, and the working load and cable size determine that.
2) a magnetic part, with a much higher tripping current, that operates near instantly. The secret is to allow normal cold filament, start motor type surges, without tripping the breaker, and yet still operate near instantly if the cable is cut or a dead-short is applied.

Most of the 230V world ( Russia, China and the EU) uses 16A radials with type C breakers (5 to 10X transient rating), we tend to use 32 A breaker with a type B (2 to 5 X transient rating) characteristic -the effect is the same, the surges for domestic equipment like TV or fridge are in the range 50-80A, but a 200A dead short fault guarantees instant tripping.
Opinion is divided over type B or C at 6A for separated lighting circuits, actually both protect the wire against overload, but B can be a bit too frisky on installations with many lamps switching together (a cold tungsten filament is about 1/12 the resistance of a hot one.)
Type D is normally reserved for heavy machines and is best decided only in consultation with the makers.
Hope that gets you started

__________________
regards Mike(G7VZY)
-STICKY Reference Info @ top of forum, Has diagrams & answers to common probs-
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon Jun 06, 2005 6:05 pm    Post Subject:
Reply with quote Thanks

mapj1 wrote:
Type a (instant trip) is never used, and isn't readily available in the UK

Dunno about a Type A - I did find reference to a Type Z recently (counter-intuitively it trips faster than a B, not as you might expect from the letter progression only after several days at 1000x In...)



Code:
        ------- Thermal Trip -------    ------ Magnetic Trip ------
        Must not trip      Must Trip    Must not trip     Must trip
        over 1 hour        under 1hr    over 100ms        at 100ms

TYPE-B   1.13xRC            1.45xRC        3xRC             5xRC

TYPE-C   1.13xRC            1.45xRC        5xRC            10xRC

TYPE-D   1.13xRC            1.45xRC       10xRC            16xRC

TYPE-E   1.05xRC            1.35xRC       14xRC            18xRC

TYPE-G   1.05xRC            1.35xRC        8xRC            10xRC

TYPE-Z   1.05xRC            1.35xRC        2xRC             3xRC


They're American breakers though - don't know how much the curves differ from European ones.

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
pdcelec

from United Kingdom

Joined: 05 Jun 2005
Posts: 707
Location: Birmingham,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jun 06, 2005 9:24 pm    Post Subject:
Reply with quote Thanks

Jeyabalan.K wrote:
pdcelec wrote:
What is it going to be used for?



For COmputer applications.

2. How the grades are to be seen before selection of MCB's for any applications?


If it is for a computer installation then section 607 will also come into effect
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Cable Selection And Connections 25 800 Sun Sep 21, 2008 11:34 am
MCB selection 2 540 Sun Jul 13, 2008 10:17 am
Cable Selection for Ring Main 5 580 Mon Oct 01, 2007 7:34 pm
Boiler override selection 5 260 Sun Nov 16, 2008 1:24 pm
SWA selection 11 340 Tue Jan 06, 2009 6:01 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.