rccb

This topic originated from the How to page called Miniature circuit breakers (MCBs)
Click here to return to the page called Miniature circuit breakers (MCBs).

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
KDOE

from United Kingdom

Joined: 30 Jan 2006
Posts: 12
Location: Somerset,
United Kingdom

PostPosted: Wed Feb 01, 2006 12:58 pm Reply with quote

Can anyone tell af a rccb is a sutible substitute for a rcd on a sower radial circuit, the shower is 9.5kw on 10mm cable with a run of about 15 meters, rccb is 45a on cu. thanks
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Qedelec

from United Kingdom

Joined: 22 Jun 2005
Posts: 1160
Location: Birmingham,
United Kingdom

PostPosted: Wed Feb 01, 2006 1:48 pm Reply with quote

RCCB is Residual Current Circuit Breaker and is the full name for what most refer to as a RCD or Residual Current Device.
So the answer is Yes!
Back to top
 Alert Moderators
KDOE

from United Kingdom

Joined: 30 Jan 2006
Posts: 12
Location: Somerset,
United Kingdom

PostPosted: Wed Feb 01, 2006 2:11 pm Reply with quote

Thanks for that,

Can you or anyone tell me the best way to connect a duel element immersion (seperate side elements), ?
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 35959
Location: Hampshire,
United Kingdom
Thanked: 1253 times

PostPosted: Wed Feb 01, 2006 3:31 pm Reply with quote

KDOE wrote:
Can anyone tell af a rccb is a sutible substitute for a rcd on a sower radial circuit, the shower is 9.5kw on 10mm cable with a run of about 15 meters, rccb is 45a on cu. thanks


You will need an MCB as well, of course.
Back to top
 Alert Moderators
tomgunn

from United Kingdom

Joined: 11 Nov 2008
Posts: 2
Location: Surrey,
United Kingdom

PostPosted: Fri Jul 03, 2009 3:48 pm Reply with quote

Hi.. I think that you are getting confused between an RCCB and an RCBO, I think that you mean to ask about an RCBO as an RCCB / RCD is for mains switching. If you use an RCD / RCCB then you would use MCB’s for mechanical protection but if you use an RCBO, ( which I believe that you really mean ), then you don’t need an RCD for mains switching!

If you do use an RCBO then what you have is a fuse devise that combines an RCD & an MCB in one...so theres no need fo an RCD!

If you’re changing a CCU, ( Customers Consumer Unit ), then you would need to offer the correct protection as per the current IET / 17th edition / regs or if you’re running a new circuit and if you’re extending an existing circuit then your test should be for the disconnection time of the extended circuit of around 0.4sec / 0.2sec etc.. but if you have the old 3036 / re-wireable fuses it is unlikely that you get this osrt of reading!

For your shower unit on a 45amp fuse / RCBO / MCB etc then the cable size you would require, ( and there are several things you need to check out such as does the cable run under insulation etc etc ), would need to be checked although 10mm seems fine... but do check it out as per VD etc!
Back to top
 Alert Moderators
ericmark

from United Kingdom

Joined: 27 Jan 2008
Posts: 7203
Location: Flintshire,
United Kingdom
Thanked: 602 times

PostPosted: Fri Jul 03, 2009 4:51 pm Reply with quote

ELCB = Earth Leakage Circuit Breaker there are two main types the old voltage type now no longer used.
GFCI = ground fault circuit interrupter same as ELCB again two main types.
GFI = ELCB as above
RCD = residual current device is the same as a RCCB.
RCCB = residual current circuit breaker is a current ELCB
ALCI = appliance leakage current interrupter yet another name for RCD.

As far as I am aware all the above normally break all live conductors (Remember neutral is classed as live).

RCBO = Residual-current Breaker with Overload these units also have a MCB built in and unlike the RCD often do not open all live conductors although some do and one does have to be careful in selecting correct type.

The RCD also is sub-divided into different types and the list is long but two main types “Active” and “Passive”. The active will open with loss of supply so fails safe. The passive will stay connected during a volt drop to below the level to which they will work effectively but are used in most consumer units so after a power failure items like a fridge will continue to work.

There are main specials including auto re-setting and add on units which attach to a circuit breaker which would need a book to cover them all.

In the home most are 30ma which is considered the current which is unlikely to cause permanent damage. There are also 10ma versions used for items like pond pumps so in event of failure the main 30ma with not trip. There are also 100ma versions which were used with earth rods before the advent of 17th Edition and do not give enough protection against shock to be used with sockets under 20A.

Most RCD’s will work within 40ms but some (Type S) normally the 100ma type have a delay built in so they will not trip too often in thunder storms etc.

For a shower you need a 10ma or 30ma version.

As to duel or single pole that depends on earthing arrangements. Where a supply with earth rods (TT) is used i.e. Caravans, Boats and some houses than normally a duel pole is used or required. But with a PME (TN-C-S) often a single pole is considered as enough.
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 14170
Location: Cumbria,
United Kingdom
Thanked: 396 times

PostPosted: Fri Jul 03, 2009 10:22 pm Reply with quote

RCD is a generic term for all of the devices which operate on residual current. An RCCB is an RCD. An RCBO is an RCD. A SRCD is an RCD. GFCI is American. The OP was in 2006 and things have changed since then too.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
RCCB removal 8 440 Sat Jan 02, 2010 4:24 pm
RCCB Not switching on 22 1200 Fri Apr 16, 2010 4:35 pm
Steam Iron RCCB/RCBO 5 580 Thu Apr 15, 2010 5:20 pm
rccb,s 13 500 Thu Mar 18, 2010 7:35 pm
Wiring diagram correct for 63A RCCB and 50A MCB? 8 6940 Fri Dec 04, 2009 4:27 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.