New instalation

This topic originated from the How to page called Identifying a faulty circuit
Click here to return to the page called Identifying a faulty circuit.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
walton

from United Kingdom

Joined: 11 Sep 2005
Posts: 11
Location: Hull,
United Kingdom
Thanked: 0 times

PostPosted: Sun Sep 11, 2005 4:20 pm    Post Subject:
New instalation
Reply with quote Thanks

We recently installed a new washing machine and dishwasher. Almost immediatly we felt electric shocks from both appliancies and wall socket securing screws. I immedialty switched the power off and checked the houses earthing. I tested the earth and was registering 110v on the earth while both appliancies were plugged in. once unplugged there was no reading. now i have installed a new CU with a 100A rcd with a 32 mcb for the kitchen sockets. there is still a reading of voltage in the earth but the RCD deos not trip, can you help
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Sun Sep 11, 2005 4:29 pm    Post Subject:
Reply with quote Thanks

You get a reading of 110v between earth and where? Which earth did you test, the Main Earth Terminal (near CU)?
Back to top
 Alert Moderators
yai46

from United Kingdom

Joined: 09 Sep 2005
Posts: 38
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Sep 11, 2005 4:37 pm    Post Subject:
Reply with quote Thanks

in my experience your probably find that that socket has not got an earth wire connected at the socket in which its connected to, if it has a switched fuse spur above worktop check the earth has not come adrift from the terminal
What it sounds like is voltage is being induced into the earth and pipes due to being no earth .
Back to top
 Alert Moderators
walton

from United Kingdom

Joined: 11 Sep 2005
Posts: 11
Location: Hull,
United Kingdom
Thanked: 0 times

PostPosted: Sun Sep 11, 2005 4:38 pm    Post Subject:
new installtion
Reply with quote Thanks

I got a reading both from the earth from the back of the socet after disconnecting and doing a reading to the earth feed, and from disconnecting the main earth feed in the CU
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Sun Sep 11, 2005 4:43 pm    Post Subject:
Reply with quote Thanks

So the measurement was between the machine and the house earth. Please be aware that what you did to obtain this reading is very dangerous. You must never disconnect an earth from a live circuit. The voltage you were seeing was more than likely due to a mains filter in the washing machine.
Back to top
 Alert Moderators
walton

from United Kingdom

Joined: 11 Sep 2005
Posts: 11
Location: Hull,
United Kingdom
Thanked: 0 times

PostPosted: Sun Sep 11, 2005 4:47 pm    Post Subject:
Reply with quote Thanks

Yes agreed but why is there a reading in the first place, and even with the new CU installed I still get a reading through the earth which again I tracked down to the new appliancies. could they both be faulty, and if so why isnt the RCD (which is an 80 A not 100) not tripping.
Back to top
 Alert Moderators
yai46

from United Kingdom

Joined: 09 Sep 2005
Posts: 38
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Sep 11, 2005 4:49 pm    Post Subject:
Reply with quote Thanks

what have you used for testing the earth with.
Back to top
 Alert Moderators
walton

from United Kingdom

Joined: 11 Sep 2005
Posts: 11
Location: Hull,
United Kingdom
Thanked: 0 times

PostPosted: Sun Sep 11, 2005 4:49 pm    Post Subject:
Reply with quote Thanks

digital multimeter
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Sun Sep 11, 2005 4:50 pm    Post Subject:
Reply with quote Thanks

walton wrote:
Yes agreed but why is there a reading in the first place, and even with the new CU installed I still get a reading through the earth which again I tracked down to the new appliancies. could they both be faulty, and if so why isnt the RCD (which is an 80 A not 100) not tripping.

It is the mA leakage which causes the RCD to trip. If the mA leakage is not high enough, the RCD doesn't trip.
What type of supply do you have? http://www.diynot.com/forums/viewtopic.php?t=7553&postdays=0&postorder=asc&start=9
Back to top
 Alert Moderators
walton

from United Kingdom

Joined: 11 Sep 2005
Posts: 11
Location: Hull,
United Kingdom
Thanked: 0 times

PostPosted: Sun Sep 11, 2005 4:53 pm    Post Subject:
Reply with quote Thanks

the mA reding was 6 and the voltage was 110v are the appliancies faulty
Back to top
 Alert Moderators
yai46

from United Kingdom

Joined: 09 Sep 2005
Posts: 38
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Sep 11, 2005 4:53 pm    Post Subject:
Reply with quote Thanks

try pluging the machine into an other socket in an other room via an extension lead, i would imagine your find that there is no problem with the appliance by doing this and the fault is due to the earth being no good or loose.

What is the continuity of the earth reading?
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Sun Sep 11, 2005 4:56 pm    Post Subject:
Reply with quote Thanks

walton wrote:

the mA reding was 6 and the voltage was 110v are the appliancies faulty

No, not necesseraly.
6mA is not enough to trip an RCD (I assume it is 30mA?).
How many earth wires enter the socket (excluding the back box loop)?
Is the circuit a ring main?
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
PIR Security light (500w) instalation (with pictures) Help 10 1120 Wed Dec 05, 2007 11:16 am
cooker hood instalation 7 400 Tue Sep 02, 2008 1:29 pm
Electric Shower Instalation Help 6 280 Tue Nov 04, 2008 12:35 pm
Garage power instalation 8 620 Mon Oct 01, 2007 2:27 pm
Instalation Certificaiton 3 600 Tue Dec 05, 2006 4:03 pm