Posted: Mon Dec 19, 2005 5:18 pm Post Subject: Dimmer switch earth |
 |
|
In our new house the supply cable earth is already attached to the mounting box earth terminal.Is it perfectly OK to attach the earth on a metal dimmer switch to the same mounting box terminal i.e. I'd have 2 wires connected there? Is there any preference for the dimmer's earth to mounting box earth terminal, being sleeved cable rather than flex? |
|
plugwash

Joined: 28 Mar 2004 Posts: 6930 Location: United Kingdom Thanked: 15 times
|
Posted: Mon Dec 19, 2005 10:52 pm Post Subject: |
 |
|
for the earth link between backbox and faceplate sleeved earth from T&E is acceptable but it can be a little unwieldly.
a bit of earth from flex of appropriate size (e.g. 1mm or more for lighting stuff) would be fine so would a peice of single core earth wire. |
|
ban-all-sheds

Joined: 27 Aug 2003 Posts: 21979 Location: London, United Kingdom Thanked: 78 times
|
Posted: Mon Dec 19, 2005 10:58 pm Post Subject: |
 |
|
I always keep odd lengths and offcuts of flex for just this purpose. __________________ I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth. |
|