Lighting Circuit

This topic originated from the How to page called Preparing cable for connection
Click here to return to the page called Preparing cable for connection.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
AD1

from United Kingdom

Joined: 02 Oct 2005
Posts: 3
Location: Shropshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Oct 02, 2005 12:35 pm    Post Subject:
Lighting Circuit
Reply with quote Thanks

hi - hope someone can help.
I have a hall light that is 2 way and need to fit a new pendant - but being a donkey, I did not write down the wiring positions.
I have Earth, Neutral and Live on my pendant. From the ceiling, I have a 3 core wire and a 4 core wire. The 3 core has a black, Earth and Red. The 4 core has blue, earth, red and yellow. I assume the yellow is power. Can anyone pls tell me what joins with what. The switch is 2 way. thanks
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Sun Oct 02, 2005 12:41 pm    Post Subject:
Reply with quote Thanks

thats NOT a normal combination!

whats the wiring like at the switch?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon Oct 03, 2005 11:11 am    Post Subject:
Re: Lighting Circuit
Reply with quote Thanks

AD1 wrote:
I assume the yellow is power

Why?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
kendor

from United Kingdom

Joined: 16 Mar 2004
Posts: 5066
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 03, 2005 11:27 am    Post Subject:
Reply with quote Thanks

plugwash wrote:
thats NOT a normal combination!

whats the wiring like at the switch?
it is if it's conversion method
3 core and earth between switches.

AD1 it's likely that the red in what you call the 3 core( which is actually twin and earth) is live although some bright spark may have made the black live but it doesn't matter as long as you mark both cores red with tape.
Connections are as follows: at the switch with two cables connect the red from what you call the 4core cable ( which is actually 3 core and earth) to the common terminal on your two way switch, in L1 put the red from the twin and earth cable with the yellow from the 3 core and earth cable.
Connect the remaining black(marked with red tape) and blue wires to L2
at the other two way switch ( just the three cores there)the connections should be as follows:
red to common, yellow to L1 and blue to L2. obviously earths go their respective terminals in the back of the switch boxes.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon Oct 03, 2005 11:46 am    Post Subject:
Reply with quote Thanks

Err - kendor - I suggest you read the Q again - he has T+E and 3C+E at the ceiling rose, not at switches...

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
kendor

from United Kingdom

Joined: 16 Mar 2004
Posts: 5066
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 03, 2005 11:49 am    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
Err - kendor - I suggest you read the Q again - he has T+E and 3C+E at the ceiling rose, not at switches...
Ban agreed it could be read that way but i have read it again and i beleive he has not been clear in his description and that at the switches he is quoting the cables read again and you might see what i mean.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon Oct 03, 2005 11:58 am    Post Subject:
Reply with quote Thanks

kendor wrote:
Ban agreed it could be read that way but i have read it again and i beleive he has not been clear in his description and that at the switches he is quoting the cables read again

OK.

AD1 wrote:
I have a hall light that is 2 way and need to fit a new pendant

So he's talking about a new light fitting on the ceiling, not a new light switch.

AD1 wrote:
I have Earth, Neutral and Live on my pendant.

So he's got a new light fitting for the ceiling, not a new light switch.

AD1 wrote:
From the ceiling, I have a 3 core wire and a 4 core wire.


kendor wrote:
and you might see what i mean.

Sorry, no....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
kendor

from United Kingdom

Joined: 16 Mar 2004
Posts: 5066
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 03, 2005 12:04 pm    Post Subject:
Reply with quote Thanks

Ok ban "from the ceiling" could mean he's at the switch and two cables disappear up to the ceiling do you see what i mean now? he's not been clear enough in his description and it could be taken bothe ways, so although i'm not disagreeing with your interpretation , i believe he meant the 3C+E and twin and earth are in fact at the switch which he has removed this would seem the logical place to find this arrangement.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon Oct 03, 2005 12:08 pm    Post Subject:
Reply with quote Thanks

Ah well - no point arguing - we'll wait for the OP to respond....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
kendor

from United Kingdom

Joined: 16 Mar 2004
Posts: 5066
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 03, 2005 12:09 pm    Post Subject:
Reply with quote Thanks

yep agreed
Back to top
 Alert Moderators
AD1

from United Kingdom

Joined: 02 Oct 2005
Posts: 3
Location: Shropshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 03, 2005 12:25 pm    Post Subject:
Reply with quote Thanks

sorry for the confusion, the wires are dangling from the ceiling. My reference to the switches is that the light is operated by 2 switches (hence 2 way). I assume yellow is power because in new builds I thought that was the lighting power cable - I may be wrong.

I cannot see tape on any of the wires.

thanks

++++++++++++++++++++++++++++

sorry - forgot to add that I am doing nothing at the switches - they are fine.

________________________
moderator

please note 10a which is here
Back to top
 Alert Moderators
Gary0

from United Kingdom

Joined: 30 Sep 2005
Posts: 139
Location: Hertfordshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 03, 2005 12:42 pm    Post Subject:
Reply with quote Thanks

I believe the problem was, from which point are the cables dangling from the ceiling. But I think we can assume from the point where your light fitting is/was.

In which case there is something wrong with the way the circuit was wired. Have a check with the diagrams in the sticky thread.

The blue, red, and yellow cable is for connecting between 2 switches, it shouldn't normally go near the light. Although I have seen (and not paid too much attention too) circuits whereby both switch cables end up at the light fitting (rose or junction box) and one core is just connected through. I'll see if I can find the diagram.

Ultimately I think you need to open up the switches and note what cable/core is connected where, to each. If you can work out where they end up, it become less of a task to work out how they need to be wired at the light.

-------------

Darn, checked last week's history on this PC, no dice. May have seen it on PC at home, but in any case I think I've worked out what the diagram must have shown.

The following for interest only, as a possibility, do check out what it is you really have.

If 4 cables came into the rose or junction box at the ceiling then 2 can be accounted for as mains in, and mains out (if this is the end of the run there may not be a mains out as unlike rings one doesn't tend to feed the end back to the c/u).

Remembering that the colours are interchangeable in the following description (although obviously you have to make any changes consistent throughout icon_smile.gif consider the following ...

3rd cable goes to one switch, 4th cable to the other.
At both switches yellow (for example) is connected to the common, blue and red to the other two connections.
Back at the rose or jb, yellow from each cable is just connected together so effectively goes from one switch common to the other.

Red (for example) on both switch cables, gets connected to the live at the rose. Blue (for example) on both cables, gets connected together and treated as the 'switched live', and taken to the lamp.

This, of course, assumes that there are cables still up in the ceiling that you are not aware of yet.

Now that may not be what you have, and I'll check the diagram (just in case that description goes bang icon_wink.gif) I've just sketched out again, but when you check what you have at the switches, you may find that, that just might be what you started with.

Personally I'd try to rewire it more conventionally if I were you, in any case.

------------

icon_redface.gif Well blow me down if it wasn't right here on this site after all !

The cable saving pic here

__________________
I may take 10 times as long, but all the decent professionals are too busy to look and estimate.


Last edited by Gary0 on Fri Oct 07, 2005 6:05 pm, edited 4 times in total
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Mon Oct 03, 2005 1:41 pm    Post Subject:
Reply with quote Thanks

plugwash wrote:
thats NOT a normal combination
... for a hall light.
Gary0 wrote:
The blue, red, and yellow cable is for connecting between 2 switches, it shouldn't normally go near the light
...in a hall.



It is reasonably common at the ceiling roses in bathrooms and toilets where a L/SL/N supply is taken to a fan.


PS - Kendor - you owe me a bacon sandwich and 3 illegal acts. icon_wink.gif

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Mon Oct 03, 2005 4:53 pm    Post Subject:
Reply with quote Thanks

ban-all-sheds wrote:
It is reasonably common at the ceiling roses in bathrooms and toilets where a L/SL/N supply is taken to a fan.

indeed but that would only bee seen if it was a loop in fed rose with a fan spurred off it, he only has one twin and earth cable at his light so it can't be a loop in rose with a fan spurred off it.
Back to top
 Alert Moderators
kendor

from United Kingdom

Joined: 16 Mar 2004
Posts: 5066
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 03, 2005 9:32 pm    Post Subject:
Reply with quote Thanks

apologies for wrong interpretation of post.
That is indeed a strange setup and i'm trying to think how it could work as a two way circuit unless there is also a cable going between the switches.
reason i say this is because there are only 5 cores involved bar an earth having been used illegally conversion method wouldn't work in this case as the connections are at the rose not at the switch. Alternatively if wired as live, strappers and switchline then there would still need to be more cores.
as suggested unscrewing of switches in order to ascertain what is going on would be necessary now. Also is there a Joint box above from where these two cables come from? this may explain the lack of cores with interconnecting being done before the two cables appear at the rose.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Adding to lighting circuit 5 320 Tue Nov 28, 2006 8:39 am
Lighting circuit for standing floor lamps....? 8 500 Mon Nov 27, 2006 3:55 pm
Shaver - Lighting circuit with no earth 3 2620 Mon Nov 27, 2006 2:44 pm
Plugging computer equipment into lighting circuit 19 3000 Sun Nov 19, 2006 7:13 pm
Lights that can't be connected to the lighting circuit? 9 460 Sun Dec 10, 2006 10:06 am