How big a boiler do I need?


 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Search this topic :: View previous topic :: View next topic  
Author Message
hjalfi

from United Kingdom

Joined: 15 Apr 2005
Posts: 42
Location: Berkshire,
United Kingdom

PostPosted: Wed Aug 10, 2005 3:10 pm Reply with quote

I'm attempting to replace my existing back boiler and indirect tank with a condensing boiler. Unfortunately, I'm having a lot of trouble working out just how big a boiler I need.

My house is a 1900 terrace with three bedrooms, six radiators, and one bathroom. So far, the estimates of what I need vary from 30kW (from the plumber who's going to fit the boiler) to 15kW (from B&Q)... which doesn't really help me much.

It does occur to me that given that a really powerful electric shower is 10kW, a 30kW boiler could well be overkill for me. But I do need it able to produce enough hot water for a shower *and* run the CH at the same time.

Any suggestions?
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
htgeng

from United Kingdom

Joined: 01 Jun 2004
Posts: 2123
Location: Lancashire,
United Kingdom
Thanked: 98 times

PostPosted: Wed Aug 10, 2005 3:27 pm Reply with quote

hjalfi wrote:


Any suggestions?


15kw is realistic for the heating side. If you are keeping a cylinder then that is going to be enough for the hot water too.
Back to top
 Alert Moderators
hjalfi

from United Kingdom

Joined: 15 Apr 2005
Posts: 42
Location: Berkshire,
United Kingdom

PostPosted: Wed Aug 10, 2005 3:32 pm Reply with quote

Not enough sleep. I meant to say condensing combi boiler --- it'll be heating the water on demand, so no cylinder.

So if 15kW is all right for heat, plus 10kW for the hot water, that's 25; not far off the plumber's recommendation.
Back to top
 Alert Moderators
ChrisR

from United Kingdom

Joined: 24 Jul 2003
Posts: 23353
Location: London,
United Kingdom
Thanked: 1072 times

PostPosted: Wed Aug 10, 2005 3:46 pm Reply with quote

The smallest combi you'll get is 24kw. The HW will stop the CH, while it's being drawn.
I would recommend you spend a little extra to get a 28-30kW combi, because the improvement in the HW is quite noticeable, especially in the winter when the mains is v cold.
The boiler will be 35 - 150 more depending on make. The plumber might mention that the gas pipe needs to be bigger. Depending what's there if anything, & that could add a significant cost. If it's all new pipe and quite short there will probably be no difference.
Back to top
 Alert Moderators
hjalfi

from United Kingdom

Joined: 15 Apr 2005
Posts: 42
Location: Berkshire,
United Kingdom

PostPosted: Thu Aug 11, 2005 11:49 pm Reply with quote

Cool. Thanks.

Any suggestions as to a boiler make to go for, or more importantly, stay away from? The basic ones I'm looking at are Ravenheat or Biacsi --- the general impression I'm getting is that they're about average.
Back to top
 Alert Moderators
Slugbabydotcom

from United Kingdom

Joined: 10 Mar 2005
Posts: 3505
Location: Middlesbrough,
United Kingdom
Thanked: 83 times

PostPosted: Fri Aug 12, 2005 3:58 am Reply with quote

hjalfi wrote:
Cool. Thanks.

Any suggestions as to a boiler make to go for, or more importantly, stay away from? The basic ones I'm looking at are Ravenheat or Biacsi --- the general impression I'm getting is that they're about average.


This is the one question that everyone seems to clam up on. Theres so many factors involved and the true answer will not be known till several years after the installation. Theres not a boiler out there that hasnt been tested for safety and economy hence the CE marks and sap ratings.They all deserve some consideration apart from the french ones. Have a look at THIS if you want to throw economy into the equation
The best way to get an idea when looking for reliability is to go into a gas spares stockists and ask what they sell most spare parts for but this has to be weighed against the number of boilers in service How the hell can you do that, apart from guessing at how many boilers there are of each make out there?

Here's just my opinions / thoughts on it with all due respects to opinions of other posters.
Ravenheat CSI 85 T. After 5 years of production they seem to have their act together on this after changing their wet pocket ch thermistors for a dry version and slinging everything that honeywell have started making in china. Band A rated atmospheric. British company iso 9001. It won an idhee award and they claim icon_rolleyes.gif a 22.5% share of condensing combi market courtesy of the sheds.
The condensate trap is a pig to get to, take a 12mm ring spanner when you fit it and a stanley knife to cut one knobbly bit off the flue gasket.

Biasi M96. garda HE and riva HE Band B rated atmospheric. They claim icon_rolleyes.gif a 20% share of the market again thanks to the sheds. Easier to fit and less teething troubles.Less efficient, more output. Condensate trap is hard to get to and so is the plate heat exchanger unless you have a 4 mm variable angle allen key then its a doddle.

An interesting thing about biasi is they make a couple of boilers for Ideal so watch out for the 'skoda vw audi' type scam .... Same product different badge.

One I have got my eye on is the new vokera linea HE with the premix burner.
Its a natural progression from their other stuff. They have found a cheap way of producing a condensing heat exchanger and have an own make programmable roomstat and it seems to be electronically superior but will it stand the test of time?

Generally though when you buy any boiler:
the heat exchangers and diverter valves are made by giannoni
the gas valve is SIT Dungs or honeywell
pumps are wilo or grundfoss
premix burners are Reillo group /giannoni
Time clocks are graslin



icon_mad.gif icon_mad.gif icon_mad.gif icon_mad.gif icon_confused.gif icon_confused.gif icon_confused.gif icon_confused.gif icon_confused.gif



No wonder the mind boggles .... Sod it just get the cheapest then if it does go wrong you just throw it away and get another icon_lol.gif


Last edited by Slugbabydotcom on Tue Jan 15, 2008 4:51 am, edited 1 time in total
Back to top
 Alert Moderators
DP

from United Kingdom

Joined: 10 Dec 2003
Posts: 6508
Location: Glasgow,
United Kingdom
Thanked: 747 times

PostPosted: Fri Aug 12, 2005 6:50 am Reply with quote

Slugbaby hits the nail on the head.

Reading the post I get the impression the homeowner is opening a can of worms. If he can not comprehend that a smallest combi is rated at 20kw, it can only provide HW OR CH at any one time, is comparing the output to that of an electric shower rated 10kw, what chance has he got of making a successful fit when he opens the box and starts putting things together.
Back to top
 Alert Moderators
hjalfi

from United Kingdom

Joined: 15 Apr 2005
Posts: 42
Location: Berkshire,
United Kingdom

PostPosted: Fri Aug 12, 2005 11:36 am Reply with quote

Thanks, SB, tons of useful information.

I'm actually not particularly bothered about how difficult they are to service or install --- while I like explosions, I wouldn't want to live in one, and so it's CORGI all the way. I think I'll go for a 30kW if I can find one; it's probably overkill for my requirements, but as you say, it's very little more money and will solve any possible flow rate problems.

The only problem seems to be that I want a condensing boiler, and condensing combis are physically larger than non-condensing --- and my space is limited. I can't seem to find any details on the various product web sites on how much clearance they require. I've heard that they tend to need anything from 100mm to 200mm below, but Ravenheat's publicity shots clearly show boilers in cupboards with much less clearance than that...
Back to top
 Alert Moderators
Slugbabydotcom

from United Kingdom

Joined: 10 Mar 2005
Posts: 3505
Location: Middlesbrough,
United Kingdom
Thanked: 83 times

PostPosted: Sat Aug 13, 2005 3:18 am Reply with quote

For clearance details contact manufacturers. Wont take long to email them or give them a call

Riva compact HE 28kw
h 803
w 400
d 350

By comparison
Riva compact [non condensing]
h 703
w 400
d 325

CSI 85 T 25kw
h 850
w 450
d 350


Vokera syntesi 29e
h 820
w 450
d 350
clearances
sides 12
top 150
bottom 150
front 600

Details for Vokera linea HE arent out yet AFAIK, but I was at vokera last week looking at one and heres my guesstimate
h 840
w 400
d 360

Output of 25 kw and over gives at least an adequate flow rate IMHO

28. 29 or 30 kw All give a formidable flow rate and you wouldnt tell the difference

Most combi's will modulate down to about 11 kw on the heating side. They just need the big inputs for heating hot water
All combis will stop heating rads when there is a call for hot water


Riva compact he is looking the best bet of those Ive mentioned for you from what you have told me.

Remember to take your blinkers off when selecting a boiler. There are other makes out there which may fit your bill better.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Ideal Icos m3080 boiler not staying alight 5 1120 Tue Apr 20, 2010 2:27 pm
Firebird Super Q Boiler - Elp! 3 100 Sat Jan 15, 2011 11:03 am
Combination boiler 4 300 Thu Aug 26, 2010 10:33 am
Pressure vessel on cold water supply to boiler? 9 640 Wed Mar 31, 2010 8:43 pm
general combi boiler query, running noise 2 160 Tue Mar 09, 2010 11:08 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.