Spur

This topic originated from the How to page called Adding a spur to a ring circuit from a junction box
Click here to return to the page called Adding a spur to a ring circuit from a junction box.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
Grandad-Seaweed

from United Kingdom

Joined: 01 Feb 2006
Posts: 11
Location: Sussex,
United Kingdom
Thanked: 0 times

PostPosted: Wed Feb 01, 2006 5:42 pm    Post Subject:
Spur
Reply with quote Thanks

If I run a spur off an existing socket using a 13a FCU first off, can I daisy chain other sockets from the new socket. i.e existing socket-fcu-new socket-new socket-etc,
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Wed Feb 01, 2006 7:21 pm    Post Subject:
Reply with quote Thanks

yes. wire new sockets to "load" side of FCU, wire mains supply to "supply"
Back to top
 Alert Moderators
bpowell555

from United Kingdom

Joined: 19 May 2005
Posts: 314
Location: Sussex,
United Kingdom
Thanked: 0 times

PostPosted: Wed Feb 01, 2006 9:46 pm    Post Subject:
Reply with quote Thanks

Does this mean you can spur off a spur?!!
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Wed Feb 01, 2006 9:55 pm    Post Subject:
Reply with quote Thanks

It means that if you have a fused spur, as he described, you can put seeral small loads it safe in the knowledge that the total load will never exceed 13Amp because that it waht you have fused it down to. The other items are run in a single line, not branching off into spurs. It's a radial.
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Wed Feb 01, 2006 9:58 pm    Post Subject:
Reply with quote Thanks

bpowell555 wrote:
Does this mean you can spur off a spur?!!


Trying to catch me out eh? didn't work icon_wink.gif
Back to top
 Alert Moderators
bpowell555

from United Kingdom

Joined: 19 May 2005
Posts: 314
Location: Sussex,
United Kingdom
Thanked: 0 times

PostPosted: Thu Feb 02, 2006 4:40 pm    Post Subject:
Reply with quote Thanks

crafty1289 wrote:
bpowell555 wrote:
Does this mean you can spur off a spur?!!


Trying to catch me out eh? didn't work icon_wink.gif



hehe if I ever caught you out it would be a complete fluke!!!

Seriously though, let me get this right, you can't spur off a spur but you can run an FCU off a spur? This is brilliant! That's made my day icon_smile.gif
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Thu Feb 02, 2006 7:56 pm    Post Subject:
Reply with quote Thanks

bpowell555 wrote:
Seriously though, let me get this right, you can't spur off a spur but you can run an FCU off a spur? This is brilliant! That's made my day icon_smile.gif

noooo! come back!

you can have a spur (chain of sockets on 2.5mm˛) as long as you want, with as many sockets as you want, PROVIDING you start the chain of sockets with an FCU with a 13A fuse in it!

Think about it like those 10-way trailing sockets you can buy now, they start with a 13A plug, its just the same.
Back to top
 Alert Moderators
bpowell555

from United Kingdom

Joined: 19 May 2005
Posts: 314
Location: Sussex,
United Kingdom
Thanked: 0 times

PostPosted: Mon Feb 06, 2006 9:38 am    Post Subject:
Reply with quote Thanks

crafty1289 wrote:
bpowell555 wrote:
Seriously though, let me get this right, you can't spur off a spur but you can run an FCU off a spur? This is brilliant! That's made my day icon_smile.gif

noooo! come back!

you can have a spur (chain of sockets on 2.5mm˛) as long as you want, with as many sockets as you want, PROVIDING you start the chain of sockets with an FCU with a 13A fuse in it!

Think about it like those 10-way trailing sockets you can buy now, they start with a 13A plug, its just the same.



Ok I get you the FCU must be at the start of the spur. So if you have a spur you want to extend and are sure its not already a spur off a spur, then you should cut an FCU in before the spur after which you can extend ad infinitum - for low load items.

This is cool. It gives me some options for wiring I hadn't thought were available before icon_smile.gif

Cheers!
Back to top
 Alert Moderators
andy

from United Kingdom

Joined: 14 Sep 2004
Posts: 3972
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon Feb 06, 2006 9:41 am    Post Subject:
Reply with quote Thanks

bpowell555 wrote:
crafty1289 wrote:
bpowell555 wrote:
Seriously though, let me get this right, you can't spur off a spur but you can run an FCU off a spur? This is brilliant! That's made my day icon_smile.gif

noooo! come back!

you can have a spur (chain of sockets on 2.5mm˛) as long as you want, with as many sockets as you want, PROVIDING you start the chain of sockets with an FCU with a 13A fuse in it!

Think about it like those 10-way trailing sockets you can buy now, they start with a 13A plug, its just the same.



Ok I get you the FCU must be at the start of the spur. So if you have a spur you want to extend and are sure its not already a spur off a spur, then you should cut an FCU in before the spur after which you can extend ad infinitum - for low load items.

This is cool. It gives me some options for wiring I hadn't thought were available before icon_smile.gif

Cheers!


altho if you do go this way, be aware that you only have 13A to play with for all the sockets fed form the FCU. so no using the hoover and electric heater....
Back to top
 Alert Moderators
richardpy1

from United Kingdom

Joined: 15 Feb 2006
Posts: 14
Location: Coventry,
United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 22, 2006 4:01 pm    Post Subject:
Reply with quote Thanks

To further clarify, if you have a socket which is already on a spur and then you fit an FCU to "extend" the spur, the length of cable running between the socket and the FCU is technically an unfused spur itself (as the FCU comes AFTER it not before it.) Therefore this length of cable, however short, is "an unfused spur off an unfused spur" which is not allowed ?

Views ??

Hope that doesn't confuse !


Rich
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21984
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Wed Mar 22, 2006 6:10 pm    Post Subject:
Reply with quote Thanks

bpowell555 wrote:
This is cool. It gives me some options for wiring I hadn't thought were available before icon_smile.gif


Sounds as if you need to improve your knowledge before embarking on any more work.

Useful books, from which you can learn a great deal.

IMPORTANT NOTE - when buying books from Amazon, seek confirmation that they are the latest versions.

http://www.amazon.co.uk/exec/obidos/ASIN/0852028172

http://www.amazon.co.uk/exec/obidos/ASIN/0863413749

or http://www.iee.org/Publish/Books/WireAssoc/index.cfm?book=WR%20261


http://www.iee.org/Publish/Books/WireAssoc/index.cfm?book=WR%20500


http://www.amazon.co.uk/exec/obidos/tg/stores/detail/-/books/0953788547

or http://www.tlc-direct.co.uk/Main_Index/Electricians_Guide_Book/index.html

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
johnny_t

from United Kingdom

Joined: 26 Aug 2005
Posts: 1596
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 22, 2006 6:38 pm    Post Subject:
Reply with quote Thanks

richardpy1 wrote:
To further clarify, if you have a socket which is already on a spur and then you fit an FCU to "extend" the spur, the length of cable running between the socket and the FCU is technically an unfused spur itself (as the FCU comes AFTER it not before it.) Therefore this length of cable, however short, is "an unfused spur off an unfused spur" which is not allowed ?

Views ??

Hope that doesn't confuse !


Rich


The FCU goes before the first socket in the spur, so it is connected to the existing socket (on a ring or radial), not after the existing spur socket. If you want to turn an existing unfused spur into a fused spur, the fuse goes before the socket on that spur.

With regard to the cable up to the fuse, the current in this is still limited to the fuse current, unless of course you manage to stick a nail through it, but in that case the current is then picked up by the fuse on the existing circuit.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
lighting spur from a ring main/socket 25 5820 Sun Dec 02, 2007 10:22 am
Installation of new spur. 2 140 Sun Dec 02, 2007 8:11 pm
Lighting & Fan Spur 2 220 Tue Nov 27, 2007 11:48 pm
Fused spur/ socket/ switched socket 6 640 Mon Nov 26, 2007 9:11 pm
Adding a socket to an existing spur 5 500 Mon Nov 26, 2007 4:40 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.