shed electrics
I would be grateful for some advice on the installation of electricity to my shed.
I'm going to put 4mm or 6mm SWA cable underground with junction box either end, as the entire run from main consumer box to shed consumer box is approx. 20m.
I'll be using a 30A MCB in the main consumer unit, and have a dedicated shed consumer box with a 63A RCD, along with a 16A and 6A MCB's.
This will be to power a light or 2, along with maybe 3 sockets for lawnmower/portable stereo/exercise bike, though not all used at once.
My query is with the SWA cable.
I was reading a DIY manual on electrics, and they recommended the conduit/standard cable route, as opposed to the SWA cable option.
This because of having to fit the glands, and to prevent deterioration of the cable interiors.
Surely fitting the glands to the SWA isn't a hard job? I am a keen DIY'er and thought this job wouldn't be too advanced.
My second query is with the earth cable, and was advised to fit an earth rod next to the shed, and connect the earth cable to this from the shed consumer unit. But do I still connect the earth from the main consumer to the shed consumer unit?
Lastly, is 3 core SWA simply just 2 core and earth?
Joined: 03 Jan 2003 Posts: 23346 Location: Sussex, United Kingdom Thanked: 5 times
Posted: Sun Jul 10, 2005 8:03 am Post Subject:
bertoli wrote:
So a standard straight earth connection from main to shed consumer units(via junction boxes) would suffice?
so long as the boxes are metal, and you connect to the box or use the "banjo" supplied with glands it wuill be fine
bertoli wrote:
Would you be aware why the use of an earth rod is advised? It was recommended as the shed was 15m away from house.
thanks for your help
no idea, i didn't write the book, but it may be the writer thought it a good idea, but it can cause motre problems, and also as i said, how would you test it?
__________________ Do you like music Mr Finch?
Forum = Opinions
Joined: 10 Jul 2005 Posts: 19 Location: United Kingdom Thanked: 0 times
Posted: Sun Jul 10, 2005 10:34 pm Post Subject:
breezer wrote:
no idea, i didn't write the book, but it may be the writer thought it a good idea, but it can cause motre problems, and also as i said, how would you test it?
With you quite rightly asking how I would test it, how would I test that earthing the shed consumer unit to the main consumer unit would be enough, or is it accepted that all wiring connected would be earthed properly as long as it is installed correctly to the main board?
Joined: 03 Jan 2003 Posts: 23346 Location: Sussex, United Kingdom Thanked: 5 times
Posted: Sun Jul 10, 2005 10:38 pm Post Subject:
so long as you install the glands corretcy use suitable galvanised boxes and or banjos yes it should be fine, that said get a an electrician to do it for you
__________________ Do you like music Mr Finch?
Forum = Opinions
Joined: 10 Jul 2005 Posts: 19 Location: United Kingdom Thanked: 0 times
Posted: Mon Jul 11, 2005 9:32 am Post Subject:
ban-all-sheds wrote:
1) Are you aware of the requirements of Part P of the Building Regulations vis-a-vis this work?
Does Part P regulations apply the same in Scotland, as it does in the rest of the UK? I thought this only applied to England/Wales, and what if the job was finished last year ?
ban-all-sheds wrote:
2) Do a search here for terms like shed, garage, garden, outside, outbuilding, outhouse - this general topic has been covered many times before.
I always make a point of searching through the forum before asking questions. Maybe I failed to see it, but I couldn't find a similar query regarding earth rods, or using the 3rd core in a 3 core SWA cable as an earth. With me failing to see similar questions having been asked, I thought it proper to ask just to be on the safe side.
ban-all-sheds wrote:
3) Testing is important - don't just assume everything is OK.
I am aware of this, but breezer asked me on two occasions "how would/could I check that the earth rod was working properly?"