Gram1

Joined: 03 Sep 2003 Posts: 2 Location: United Kingdom Thanked: 0 times
|
Posted: Wed Sep 03, 2003 4:48 pm Post Subject: electric oven |
 |
|
I am currently having a new fitted kitchen and had an electrician run a spur from a double socket to below the worktop level for the oven to be powered from after being assured that it wasnt necessary to have thicker cooker wire. Is this correct. According to the installation instructions the power max usage is 2.07kW and the fuse rating is 13AMP. Any information would be appriciated as i am not very good with electrics |
|
breezer

Joined: 03 Jan 2003 Posts: 23346 Location: Sussex, United Kingdom Thanked: 5 times
|
Posted: Wed Sep 03, 2003 6:08 pm Post Subject: |
 |
|
it would have been better if he could have extended the ring but yes it is fine, because it only draws (as you said) 2.07Kw a plug / socket can supply up to 3 kw. __________________ Do you like music Mr Finch?
Forum = Opinions |
|
Gram1

Joined: 03 Sep 2003 Posts: 2 Location: United Kingdom Thanked: 0 times
|
Posted: Wed Sep 03, 2003 6:25 pm Post Subject: |
 |
|
Cheers breezer thats very useful to know |
|
alexnic

Joined: 19 Dec 2002 Posts: 186 Location: United Kingdom Thanked: 1 time
|
|