Posted: Tue Sep 27, 2005 8:48 pm Post Subject: Adding a spur on a radial circuit? |
 |
|
Is it possible to add a new double socket from the back of a single socket which I belive is part way along a radial circuit protected by a 32 MCB?
The circuit is in a small flat and is the only circuit feeding the electrical sockets.
Any advice greatly received.
Thanks |
|
andy

Joined: 14 Sep 2004 Posts: 3972 Location: United Kingdom Thanked: 0 times
|
|
stl

Joined: 27 Sep 2005 Posts: 22 Location: United Kingdom Thanked: 0 times
|
Posted: Thu Sep 29, 2005 8:28 pm Post Subject: Spur on a Radial circuit |
 |
|
Thanks for the reply.
Probably a daft question, but is there anyway of telling if the cable is 4mm - other than going into a shop and comparing with one there.
Also I have noticed elsewhere in my flat there is another double socket spur off a double socket but this appears to have been wired between the two using a domestic appliance cable (e.g. similar to a kettle or washing machine) - Am I correct in assuming this in unsafe? - It was in theflat when I moved in!!
thanks |
|
pdcelec

Joined: 05 Jun 2005 Posts: 707 Location: Birmingham, United Kingdom Thanked: 0 times
|
Posted: Thu Sep 29, 2005 8:46 pm Post Subject: |
 |
|
Get an electrician in to do a Periodic Inspection Report. If you have found these two faults already, what else could be lurking around!. |
|
kai

Joined: 15 Aug 2004 Posts: 729 Location: United Kingdom Thanked: 5 times
|
Posted: Thu Sep 29, 2005 8:46 pm Post Subject: cable |
 |
|
If the second double socket was wired in 2.5.sq.mm. flex, through a 13amp fuse-connection unit, then it should be safe (assuming the earthing is satisfactory). |
|