Pipe frost stat

Joined
31 Mar 2006
Messages
20,027
Reaction score
1,391
Location
Leeds
Country
United Kingdom
Hi all.

I have a rad in my garage. The pipes for it run through an unheated part of the garage to the room where the rad is.

A few years ago when winter was really cold one of the pipes froze and burst and the rad also split. The rad has been disconnected since then.

I'm now looking to recommission the the rad but I now realise some frost protection is a must.

I was thinking a pipe stat on the return pipe set at a couple of degrees above freezing to fire the boiler and run the garage circuit would be the best way to prevent freezing.

Can you recommend a pipe stat which a range low enough to facilitate this? All the ones I've seen so far have a minimum setting of 40 degrees C.

Or is there a better way to protect the pipes from freezing? I looked at trace heating but I don't think it would be the best soloution for me.
 
Sponsored Links
Use a wall mounted frost stat to close when the air temp in the area to be protected is just above freezing and a pipe stat in series on the return to open when the pipe temp reaches 10-15 degrees C.. Honeywell make them and are nice and cheap..
 
That was my plan, I'm just struggling to find a pipe stat which operates at temperatures low enough for frost protection.
 