testing earth fault loop impedance

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 15902
Location: Yorkshire,
United Kingdom
Thanked: 220 times

PostPosted: Tue Aug 30, 2005 6:37 pm Reply with quote

how is this done? Is expensive kit required? If so, how does this kit work? Just curious as so how one finds the resistance of something (earth rod) without passing a current through it and measuring the other side icon_confused.gif
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
andy

from United Kingdom

Joined: 14 Sep 2004
Posts: 3971
Location: United Kingdom
Thanked: 2 times

PostPosted: Tue Aug 30, 2005 6:38 pm Reply with quote

crafty1289 wrote:
how is this done? Is expensive kit required? If so, how does this kit work? Just curious as so how one finds the resistance of something (earth rod) without passing a current through it and measuring the other side icon_confused.gif


get an earth fault tester. put the earth lead on earht, and live on live. wait a few secs and there you have it - the earth fault impedance

as for price - i got mine for 70 from ebay!
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 15902
Location: Yorkshire,
United Kingdom
Thanked: 220 times

PostPosted: Tue Aug 30, 2005 9:12 pm Reply with quote

Quote:
wait a few secs and there you have it - the earth fault impedance


dont give much away, do you? How exactly does this thing work? And what exactly are you measuring the resistance (ohms) between?
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 8429
Location: United Kingdom
Thanked: 197 times

PostPosted: Tue Aug 30, 2005 9:16 pm Reply with quote

its the loop impedance between live and earth.

i'm not sure exactly how they measure it, my guess is they use a varying load and measure how it affects the voltage but i don't know for sure. Sparkys just treat the things as black boxes.

theres also meters for testing rods theese are used to measure the resistance of a rod in isolation and involve several temporary test electrodes a long distance from the rod. Afaict theese meters are only generally used when putting in a rod for a generator install or similar where you can't just measure loop impedance as your generator is on the same rod as your load.
Back to top
 Alert Moderators
mikely

from United Kingdom

Joined: 11 Feb 2005
Posts: 305
Location: Lancashire,
United Kingdom
Thanked: 72 times

PostPosted: Tue Aug 30, 2005 10:16 pm Reply with quote

Back to top
 Alert Moderators
pdcelec

from United Kingdom

Joined: 05 Jun 2005
Posts: 707
Location: Birmingham,
United Kingdom

PostPosted: Tue Aug 30, 2005 10:40 pm Reply with quote

plugwash wrote:
its the loop impedance between live and earth.

i'm not sure exactly how they measure it, my guess is they use a varying load and measure how it affects the voltage but i don't know for sure.


The meter injects a current into the circuit (25A, or 15mA for a non RCD trip type) and measures the volt drop. V= IR seems to cover this one.

The 25A are more accurate since the current also tests joints in conduit etc.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 8429
Location: United Kingdom
Thanked: 197 times

PostPosted: Tue Aug 30, 2005 11:18 pm Reply with quote

right but there is already voltage in the cuircuit so the forumulae is actually

R=dV/dI

however what i'm not sure of is how they compensate for other voltage variations that are not linked to the variation in test current (e.g. caused by other loads on the supply switching on and off etc).


as for rod testing from the TLC site it seems its done with a 4 wire ohmmeter type test arrangement with one of the pairs connected to the rod under test and the other pair connected to ground through temporary electrodes. provided the electrodes are far enough apart with this system the resistance of the temporary test electrodes to earth should have negligable effect on the overall resistance reading.
Back to top
 Alert Moderators
Lectrician

from United Kingdom

Joined: 18 Jul 2004
Posts: 7450
Location: Devon,
United Kingdom
Thanked: 270 times

PostPosted: Wed Aug 31, 2005 6:38 am Reply with quote

The loop tester puts a set impedance across L and E.

It measures the volts, mesaures the current flow throught its impedance, hence, it can calculate the Ze in ohms.

All loop testers work the same, and the impedance inside (probably just a resistor or a summet!) will get hot, and after to much work, will shut down.

You are measureing the resistance in ohms between live and earth - this is down the live all the way to the transformer, through the transformer coil, out the neutral and onto the earth. Then up the earth and back to the tester. A big loop!

The transformers internal resistance will be very low, and extreamly low on larger transformers (think of the cable sizes exiting the tranny, the internal coils will need to be sized according to current carrying capacity aswell! (although, they are allowed to run hotter).
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46147
Location: London,
United Kingdom
Thanked: 1659 times

PostPosted: Thu Sep 01, 2005 12:23 pm Reply with quote

Lectrician wrote:
The transformers internal resistance will be very low, and extreamly low on larger transformers (think of the cable sizes exiting the tranny, the internal coils will need to be sized according to current carrying capacity aswell! (although, they are allowed to run hotter).

Not too hot though:

http://205.243.100.155/frames/longarc.htm#Blowup
Back to top
 Alert Moderators
comms

from United Kingdom

Joined: 13 Nov 2004
Posts: 882
Location: Berkshire,
United Kingdom
Thanked: 8 times

PostPosted: Thu Sep 01, 2005 8:57 pm Reply with quote

Just took a look at the link to tlc for measuring efli it shows diagram of direct measurment, then states dissconnect equipotential bonding before conducting test, GN3 states the opposite(2.7.14) for direct measurement of Zs
Back to top
 Alert Moderators
pdcelec

from United Kingdom

Joined: 05 Jun 2005
Posts: 707
Location: Birmingham,
United Kingdom

PostPosted: Thu Sep 01, 2005 10:45 pm Reply with quote

comms wrote:
Just took a look at the link to tlc for measuring efli it shows diagram of direct measurment, then states dissconnect equipotential bonding before conducting test, GN3 states the opposite(2.7.14) for direct measurement of Zs


Who writes the regs? TLC or IEE. You decide.

Try this discussion on the topic http://www.iee.org/Forums/forum/messageview.cfm?catid=205&threadid=6173&enterthread=y
Back to top
 Alert Moderators
mits2hils

from United Kingdom

Joined: 29 Oct 2010
Posts: 3
Location: United Kingdom

PostPosted: Fri Oct 29, 2010 10:04 am Reply with quote

Steve wrote:
how is this done? Is expensive kit required? If so, how does this kit work? Just curious as so how one finds the resistance of something (earth rod) without passing a current through it and measuring the other side icon_confused.gif


felling icon_redface.gif about not knowing,, do what i did ,, goto ebay and type in this ,,Digital Multi Function Loop Tester (Socket and See) all the instructions are there it will tell you whats wrong and the fault,, then goto electriciandiy.co.uk and there you will proberbly find the right way to resolve your problem,, now you might just feel like icon_lol.gif good luck
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 35921
Location: Hampshire,
United Kingdom
Thanked: 1248 times

PostPosted: Fri Oct 29, 2010 10:14 am Reply with quote

if you seriously want to try it out of interest, not professionally, you can often buy a single-function old model, certification expired, very cheaply on fleabay.

beware of touching the earth probe (if it has one) or anything it is touching during testing as there is a momentary connection to L

edit: damn, a 5-year old post walks again icon_redface.gif
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 46147
Location: London,
United Kingdom
Thanked: 1659 times

PostPosted: Fri Oct 29, 2010 7:27 pm Reply with quote

mits2hils wrote:
felling icon_redface.gif about not knowing,, do what i did ,, goto ebay and type in this ,,Digital Multi Function Loop Tester (Socket and See) all the instructions are there it will tell you whats wrong and the fault,, then goto electriciandiy.co.uk and there you will proberbly find the right way to resolve your problem,, now you might just feel like icon_lol.gif good luck

I don't know whether to laugh or cry....
Back to top
 Alert Moderators
Grizzly

from United Kingdom

Joined: 18 Jun 2008
Posts: 288
Location: London,
United Kingdom
Thanked: 16 times

PostPosted: Fri Oct 29, 2010 11:09 pm Reply with quote

ban-all-sheds wrote:
mits2hils wrote:
felling icon_redface.gif about not knowing,, do what i did ,, goto ebay and type in this ,,Digital Multi Function Loop Tester (Socket and See) all the instructions are there it will tell you whats wrong and the fault,, then goto electriciandiy.co.uk and there you will proberbly find the right way to resolve your problem,, now you might just feel like icon_lol.gif good luck

I don't know whether to laugh or cry....


Cry, I reckon.
Apart from the ropey spelling, grammar & punctuation, and the resurrecting of a 5 year old thread, it doesn't look like 'electriciandiy.co.uk' even exists!
A great effort for a first post.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
diagram of an earth fault loop impedance path for TN-S and.. 7 15040 Sat Mar 06, 2010 2:18 pm
Earth Fault Loop Impedance 7 1680 Sun Jun 17, 2007 12:27 pm
2391 practical - Earth Fault Loop impedance 30 2880 Thu Aug 05, 2010 1:51 pm
Earth fault loop impedance 3 1020 Tue Sep 11, 2007 6:47 pm
Max Earth Fault Loop Impedance 8 1900 Tue Jun 10, 2008 4:46 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.