pressure prob i think???help

This topic originated from the How to page called Choosing a shower
Click here to return to the page called Choosing a shower.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
leonuk

from United Kingdom

Joined: 30 Jan 2006
Posts: 1
Location: Nottingham,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jan 30, 2006 10:00 pm    Post Subject:
pressure prob i think???help
Reply with quote Thanks

just installed a triton aquatronic 3+ 9.5kw shower into our bathroom,its connected straight to the mains when the shower settings are turned down to cold the pressure is fine but when i turn the temp up the pressure goes and just trickles out!! is this because there is not enough pressure frm the cold water feed(mains).just to let u know i live in a ground floor flat not a house some one pls help
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Prof.plumb

from United Kingdom

Joined: 09 Feb 2006
Posts: 188
Location: Leicester,
United Kingdom
Thanked: 2 times

PostPosted: Thu Feb 09, 2006 2:47 pm    Post Subject:
Your problem
Reply with quote Thanks

Very strange. Firstly let me explain how an electric shower works.
Cold water from the mains comes in and it is heated via an element. similar principle to a kettle if you like. Now, obvioulsy when there is a demand for cold water the pressure is good as the shower is not having to heat the water up. And when the demand is for hot water the shower is put through its paces.
Now, the problem you are encountering i would say would be common place with a 7.5Kw shower or and 8Kw shower but 9.5Kw showers usually have a good flow rate.
There are a few things that could cause this problem.
1- Mains water was isolated at stop cock and hasn't been fully re-opened.
2- You may have assumed it is mains you have tapped onto but if it is tank fed cold water then this would explain the problem immediately.
3- what power is there at the shower if it is 230 V the performance of the shower may only sort of be around 8Kw opposed to 9.5 at 240.
4- it could be a faulty element.
My advice to you is check the shower is installed correctly and if it is call the manufacturers as they cover all products for a year and get them to come have a look.
Best of luck!
Back to top
 Alert Moderators
ChrisR

from United Kingdom

Joined: 24 Jul 2003
Posts: 18661
Location: London,
United Kingdom
Thanked: 62 times

PostPosted: Thu Feb 09, 2006 3:06 pm    Post Subject:
Reply with quote Thanks

Measure the flow at showering temperature. You can only expect about 4 litres/minute.
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19532
Location: United Kingdom
Thanked: 6 times

PostPosted: Sat Feb 11, 2006 9:05 pm    Post Subject:
Re: Your problem
Reply with quote Thanks

Prof.plumb wrote:
3- what power is there at the shower if it is 230 V the performance of the shower may only sort of be around 8Kw opposed to 9.5 at 240.

Really? You've calculated that have you? According to my rudimentary arithmetic, 9.5kW would draw 39.6 Amps at 240V and 37.9 Amps at 230V - the latter equates to 8.7kW, not "sort of around 8kW".

Prof.plumb wrote:
My advice to you is check the shower is installed correctly and if it is call the manufacturers as they cover all products for a year and get them to come have a look.
Best of luck!

Best of luck indeed - roughly how many manufacturers have you witnessed being successfully persuaded to "come and have a look" at a customer's installation? Just roughly mind - is it more than 0? More than 1? More than 2?
Back to top
 Alert Moderators
chrishutt

from St. Pierre and Miquelon

Joined: 20 May 2005
Posts: 5346
Location: St. Pierre and Miquelon
Thanked: 2 times

PostPosted: Sat Feb 11, 2006 9:54 pm    Post Subject:
Reply with quote Thanks

Leonuk, ignore Plod.plumb - do what ChrisR suggests.

__________________
Let's face FAQs.
Back to top
 Alert Moderators
dal5band

from United Kingdom

Joined: 03 Mar 2005
Posts: 417
Location: Surrey,
United Kingdom
Thanked: 1 time

PostPosted: Sat Feb 11, 2006 10:11 pm    Post Subject:
Reply with quote Thanks

yup - electric shower flow rates are not very good - esp in winter as the incoming water is at its coldest.

What you think is a trickle may be the best the shower can do. Maybe you need a finer showerhead to create a bit of a spray.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Swiftflow 75 pressure prob - advice gratefully received 7 960 Fri Nov 12, 2004 2:38 pm
electric shower, pressure prob? 8 280 Fri Sep 05, 2008 3:09 pm
halstead prob 9 360 Sun Mar 26, 2006 10:24 pm
Connecting onto a bar shower prob 9 560 Mon Mar 27, 2006 8:48 pm
Potterton -Performa 24 - Keeps coming on - Micro-Switch Prob 21 5240 Fri Apr 07, 2006 6:13 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.