- Joined
- 27 Jan 2008
- Messages
- 23,624
- Reaction score
- 2,661
- Location
- Llanfair Caereinion, Nr Welshpool
- Country
So if an installation has not be modified or altered since the previous edition and it complied fully with previous edition does that mean it still complies or not?The Regulations apply to the design. erection and verification of electrical installations, also additions and alterations to existing installations. Existing installations that have been installed in accordance with earlier editions of the Regulations may not comply with this edition in every respect. This does not necessarily mean that they are unsafe for continued use or require upgrading.
Code 4 was so easy. The loss of code 4 means we have to decide if it should be not coded or if it should get a code 3.
To put a note "This installation was installed to an old edition of BS 7671 and any alterations may require an upgrade first to current regulations." is a fair comment.
But filling a report with code 3's which are in essence all down to the same change in regulations is hiding real faults.
When for example inspecting a bathroom the bonding required depends on the presence of RCD protection. How can one report the same fault twice? If one says bonding is missing and RCD protection is missing then one is reporting the same fault twice. To say protection is missing is rather too vague. If one says either bonding or RCD protection is required that is also incorrect as with a new bit of installation it needs RCD protection and once you work on it that bit is new.
I keep seeing EICR's with reams of code 3's each one referring to the same thing no RCD protection.
To in a report write "Note 1 :- This installation does not have the RCD protection required in new installations since 2008 which mean many items fail to reach the standards set in BS7671:2008 this does not make the installation dangerous but will mean any additions or alterations will required the addition of RCD protection." then with every item which fails because of no RCD enter see note 1 is fair enough.
But to fill the report with Code 3's which all refer to the same regulation change just hides real faults.
What does the team think?