Maximum earth fault loop impedance for a BS1362 fuse

Joined
14 Sep 2004
Messages
18
Reaction score
0
Country
United Kingdom
Could someone please tell me the maximum earth fault loop impedance for a BS1362 3A fuse or where I can find the info. I need both 5sec and 0.4 sec disconnection times. The 13A spec is in the regs but not the 3A.
 
Sponsored Links
Probably not included in the regs, since no guarantee that a user would fit that fuse rating in a 13A plug. (Worst case situation adopted).
 
I was told by an NICEIC inspector to add it to a minor works cert for a fused spur supplying a spa bath. He said not only to mention the 32A ring breaker Zs but also to split the box and add the spec for the 3A fuse as well. What do you reckon?
 
Sponsored Links
The tables are for specific devices such as the BS1362 etc so as long as the readings fall within the specs of that you are ok, so no need to bring the rating into it?
 
Newspark said:
I was told by an NICEIC inspector to add it to a minor works cert for a fused spur supplying a spa bath. He said not only to mention the 32A ring breaker Zs but also to split the box and add the spec for the 3A fuse as well. What do you reckon?
I reckon that's NICEIC making up their own regulations, again...
 