connecting cable

This topic originated from the How to page called Extending a ring circuit using junction boxes
Click here to return to the page called Extending a ring circuit using junction boxes.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
uncletam

from United Kingdom

Joined: 13 Aug 2005
Posts: 1
Location: Perthshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Aug 13, 2005 6:56 am    Post Subject:
connecting cable
Reply with quote Thanks

hi there i am connecting cable in a bedroom where 2 sockets go to the ring so there are four 2.5mm cables needing connected. Do i use a block of cable connectors as i have tried a 20 amp junction box and that has no where near able to handle the size of the cable. Block connectors are used in the attic are they safe to use on a ring main? have been told these can over heat!
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
slippyr4

from United Kingdom

Joined: 12 Jul 2005
Posts: 681
Location: Bedfordshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Aug 13, 2005 6:59 am    Post Subject:
Reply with quote Thanks

que? why four cables? describe the circuit better.

a 20A junction box is a definate no-no. junction boxes should be in accesible locations, and you'd need something rated at 32A for a ring main anyway, not 20A.
Back to top
 Alert Moderators
Qedelec

from United Kingdom

Joined: 22 Jun 2005
Posts: 1141
Location: Birmingham,
United Kingdom
Thanked: 0 times

PostPosted: Mon Aug 15, 2005 11:49 am    Post Subject:
Reply with quote Thanks

Sounds to me like you have two spurs off a ring main at the socket interface and that is definitely not allowed.
Rule of thumb, if the cables won't go into the terminals then there is something very wrong.

Consider adding another outlet next to this one and connect the two ends of the ring to each. Then connect them together with a new peice of cable.
You will then have two connection points to which you can connect the spurs, one to each. That will satisfy the regs.

__________________
"Shock me again and I'm gonna turn you off"
Life's a beach.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Advice connecting cable to poleswitch 3 260 Thu Apr 22, 2004 6:24 pm
Connecting 25mm2 cable to a 45a switch 4 440 Thu Aug 09, 2007 5:16 pm
Cable connecting consumer units 3 860 Fri Mar 31, 2006 7:40 am
Connecting Armoured Cable 22 1240 Tue Oct 02, 2007 8:37 am
SWA Cable connecting to normal flex via junction box 6 1160 Tue Apr 03, 2007 1:24 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.