I am putting in a new electric shower. The current wiring is 10mm (sq.) wiring back to a re-wirable fuse of 30A.
I am looking at replacing the current shower (8KW) with an 8.5 or 9 kW. Both shower installation guides (I haven't bought it yet - just checking on the internet) specify a cartridge fuse of rating 45A. Can I just replace my re-wirable fuse (30A) with a cartridge type (45A) and are there any other implications ? Help appreciated |
|
ban-all-sheds

Joined: 27 Aug 2003 Posts: 21984 Location: London, United Kingdom Thanked: 78 times
|
Posted: Sun Oct 30, 2005 11:07 am Post Subject: |
 |
|
You would be much better off installing a separate shower CU, as I'll bet your existing installation does not have an RCD.
You are aware, I take it, of your legal obligation to notify LABC about the shower replacement before you start? __________________ I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth. |
|
Steve

Joined: 15 Apr 2005 Posts: 12845 Location: Yorkshire, United Kingdom Thanked: 21 times
|
Posted: Sun Oct 30, 2005 7:31 pm Post Subject: |
 |
|
You have to have a 45A MCB and an RCD is also recommended for shower circuits, as ban has pointed out.
OOI, how do you know the current MCB is 10mm˛? I wouldn't think anyone would put a 10mm˛ cable on a 30A fuse, unless it is a very long run. Sure its not 6mm˛? The difference is crucial. |
|